Where to locate neutral to ground bond?
Sun Dog
Solar Expert Posts: 115 ✭✭
Recently discovered that there is no neutral to ground bond in our system. There are three locations where this could be done, in the distribution panel that is connected to our XW4024, in the main panel (about 5ft away from the inverter) or in the panel in the house.
Which is the best choice.......and why?
Which is the best choice.......and why?
Comments
-
I would put it in the box with the shortest, most direct route to the ground electrode.
As for terminology, "main panel" usually means the box with the neutral-ground bond. The downstream boxes without the bond are subpanels of the main panel.
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
In my case that would be the distribution panel. Thanks for the explanation.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed