Your Ideal Solar Setup

Good afternoon all,
The wife and I are looking at constructing a house in the next year or so, very preliminary stages, so specifics will be hard to come by.
My question regarding a solar system is, if you were in my position, what would your ideal setup look like? 24v? 48v? LIFEPO4 battery bank?
We would be looking at an off grid installation with our current energy usage running somewhere around the 750-850kwh/month mark. Would it be feasible to replicate that energy usage for around $30k? Am I just scratching the surface with the info that would be needed to answer this question? Please bear with me as I'm fairly new to the world of solar. 2500sqft or so house.
Thanks!
The wife and I are looking at constructing a house in the next year or so, very preliminary stages, so specifics will be hard to come by.
My question regarding a solar system is, if you were in my position, what would your ideal setup look like? 24v? 48v? LIFEPO4 battery bank?
We would be looking at an off grid installation with our current energy usage running somewhere around the 750-850kwh/month mark. Would it be feasible to replicate that energy usage for around $30k? Am I just scratching the surface with the info that would be needed to answer this question? Please bear with me as I'm fairly new to the world of solar. 2500sqft or so house.
Thanks!
Comments
http://members.sti.net/offgridsolar/
E-mail [email protected]
Thanks!
Sorry, I forgot to post the link to HomePower Mag:
http://www.homepower.com/
Just to give you some math as a starting point using "nominal" off grid rules of thumb (lead acid battery bank--We can talk about the Li-Ion battery stuff later):
- 850 kWH per month / 30 days per month = 28.3 kWH per day
- 28,300 WH per day * 1/48 volt battery bank * 1/0.85 inverter eff * 2 days of storage * 0.50 max discharge = 2,775 AH @ 48 volt battery bank
A set of forklift batteries (which can last 15-20+ years) would run around:- 2x series * 3x parallel strings Crown Industrial Battery - 24 Volts, 935 Amp-hours $4,561.00 = $27,366 @ 8,640 lbs
Next, the solar array... Two types of calculations, first based on size of battery bank: 5% to 13% rate of charge, with 10%+ for full time off grid home:- 2,775 AH * 59 volts charging * 1/0.77 panel+charge controller deratings * 0.05 rate of charge = 10,631 Watt array minimum
- 2,775 AH * 59 volts charging * 1/0.77 panel+charge controller deratings * 0.10 rate of charge = 21.263 Watt array nominal
- 2,775 AH * 59 volts charging * 1/0.77 panel+charge controller deratings * 0.13 rate of charge = 27,642 Watt array "cost effective" maximum
And based on the amount of sun you get in your area... Assuming a fixed array around Oklahoma City Oklahomahttp://solarelectricityhandbook.com/solar-irradiance.html
Oklahoma City
Measured in kWh/m2/day onto a solar panel set at a 54° angle from Vertical:Average Solar Insolation figures
(For best year-round performance)
- 28,300 WH per day * 1/0.52 off grid system eff * 1/4.79 hours of sun per day = 11,362 Watt array minimum (Oct "break even month")
So, somewhere between 11 to 21 kWatt array, or around $11,000 to $21,000 for solar array (at ~$1 per watt for solar panels)--Mounts, wiring, etc. will be a significant amount of costs too (used to be ~$1 per watt--not sure now, hopefully less).Solar Charge controllers:
- 21,000 Watts (recommended) * 1/59 volts charging * 0.77 panel+controller derating * 1/80 amps per typical controller = 3.4 ~4 controllers
4 controllers * ~$600 each = $2,400 for charge controllers.A 4-8 kWatt AC inverter-charger would run around $4,000 or so...
Backup genset around 10-20 kWatt (diesel, propane, gasoline, etc.)...
Roughly, you can see where your major costs are. The above pricing is based on US materials. You can save money on less expensive hardware in some cases (but many people come back to "brand name" products after problems with the inexpensive stuff).
Power usage is a highly personal set of choices... I am not questioning your choices--But I do suggest you look at your power needs and think "what would you do if your present utility bill went up by 10x"--Effectively what happens when you go off grid.
Also, look at the options for utility power to your property. In many cases, the value of the property and ease to sell later will be higher if there is utility power on-site already. Plus, as decades pass, utilities are charging more and more for new power connections in rural areas.
-Bill
OK, so I got a generator. I build my solar system to run lights, radio, laptop computer, small RV pump, ultra efficient fridge and freezer. No electric heat or hot water or air conditioning.
For laundry, power tools, vacuum, etc we use the generator if the sun is not shining bright. For us, the cost of avoiding the generator for a night time laundry would be a doubling of the battery bank. Of course, a larger battery needs more charging resources ... so add in the cost of a larger solar array and controller, and a larger generator. All to avoid 30 hours a year of generator use.
IMO, living off grid is all about batteries. The less battery the better. My simple 120 volt, 3500 watt Outback Inverter draws 20 watts just being turned on and doing nothing (tare loss). That's as much energy as my refrigerator uses in a day! When you get into 240 volt split phase dual inverter systems you will have higher tare losses, need bigger batteries, a 240 volt generator, and all the rest.
