Controlling Mini Split via inverter AUX function
Desert Rat
Solar Expert Posts: 147 ✭✭✭
I'm planning to install a mini split air conditioner in my off grid home,, and have been thinking about a way to incorporate an automatic shutoff in the event that I'm not home and it gets cloudy. We often have sudden thunderstorms in the summer, and an otherwise sunny day can get cloudy unexpectedly. I want to prevent discharging the batteries when this happens.
I'm thinking I could wire the AUX relay in my inverter to a DC/AC relay, and have that relay cut power to the mini split circuit. Any problem doing this? Would this type of relay be suitable?
http://www.amazon.com/uxcell-SSR-75DA-H-Single-Phase-90-480V/dp/B00VG705G0/ref=sr_1_15?ie=UTF8&qid=1459386503&sr=8-15&keywords=DC+AC+relay
That will work but in general I prefer mechanical relays for applications like this. SSR's get pretty warm during higher current operation.
Look at the specs for RIB relays, I think one of these will work fine. They are inexpensive and come in many configurations18- 235 W Kyocera panel, 12- 4-KS-25PS Rolls 1350 Ah, Magnum MS4448PAE, ME RC50, ME AGS, Outback FM 80, Generac 8KW LP generator, 6.5 Honda Portable generator
stillchillin said:Look at the specs for RIB relays, I think one of these will work fine. They are inexpensive and come in many configurations
If the AUX contact that you are going to use is a dry contact you can use the line voltage from the mini split as the coil voltage and just switch that to control the relay. So your coil voltage would be 120V or 230V depending on the size of your mini split.
18- 235 W Kyocera panel, 12- 4-KS-25PS Rolls 1350 Ah, Magnum MS4448PAE, ME RC50, ME AGS, Outback FM 80, Generac 8KW LP generator, 6.5 Honda Portable generator -
Just pulled a relay of the shelf its a RIBU1C coil voltage is 10-30 VDC or 120 VAC contacts are SPDT and are rated for 10A you can get the contacts rated up to 30A. Hope this helps
Yes have to use rib relays, it gives best work and low-cost in your budget. RIB with additional value of very low power on the input, it suggest u can control 10-20amp relay from other device.
- 228 Forum & Website
- 618 Discussion Forums/Café