Rotating batteries in a battery bank!

Farmerboyz1721
Farmerboyz1721 Registered Users Posts: 39 ✭✭
I would like to get everyone's opinion on rotating batteries. I have tried to google this and can't find anything.

I have a 12 volt battery bank @ 1248 Amphr. Built with 12 6 volt batteries in parallel and series. 
I have a DC amp clamp and i can monitor and see that the bulk of the amps get pulled from the front of the battery bank.(60 amps) Where the load is connected too. The batteries on the back end of the bank pull a much smaller (8 amps) .

This got me to wonder if the batteries should be rotated in different spots of the battery bank every so often. Any thoughts on this???
«1

Comments

  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
    Welcome to the forum,

    The basic problem is that you have too many parallel batteries... it's doomed to failure.  I just explained this to someone with 4 strings in parallel:   http://forum.solar-electric.com/discussion/comment/356663/#Comment_356663

    If you want to make the best of a bad (parallel) situation, it helps to wire them with bus bars.  

    Another factor that can cause batteries (series or parallel) to diverge is temperature variation.  All the batteries must be at the same temperature. 

    If you decide to do an equalization, disconnect 5 of your battery strings and equalize just one string at a time.

    --vtMaps

    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • Farmerboyz1721
    Farmerboyz1721 Registered Users Posts: 39 ✭✭
    vtmaps,

    Thank you for the information. Did not know that there should be limits to parallel connections. Could you elaborate on wiring them with bus bars? I would love to do what i can to keep this battery bank alive. It has no more then 150 cycles on it. Also i will ask again is there any logic to battery rotation? What about wiring the main line into the middle of the battery bank?
  • Farmerboyz1721
    Farmerboyz1721 Registered Users Posts: 39 ✭✭
    I did find this site. It defiantly helped me see some of my errors. It also explained balancing the batteries better. 

    It sounds like to me that the answer is not to rotate batteries but to get them balanced. 

    http://www.smartgauge.co.uk/batt_con.html

  • Brock
    Brock Solar Expert Posts: 639 ✭✭✭✭
    On that diagram basically #3 is how you would wire up a bus bar, with each battery sting + leading to the + bus bar and each - to the - bus bar.  If you have more than 2 stings you really need to wire them that way.  If you do this you will get as even of a draw from each string as you can and then there is no need to rotate.  Rotating them helps, but they will get further and further out of balance from each other to a point where they start a cascading failure.
    3kw solar PV, 4 LiFePO4 100a, xw 6048, Honda eu2000i, iota DLS-54-13, Tesla 3, Leaf, Volt, 4 ton horizontal geothermal, grid tied - Green Bay, WI
  • BB.
    BB. Super Moderators, Administrators Posts: 33,623 admin
    Getting the battery bank "rewired" to balance current (load and charging) will help a lot.

    There has been discussion here by a few people that even with one string of batteries (no current balancing issues) that find they have better battery life/performance if they rotate the batteries once a year. For some folks, the battery near the + bus may not charge to the same level as the battery at the other end of the string.

    I cannot give you a reason why this is true for some folks (other than if battery ventilation is uneven--temperature variations)--But it has been seen.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,905 ✭✭✭✭✭✭
    I can give you 87 examples of why not rotating batteries in a single string bank has done no harm.
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • BB.
    BB. Super Moderators, Administrators Posts: 33,623 admin
    Just to be clear--It was a "few people" here (handful or less?) that found rotating battery positions was helpful for them.

    I certainly do not recommend it as a matter of standard operating procedure.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,905 ✭✭✭✭✭✭
    It makes my back hurt just thinking about it.
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • Johann
    Johann Solar Expert Posts: 245 ✭✭✭
    edited April 2016 #10
    Looks like the way you measure makes it look like that you get the wrong results or even make it look like that you have a major  problem.


    The way you got it wired the way I understand is like in this link http://www.smartgauge.co.uk/batt_con.html
      figure #1.
    You have the incoming wire to the battery and then you measure the amps right in front of the battery bank at the incoming wire to the batteries.......this will give you the total amps that all your batteries will take since the battery-supply-wire in front of the bank will supply power to all of the batteries and strings.
    Then if you take a measurement between string # 1 and string # 2 you will measure only the last 5 strings while you leave the 1st string out of your measurement and this will lower the amp reading since you only measure the amps of 5 strings and not 6 strings now.
    If you go between the 5th and 6th string (last string of the batteries) then you read only the amps of the last or 6th string ....right at that location of your measurement, you are reading the amps of one string only and that is why you get the lowest reading there.