Watch out for defining loads. These are loads that stand out and by themselves require a larger system than would otherwise be needed. Example: Well pumps can be huge loads. I've seen quite a few systems where, except for the well pump, the system could be half the size. In those circumstances, I think it is wiser to buy a more expensive ultra efficient, low surge pump than to consign yourself to a lifetime of twice the battery.
You are wise to be working this all out in advance... do more research into ways of avoiding electrical energy use. Do some generator research. good luck
--vtMaps
The equipment now is very easy to use and living offgrid is one of the sweet things in life to me and many of the people I know.
Good Luck!
http://members.sti.net/offgridsolar/
E-mail [email protected]
TrevorDav, Keep in mind that you did ask for the "ideal setup" so they are suggesting systems like we all dream of owning.
I am the least knowledgeable of the people to reply to your thread but if you had...
6500+ watts in panels and about 1000 amp/hr in 48v batteries (a bit larger would be super nice) with a 6000+ watt inverter and 2 80 amp charge controllers. You'd be impressed at how rarely you ran the generator or the battery bank got below 50%, especially if you did laundry and dishwashing mostly on sunny days or on evenings when you knew the sun would be out the next day.
Without the items listed below assuming energy efficient devices and being a little mindful about power use two people should be able to live comfortably on 360 kw/hrs per month. That number assumes that items like a toaster oven, microwave, well pump, and occasional hair dryer stay on the solar system.
My 1700 sf home has 2 people and a deep well; we need to supplement the panels energy about 2-3 times a month this time of year (December and January) since the items listed below are either gas or on the grid, not on the solar system. We have 4500 watts in panels and a smaller (395 amp) battery bank with a 6k inverter but average 5.4 hrs sun per day here in GA. This time of year the small battery bank SOC rarely gets below 68%.
Clothes dryer, stove, water heater, and home heating would need to be off the solar system, AC would also need to be off the solar system although you could probably get away with a 9000 btu mini split or two on sunny days, especially if you added a few panels and enlarged the battery bank a bit.
Conext XW6848 with PDP, SCP, 80/600 controller, 60/150 controller and Conext battery monitor
21 SW280 panels on Schletter ground mount
48v Rolls 6CS 27P
2nd - LFP batteries are still quite young, and charge/discharge regimes are still being developed. At least 2 more years before I would make a decision.
3rd - 48V based system is going to give best performance, And a backup genset, Cloudy weather here for the last 5 days, and 10 more days forecast. Learn with a manual start genset, You will become well acquainted with load shifting to sunny days, Knowing you have to go outside to start if you want power in the AM. Auto-run systems are fine till the oil gets low, or the fuel runs out because you forgot to check it. While I run the genset, I check water levels in the batteries,
4th - Buildings. Batteries & protected electronics in one, Generator in a different one, Don't want 1 accident to take out everything
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
My takeaways thus far is 48v system is going to be the most efficient. I'm going to need a larger than 10kw solar array panel. And batteries are expensive as all get out.
It looks like to me, and many of y'all have already mentioned this, I'm going to have to get energy consumption down to AT LEAST 700 kwh if I'm going to make this even kind of feasible.
The part where I'm having the most trouble is with the battery bank. I'm just not even close to knowledgeable enough to put one together. I asked a question on another post about the Tesla Powerwall. Is the main reason it's not really feasible to use is because of the discharge rate? At least I think that's what people were saying.
Also, would the solar panel array need to be set up a certain way for the 48v system?
Again, y'all have been very helpful and I appreciate your time and effort.
You will get much more bang for the buck with flooded lead acid batteries. Lithium technologies have some advantages over lead acid, but most of the advantages won't make a difference in a large off grid system. The one off-grid advantage they do have is the ability to work at PSOC (partial state of charge) without degradation. They also have many disadvantages over flooded lead acid (cell balancing and monitoring).
How you configure your array, depends in large part on how far the array is from the controller. There are advantages to keeping your string voltage at 80-100 volts for a 48 volt system. If your array is far from your power center, then you might consider higher string voltage which requires some expensive charge controllers. Another option if your array is far from the power center is to put the power center near the array and transmit AC to the house.
One more thing... if you have the space, I recommend NOT putting the array on your roof. Do you have any electrical codes you must conform too? There are new rules, not yet adapted in all jurisdictions, that may complicate a roof top array (e.g. module level disconnect).
--vtMaps
http://zoneblue.org/cms/page.php?view=off-grid-solar
Batteries probably every 6+ years (with latest flooded cell technology.)
Cost is not always the dominant factor for everyone who decides to build an offgrid system. First conservation and then how you plan to live.
We have a friend who just sold their off grid place, and after two changes of ownership in quick sucession the latest owner, threw his hands in teh air saying "i cant stand it, sign me up for the grid."
http://zoneblue.org/cms/page.php?view=off-grid-solar
Simply a matter of privacy and preserving our majestic landscape and valuable ranching heritage.
For our way of life the grid can stay where it is.
Our electric utility bills would run over $25k in 5 years. Set of batteries in 5 years about $21k. Of course, I've got to water them 3 or for times a year. . .
http://members.sti.net/offgridsolar/
E-mail [email protected]