Hurricane Prep
18 Solartec 250w polycrystalline panels
Xantrex XW4024 Inverter/Charger
Conext MPPT 80-600 Charge Controller
12 Trojan L16G-AC 20 hour 390ah batteries tied in 3 strings at 1170ah total
LBCO is Low Battery Cut Off. The inverter shuts down to prevent damage to itself and the battery from running too low of voltage. Depending on programming, it may try a restart in 90 sec, or need manual restart from the SCP.
The XWnnNN series IS a combined inverter & charger
You can use a small genset with 240VAC output to power the AC2 input of the inverter, and it will gracefully divide the power between loads (first priority) and battery charging. AC2 breaker settings NEED to be set via SCP
Settings I use for my system: (2500W genset)
AC2 Breaker Size 19.5A
Generator Support Amps 13.1
Gen Sup+ : Enabled
Battery Charge rate 15% (beware, some settings are for single breaker, some for combined, and some are % of another #)
Battery bank size 1,000A (actually it's 800Ah, but 1000 is easy for daily adjustments as I load and unload the genset)
Just because you have a hot plate, in a blackout, I would NOT use it. Microwaves deliver about 60% of power to the food, hotplates are about 20%
The Combox is a better control and management unit - IF you have a computer to use with it.
Have you confirmed you XW will actually start your well pump in a no-Grid situation ? (It should easily start a 1Hp motor if it has good DC power to it)
Good Luck !
We were without utility power for a few hours one day and still had water, so yes it will power the well pump. Main priority for this potential down time will be the refrigerator and freezers, and water even though we do have bottled water. I'd rather pretend as much that we have no power at all. If it does in fact try to do the 90 second restart I'll just turn it off period. Let's hope we don't get there and I will not allow it to get to that point anyway. I'll just turn it off before we reach 21.4.5kw 24v System
12 Trojan L16G-AC 20 hour 390ah batteries tied in 3 strings at 1170ah total -
Don't run a hot plate off an inverter if you can help it. Its just such a waste of PV, inverter and battery.
Replace the hot plate with a propane camping stove. A full 20lb BBQ tank of propane will last weeks if all you use it for is cooking something in a pot or pan.
I keep 2 full BBQ bottles for a 10k-15k BTU radiant heater, camp stove and gas lamp.
A full tank will run that single burner radiant heater for 3 to 4 nights. Leaned that when out old heater died its final death back in winter 2011-2012.
Hmmm I never thought about that. If the power goes out for a while I had not even thought about making an effort to use the microwave. Here I am all ready to devolve back to cave man mode to go on heating with wood fire. I have the perfect microwave for this, my old 220 volt german microwave.Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Electricity is down the list from really being in or about a hurricane, in my opinion."we go where power lines don't" Sierra Nevada mountain area