    I hope that I understood it right the way you got it wired and the way you measure it..






  • Farmerboyz1721
    Farmerboyz1721 Registered Users Posts: 39 ✭✭


    First off i want to thank everyone for there inputs. I have decided to show my battery bank. I have also noted where and what the readings were. There is a correction to my original post. It is 30 amps at the load of the bank and 8 amps at the end. It appears that i need to rewire this to accommodate method #3 of the http://www.smartgauge.co.uk/batt_con.html 
  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
     It appears that i need to rewire this to accommodate method #3 of the http://www.smartgauge.co.uk/batt_con.html 
    Smartgauge does a good job of explaining how to put batteries in parallel.  The fault I find is that they do not emphasize the extent to which parallel batteries are a compromise of optimal design.  Even with perfect wiring and bus bars, 6 parallel strings is unstable. 

    By the way, it appears that you are doubling up cables on your battery interconnects.  That will increase the potential points of failure and the instability of the system.

    --vtMaps
    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • Johann
    Johann Solar Expert Posts: 245 ✭✭✭


    First off i want to thank everyone for there inputs. I have decided to show my battery bank. I have also noted where and what the readings were. There is a correction to my original post. It is 30 amps at the load of the bank and 8 amps at the end. It appears that i need to rewire this to accommodate method #3 of the http://www.smartgauge.co.uk/batt_con.html 
    That is exactly what I thought you have and the way you are measuring it.
    30 Amps is what your total battery bank is taking, while your 8 amp point is only part of one battery string out of 6 battery strings.
    To measure the 8 amp point more precise, you need to put both of your red wire (parallel wire) into your amp meter. If you clamp only 1 wire at the 8 amp point you are going to read only part of the amp reading for the last string.  You may have used both wire to measure already....

    If you want to measure the amps for each battery string (2 batteries in series), clamp your amp meter on the red and black wire together between the 2 batteries. Do this for each string,  Now compare your readings.

    Like this image below where the blue circle represents your amp clamp. Then go to the next battery string and so on. This way, you will read each battery string.


  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    I find it much easier to rotate the flywheel on my generator, and leave the batteries alone.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
    mike95490 said:
    I find it much easier to rotate the flywheel on my generator, and leave the batteries alone.
    Well, if you made some improvements to your battery box it would be easier to rotate them... you need to put your batteries on a turntable and connect them to the bus bars with some big brushes and commutator.

    The ability to rotate the batteries makes it easier to water them...  the cells in the back of the box can be rotated to the front.

    There is no reason you can't rig a motor, powered directly by solar panels, to the turntable.  The batteries would rotate continuously while charging.   Don't let them turn fast enough to develop lateral stratification.

    Good luck with the project!

    --vtMaps
    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • Brock
    Brock Solar Expert Posts: 639 ✭✭✭✭
    :)  But seriously about every year or so I disconnect everything, take the batteries out, clean everything, charge each battery individually, check each battery resting, write on the battery the resting voltage on the battery, check gravity and write that on the battery as well and make sure they are topped off and then put them all back in but move them around.  I do rock them around as move them, that might be the part that is pointless, but I do it anyway, maybe a motorized turntable  :)
    3kw solar PV, 4 LiFePO4 100a, xw 6048, Honda eu2000i, iota DLS-54-13, Tesla 3, Leaf, Volt, 4 ton horizontal geothermal, grid tied - Green Bay, WI
  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,905 ✭✭✭✭✭✭
    Are you folks using a moving coil cartridge on the turntable?
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • WaterWheel
    WaterWheel Registered Users Posts: 387 ✭✭✭
    I use a turn table with a slip ring to maintain the connection.     Works great and much easier on the back.

    I've been considering adding an automatic waterer, saw one on ebay. 

    Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor

    21 SW280 panels on Schletter ground mount

    48v Rolls 6CS 27P

  • Farmerboyz1721
    Farmerboyz1721 Registered Users Posts: 39 ✭✭

       

    Bunch of jokers on here today :):)

    Here is the total amp draw on each connection when the charger is on bulk charging mode.

  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,905 ✭✭✭✭✭✭
    How do you check the water?
    "we go where power lines don't" Sierra Nevada mountain area
       htps://offgridsolar1.com/
    E-mail offgridsolar@sti.net

  • Brock
    Brock Solar Expert Posts: 639 ✭✭✭✭
    If you don't plan to go with the bus bar idea you might actually consider rotating where you main leads attach to the bank.  So leaving the bank wired as is, but move the left side or negative lead to the second battery up and move the positive lead or right side to the second from the top.  With the way yours is setup I am guessing that would be the most balanced loading per battery, but you could move it take those same center readings again.

    The good thing is with the double wire on everything is you should have lower resistance, but the bad part of that is more connection points that could fail.

    As Dave noted, that has got to be difficult to check water they way it is now.
    3kw solar PV, 4 LiFePO4 100a, xw 6048, Honda eu2000i, iota DLS-54-13, Tesla 3, Leaf, Volt, 4 ton horizontal geothermal, grid tied - Green Bay, WI
  • Farmerboyz1721
    Farmerboyz1721 Registered Users Posts: 39 ✭✭
    It might not appear so. But, i can remove the tops and check/fill the water. It is not the greatest access but does work. 
  • Farmerboyz1721
    Farmerboyz1721 Registered Users Posts: 39 ✭✭
    Would there be a problem doubling up on the studs of the bus-bar?
    I have a 6 stud bus-bar and 6 parallel batteries to tie in. But, then i still need to wire in the inverter/charger and 12 volt load.
     
  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
    Would there be a problem doubling up on the studs of the bus-bar?
    I have a 6 stud bus-bar and 6 parallel batteries to tie in. But, then i still need to wire in the inverter/charger and 12 volt load.
    I am not aware of any bus bars that permit doubling of the conductors.  What is the amp rating of your 6 stud bus bar? 

    To combine 6 batteries properly you should have a battery combiner box with circuit breakers or fuses for each of the combined batteries.  Of course, combining 6 batteries in a cycling application is foolish, but with a combiner box you could be properly foolish.

    --vtMaps
    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • Farmerboyz1721
    Farmerboyz1721 Registered Users Posts: 39 ✭✭
    The bus bar is rated for 250 amps. 
  • Farmerboyz1721
    Farmerboyz1721 Registered Users Posts: 39 ✭✭
    edited April 2016 #26


    I quickly rewired to method # 2 because that was easy. http://www.smartgauge.co.uk/batt_con.html

     I don't think it balanced it out any better. 

    Next step to work on rewiring a bus bar. 

    Where is the best place to find a bus bar? The one i have is https://www.bluesea.com/products/2126/MaxiBus_250A_BusBar_-_Six_5_16in-18_Studs I need more terminals then 6 and i can't find one. 
  • vtmaps
    vtmaps Solar Expert Posts: 3,741 ✭✭✭✭
    Where is the best place to find a bus bar?
    I don't know if this is the best place, but it is a place:
     http://www.electrical-insulators-and-copper-ground-bars.com/ground-bar.html

    -vtMaps
    4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i
  • Mountain Don
    Mountain Don Solar Expert Posts: 494 ✭✭✭
    The company vtmaps linked to also sells copper bar stock in many sizes if you are interested in making your own buss bars from scratch.  That is what I did.
    Northern NM, 624 watts PV, The Kid CC, GC-2 batteries @ 24 VDC, Outback VFX3524M
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    I find it much easier to rotate the flywheel on my generator, and leave the batteries alone.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • BB.
    BB. Super Moderators, Administrators Posts: 33,623 admin
    Some folks here have found physically moving their batteries helps distribute wear (their high/low SG seem to follow string position and not physical battery--At least at times).

    Why--I have no clue if all is otherwise OK (good ventilation, one battery not hotter than the rest, etc.).

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • dennis461
    dennis461 Registered Users Posts: 109 ✭✭✭
    The setup you have looks OK to me, I wouldn't change anything.

    Camden County, NJ, USA
    19 SW285 panels
    SE5000 inverter
    grid tied