How to calculate / estimate how long batteries should take to charge with generator
ryan112ryan
Registered Users Posts: 11 ✭✭
I have been living off grid w/ batteries for a year and a half, but this winter we've had a few long runs with very cloudy skies. So for the first time I had to fire up my generator to bring the batteries back up to full charge. My installer told me 1-2 hours with my generator should take my batteries from 50% back up to mostly full, but I ran it for two hours and my voltage was 24.6 to 24.8 Not bad, but I was expecting more. This was what my panel was reading during the charging (http://imgur.com/X0BdbE0)
My question is, does this seem about right? How could I calculate how long it should take?
Also after finishing charging, my batteries seemed to drop voltage a bit faster than normal once I started using them with lighter than normal use, could there be something else going on? I just topped off the batteries a week ago with distilled water.
System details
My question is, does this seem about right? How could I calculate how long it should take?
Also after finishing charging, my batteries seemed to drop voltage a bit faster than normal once I started using them with lighter than normal use, could there be something else going on? I just topped off the batteries a week ago with distilled water.
System details
- (9) Canadian Solar CS-6p 250 Watt Poly Black Frame (Spec Sheet)
- (1) Schneider SW 4024 (Spec Sheet)
- (1) Schneider MPPT 60 Charge Controller (Spec Sheet)
- (8) Trojan L-16 6v 370 AH Flooded Lead Acid Batteries (Spec Sheet)
- (1) Schneider System Control Panel (Spec Sheet)
- (1) Schneider Interconnect Panel (no spec sheet)
- (1) Midnight Solar MNPV 80AMP Dinrail Breaker (Spec Sheet)
- Troy Bilt Brigs and Straton 6,250 generator Model #: 30594
- Connected to my system is 240V through a 30 amp plug
- 237V coming in from generator
- 3085 watts
- 13 amps
- image of my panel while it was charging:
<a href="http://imgur.com/X0BdbE0" target="_blank" rel="nofollow">http://imgur.com/X0BdbE0</a>
- Air temp 70 degrees F
- 24 volt system, 4 and 4 batteries in series parallel
Tagged:
Comments
-
Your battery capacity is 740 ah X 24 volts = 17760 watthours.
Subtracting loads and accounting for charger inefficiency, I would guess that you have about 2400 watts going into the battery (that means 2400 watthours every hour). 2400 watthours is 13.5% of your battery's capacity, and bulk charging tends to be very efficient, so I would expect that your SOC should rise about 13% every hour during bulk charging.
From 50% SOC, about 3.5 hours of charging should get your SOC above 90% and into absorb stage of charging.
--vtMaps
4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Measure the SG, much easier than the math....."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Your charging happens via the inverter & controlled by the SCP, which you seem to have a handle on. I don't know if the Combox would be any more useful for you or not.
But, for a 24V battery bank, I think your voltages are quite low. Full charge should be about 25.5V, and to get there, you have to drive close to 30V For 80% (Bulk only, no Absorb) at least 25V - see this chart
To understand some more about charging, this covers some of the basics
http://batteryuniversity.com/learn/article/charging_the_lead_acid_battery I think you are damaging your cells by not getting into the upper % of the charge, and could be getting some sulfation / loss of capacity.
Good luck
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
mike95490 said:Your charging happens via the inverter & controlled by the SCP, which you seem to have a handle on. I don't know if the Combox would be any more useful for you or not.
But, for a 24V battery bank, I think your voltages are quite low. Full charge should be about 25.5V, and to get there, you have to drive close to 30V For 80% (Bulk only, no Absorb) at least 25V - see this chart
To understand some more about charging, this covers some of the basics
http://batteryuniversity.com/learn/article/charging_the_lead_acid_battery I think you are damaging your cells by not getting into the upper % of the charge, and could be getting some sulfation / loss of capacity.
Good luck
Some good info in the above but the chart may be low for your specific batteries; it is for mine which are Exide 12 volt. So you will need to go to the your battery manufactures web site for your specific battery(s)
Categories
- All Categories
- 221 Forum & Website
- 129 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed