I was in a dark room and plugged in an old tool with a bad power cord into a GFCI. Seen a small, brief spark...and lost all building power.

I expected the order to be:
1) GFCI that was plugged into
2) Circuit breaker that supplied power.

No...first to cut power was my Outback Inverter. Took me a few minutes to get it going again. It acted like it was quite taken aback.
First Bank:16 180 watt Grape Solar with  FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries

Comments

  • BB.
    BB. Super Moderators, Administrators Posts: 33,613 admin
    First, your AC inverter's output protection is probably many times faster than the standard fuse or breaker (milliseconds to stop inverting vs faction of a second to minutes for a breaker/fuse to break).

    Second, GFCI only work on Hot to Earth (green wire) or Neutral to Earth shorts... Hot to Neutral looks just like an "ordinary" AC tool load (albeit with too high of current). And the GFCI will not trip in the case of a true Hot to Neutral short.

    Lastly, sometimes devices are self resetting (auto reset breakers, AC inverters that will try X times then shut down until the DC power is reset/manual reset, etc.). Manual vs Auto Reset have their advantages and disadvantages.

    Me, I carry a small flashlight (AAA or AA cell) with me.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • softdown
    softdown Solar Expert Posts: 3,896 ✭✭✭✭
    Great explanation...as usual.

    But I don't get this part: "Lastly, sometimes devices are self resetting (auto reset breakers, AC inverters that will try X times then shut down until the DC power is reset/manual reset, etc.). Manual vs Auto Reset have their advantages and disadvantages."

    Are you saying that it is likely that my inverter would have auto reset with enough time? How much time do they usually take?
    BB. wrote: »
    First, your AC inverter's output protection is probably many times faster than the standard fuse or breaker (milliseconds to stop inverting vs faction of a second to minutes for a breaker/fuse to break).

    Second, GFCI only work on Hot to Earth (green wire) or Neutral to Earth shorts... Hot to Neutral looks just like an "ordinary" AC tool load (albeit with too high of current). And the GFCI will not trip in the case of a true Hot to Neutral short.

    Lastly, sometimes devices are self resetting (auto reset breakers, AC inverters that will try X times then shut down until the DC power is reset/manual reset, etc.). Manual vs Auto Reset have their advantages and disadvantages.

    Me, I carry a small flashlight (AAA or AA cell) with me.

    -Bill

    First Bank:16 180 watt Grape Solar with  FM80 controller and 3648 Inverter....Fullriver 8D AGM solar batteries. Second Bank/MacGyver Special: 10 165(?) watt BP Solar with Renogy MPPT 40A controller/ and Xantrex C-35 PWM controller/ and Morningstar PWM controller...Cotek 24V PSW inverter....forklift and diesel locomotive batteries
  • BB.
    BB. Super Moderators, Administrators Posts: 33,613 admin
    I don't know. Try finding the programming manual and see if it has a programmable reset.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • waynefromnscanada
    waynefromnscanada Solar Expert Posts: 3,009 ✭✭✭✭
    Re "auto reset" on inverters. My Morningstar SureSine 300 inverters were designed to auto restart 3 times, after which they require a manual restart.