xantrex AGS problems...

Options
jbechhold
jbechhold Registered Users Posts: 1
i just helped a friend install an Xantrex AGS at my home...Baldor generator...Xantrex Xw hybred inverter, believe model 6040...the AGS worked great for a month...gen type 8...automatic on mode setting...why won't the AGS kick on any longer automatically.....?....am off grid....if i put mode on manual start the generator starts right up...when i take it off manual start, and put it back on auto it will not turn on by itself/automatically...any ideas...?...

Comments

  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Options
    Something changed, either broke, someone adjusted a setpoint.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • BB.
    BB. Super Moderators, Administrators Posts: 33,439 admin
    Options
    Also check voltages everywhere in the system (battery bank, leads where they connect to AGS, etc.).

    As Mike asks, something broken (lightning strike in the area, somebody tripped over a wire)?

    Can you read the various voltages in the software/display (are you getting the right numbers from sensors)?

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • new2PV
    new2PV Solar Expert Posts: 305 ✭✭
    Options
    What other components are in the system ?
    XW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array