Schneider XW 6048 Auto Start Triggers

Northern_BC
Northern_BC Registered Users Posts: 33 ✭✭

Hello.

I live off grid and use a XW 6048 inverter. I am unable to set the automatic generator start triggers to start the generator for anything other than the 30 second voltage trigger. I want to use all four, 30 second, 15 minute, 2 hour, and 24 hour. From the manual I see that the generator start has to be set to Manual Off, to change these settings, but it is still not working. The generator only triggers at the 30 second. I have had the batteries below the other set voltages, and the time has passed without the generator starting.


Can anyone help me? I must be missing something.


Thank you.

XW6048 inverter, EnerSys 1520 Ah battery bank, 1500 watt tracker & 7500 watt stationary solar, 10kw Baldor NG generator

Comments

  • new2PV
    new2PV Solar Expert Posts: 305 ✭✭
    edited February 2016 #2
    Put the AGS into standby mode when changing those settings. Try and reboot it also see if that helps after doign changes.  Any other devices on the xanbus network?  I had an issue losing data and it was the a loose terminator.
    XW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array
  • Northern_BC
    Northern_BC Registered Users Posts: 33 ✭✭

    I have put it into standby mode to make the changes, and still no luck. I also restored all the defaults on the AGS and inverter, and still does not work. I have talked to Schneider and they are going to send me an upgrade to my firmware. Hopefully that will do it. I will post if it works.

    XW6048 inverter, EnerSys 1520 Ah battery bank, 1500 watt tracker & 7500 watt stationary solar, 10kw Baldor NG generator
  • new2PV
    new2PV Solar Expert Posts: 305 ✭✭
    what version is the firmare now?
    XW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array
  • Northern_BC
    Northern_BC Registered Users Posts: 33 ✭✭
    The firmware version is 2.07.00 BN 4. Model 865-1060.
    XW6048 inverter, EnerSys 1520 Ah battery bank, 1500 watt tracker & 7500 watt stationary solar, 10kw Baldor NG generator
  • new2PV
    new2PV Solar Expert Posts: 305 ✭✭
    Ya that is old,  I hope it works after the upgrade.
    XW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array
  • Solar2
    Solar2 Registered Users Posts: 30 ✭✭
    A couple years back I had a XW6048 that was responding strangely to menu selections.
    I finally took it down and rebooted which seemed to straighten it out.
    They have something like 30,000 ufd capacitor storage so it takes several minutes for them to drain down.
    You can short the caps out if you are in a hurry.
    If you don't like the bang short them through a heater element or something.



    18 Kw PV;  2000 AHr FLA Bat; 12 Kw Inverter;  20 Kw Kohler, LP, low speed, double muffled,   Home built, ground coupled heat pump, VFD enabled;  Leaf