XW6848 load shaving balancing?
I read on the Schneider website that when using load shaving they recommend for best results to keep the phases balanced. Is this something I should be looking into? Maybe install a outback balancing transforner? If anyone has more info on this please post.
XW6848 inverter with 2 X mppt 60 150 CC , with Canadian solar 260Watt panels 2 x 3.5 kw array
    I would suggest contacting Schneider directly about this question... You can put a balancing transformer on the AC input to the inverter or on the AC output--I am not sure which would be best. Done wrong, and you can have other issues (circulating currents through the XW and balancing transformer).
    Dave Angelini Solar Expert Posts: 7,081 ✭✭✭✭✭✭
    I would say this is a basic electrician skill. You always try to balance the split phase loads to keep the panel balanced. Balancing the panel has very good effects on any split phase inverter.
  • new2PV
    new2PV Solar Expert Posts: 305 ✭✭
    I called Schneider and basically they could not tell me anything about this transformer for balancing loads when on grid. Hard to balance loads when the loads are intermittent, ie. a toaster or hair dryer used at different times.
    Yea--Short term loads are a pain. And probably not worth worrying about in the big scheme of things. The cost of the balancing transformer and its losses probably will not have payback from the energy savings/efficiency (and the complexity can cause other problems too).
    But long term loads like having all the lights, the toaster oven, the hair dryers, a 120V jet pump,and a microwave on L1 and a few small loads on L2 can cause a split phase inverter to not work well on a 60 amp service like all of these are. This happens alot when someone upgrades to from a single phase battery based inverter to a split. It is a basic electrician skill that is called for anytime a panel is wired by a pro or someone who wants to do it right.
  • new2PV
    Question how much power is lost in this transformer?
  • new2PV
    12 watts is lost for idle for the psx-240 transformer.
  • new2PV
    That is 6 watts per phase.
    ion the scheme of things, that 12w loss, is nothing
  • inetdog
    Depends on your scheme. It is after all still 288wH per day. It is less than the tare of most large inverters.
    SMA SB 3000, old BP panels.
    I would say that the key to a 12 watt loss for an offgrid application, is being able to shed the loss in bad weather. It is the key to being able to live off 4 KWH per day without a generator. It is also as Mike said, "nothing" when you have the 40 KWH available.