    yes both mppt trackers are enabled
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Options
    Telecom batteries were designed for high surge and few ( less than 50 cycles) so I would expect them to fail soon in a demanding RE application
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • 96 Degrees in the shade
    96 Degrees in the shade Registered Users Posts: 23 ✭✭
    Options
    Thanks for the heads up, I am saving for some batteries so anytime I can get from those batteries I will take.Respect
  • sub3marathonman
    sub3marathonman Solar Expert Posts: 300 ✭✭✭
    Options
    Thanks for the heads up, I am saving for some batteries

    It has been mentioned by Dave Angelini that 400ah is the minimum. I don't know if they ever changed the manual, but it used to read just 100ah for the XW6048, which confused many, many people, so obviously 400ah is much better.

    But the key to the battery size is the array size. I have a 4.7kw array, and was able to get away with 357ah batteries by partially throttling the output down with the charge controllers on occasion.

    Solar Guppy, a PV expert, advised people to get 100ah / kw of array size. So for a 6kw array for 96 Degrees in the shade, it would indicate about 600ah @ 48V for the battery bank. I'm thinking that even 400ah might be a bit too small, as that is just 2/3 the size recommended by Solar Guppy. Mine was about 76% of his recommended 470ah, and I still had to be extremely watchful. I was told part of the problem with an undersized battery bank was the ripple current that would hurt smaller batteries, but it might as well be quantum mechanics for how much I can understand it.





  • BB.
    BB. Super Moderators, Administrators Posts: 33,439 admin
    Options
    More or less, a good starting rule of thumb (from Solar Guppy) is minimum of 100 AH @ 48 volt per 1 kWatt of inverter power (lead acid batteries).

    And a maximum of 1 kWatt per 100 AH @ 48 Volt battery bank solar array sizing for lead acid batteries.

    You can go into details and discuss when/why/how to vary those numbers.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Dave Angelini
    Dave Angelini Solar Expert Posts: 6,746 ✭✭✭✭✭✭
    Options
    BB. wrote: »
    More or less, a good starting rule of thumb (from Solar Guppy) is minimum of 100 AH @ 48 volt per 1 kWatt of inverter power (lead acid batteries).

    And a maximum of 1 kWatt per 100 AH @ 48 Volt battery bank solar array sizing for lead acid batteries.

    You can go into details and discuss when/why/how to vary those numbers.

    -Bill


    And it should be mentioned we are talking about the 20 hour rate at 400 AH. The Schneider XW6848 states this as all of the XW manuals have since Mr. Guppy tried to use the system with a smaller battery close to 10 years ago.