combiner

ws9876
ws9876 Solar Expert Posts: 448 ✭✭✭
Midnite Solar MNPV6 combiner - can you put 3 breakers AND a mndc-gfp63 inside this unit??? what about a lightning surge bulb too???

Comments

  • Vic
    Vic Solar Expert Posts: 3,208 ✭✭✭✭
    Hi ws,

    In this installation manual, the right photo on page 1 shows what I believe is this exact GFI assembly mounted in a remote Combiner:
    http://www.solar-electric.com/lib/wind-sun/GFP-install.pdf

    Yes, it is a good idea to install a high-quality Surge Protector, like the MidNite MNSPD line of protectors.

    My opinions, FWIW, Vic
    Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes.  25 KVA Polyphase Kubota diesel,  Honda Eu6500isa,  Eu3000is-es, Eu2000,  Eu1000 gensets.  Thanks Wind-Sun for this great Forum.
  • ws9876
    ws9876 Solar Expert Posts: 448 ✭✭✭
    actually what I want is a box that holds 5 mnepv breakers and a mndc gf63 and a lightning bulb. I dont think the 6 will hold all that....do you know a cheap one that will??
  • Vic
    Vic Solar Expert Posts: 3,208 ✭✭✭✭
    ws9876 wrote: »
    Midnite Solar MNPV6 combiner - can you put 3 breakers AND a mndc-gfp63 inside this unit??? what about a lightning surge bulb too???

    OK, ws,

    So, if your PV string configuration can use 150 V MNEPV breakers, how about the MNPV8 Combiner (?):
    http://www.solar-electric.com/installation-parts-and-equipment/midnite/pvarco/pspv.html

    Vic
    Off Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes.  25 KVA Polyphase Kubota diesel,  Honda Eu6500isa,  Eu3000is-es, Eu2000,  Eu1000 gensets.  Thanks Wind-Sun for this great Forum.