battery bank setup
This is widely considered to be the correct way to wire a 2x2 series/parallel 24v battery bank comprising 4x12v batteries.
The diagonally positioned load/charge points attempt to balance the current through each string.For your setup you can do 3 strings of 4x6v batteries connected up in a similar arrangement, but all the extra wiring and connections will probably result in some uneven distribution of current. It's unfortunately unavoidable but doesn't mean it won't give you good service. Just monitor the bank regularly and swap the batteries around a bit if you have to. Some batteries are going to be stronger than others and what you want to try and do is get and even mix of stronger and weaker batteries in each string. Should all the weaker batteries be in "string A" and all the stronger batteries be in "string C" then what you will find is "string C" doing most of the work while "string A" sits largely idle. Worst case scenario is the weaker string discharging the stronger string - but that is unlikely with relatively new batteries at a high state of charge.
Note: wires, lugs and connection points should all be identical in gauge and length. All connections must be clean to ensure the lowest possible electrical resistance.
Could i get this http://www.amazon.com/Midnite-Solar-Photovoltaic-Combiner-3-Position/dp/B004XFYV8U
Then run each string of 4 6v batteries (24v). To a breaker each. (3 breakers) and also use this http://www.amazon.com/gp/product/B000MMC914/ref=pd_lpo_sbs_dp_ss_2?pf_rd_p=1944687762&pf_rd_s=lpo-top-stripe-1&pf_rd_t=201&pf_rd_i=B00558LSJE&pf_rd_m=ATVPDKIKX0DER&pf_rd_r=0PNA922RQ2FNEF7X22VX.
Between Inverter and Combiner Box
This is the battery bank
1460 Watts Solar @24v. 675 AH Battery Bank using 12 6v Trojan T-105. 1 Midnite Classic 150. 1500 Watt 24v Samlex Pure Sine Inverter -
The bus bar in the combiner is rated too low for combining battery currents. By the way, our forum host sells that midnite combiner for much less than amazon.Zakarume said:Could i get this http://www.amazon.com/Midnite-Solar-Photovoltaic-Combiner-3-Position/dp/B004XFYV8U
As for the Blue Sea switch, you would be better off using a DC rated breaker as a switch. Read this:
http://www.amplepower.com/primer/burnt_sw/index.html
The Blue Sea switches are not safe (or UL listed) for your application, although from looking at the picture of your battery bank, I can see that safety (and following code) is not a concern of yours.
How do u add water / maintain connections with your rack systemZakarume said:Could i get this http://www.amazon.com/Midnite-Solar-Photovoltaic-Combiner-3-Position/dp/B004XFYV8U
thomOff grid since 1984. 430w of panel, 300w suresine , 4 gc batteries 12v system, Rogue mpt3024 charge controller , air breeze windmill, Mikita 2400w generator . Added 2@ 100w panel with a midnight brat