What the heck? Panels still making power even with canvas tarp over them
Hairfarm
Solar Expert Posts: 225 ✭✭✭
Greetings,
I covered my 6 kyocera panels with a heavy canvas painters tarp today to stop them from making voltage so I could wire them to my combiner box. After covering them then I took a voltage reading from each of the three strings and they're still showing a VOC of 39.0 VDC each pair. They are 6 Kyocera KD135GX's, each with a VOC of 22.2 VDC. More importantly, how could they still be creating any power with a canvas tarp over them?
I did this to prevent any accidental shorting while wiring them to the combiner box. With all six panels covered, shouldn't the VOC have been zero? All three strings (covered with canvas tarp) were showing me the same exact VOC that they were when uncovered. Is the sun shining through my tarp? It a heavy canvas painters tarp. Am I thinking about this wrong?
thanks.
I covered my 6 kyocera panels with a heavy canvas painters tarp today to stop them from making voltage so I could wire them to my combiner box. After covering them then I took a voltage reading from each of the three strings and they're still showing a VOC of 39.0 VDC each pair. They are 6 Kyocera KD135GX's, each with a VOC of 22.2 VDC. More importantly, how could they still be creating any power with a canvas tarp over them?
I did this to prevent any accidental shorting while wiring them to the combiner box. With all six panels covered, shouldn't the VOC have been zero? All three strings (covered with canvas tarp) were showing me the same exact VOC that they were when uncovered. Is the sun shining through my tarp? It a heavy canvas painters tarp. Am I thinking about this wrong?
thanks.
Comments
-
Needs to be totally opaque to stop all light. Black plastic sheet etc. if you can see any light thru it so will the panels. it takes very little light to get voltage, just not much or any power.GT3.8 w/4600W Trina 230W, TX5000 w/5000W ET-250W, XW4024 w/1500W ET-250W, 4 L16, 5500W Gen. (never had to use) Yet!!
-
You probably have voltage but very little amperage.Northern NM, 624 watts PV, The Kid CC, GC-2 batteries @ 24 VDC, Outback VFX3524M
-
Forget trying to cover them. Heres what i do.
- leave the mc4s between the first panel in each string disconnected.
- Wire everything up, combiners, disconnect circuit protection.
- Make sure you have breakers in teh combiner, that way in future you will be able to isolate the pv hot from teh disconnect should you need to do additional work on it (which you will).
Once everything is good to go, with the dv breaker in the disco off, clip the remaining mc4s. Engage the breaker, voilà.
If you have voided your warranty and cut off the mc4s, then well, so long as you only hold one of the array wires at once, you should be ok
1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
http://zoneblue.org/cms/page.php?view=off-grid-solar -
Thanks for the suggestions. A Kyocera tech told me that VOC is even possible during a full moon and that if I had a tarp in daylight there would be still be a VOC reading on my multimeter but very little amperage, as Mountian Don said. The tech suggested using gloves and wire caps. I also like the idea of not connecting the mc4's too. Never thought of that.
thanks, -
Just only connect mc4s when you have no load on the line, else youll damage the silver plating.1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
http://zoneblue.org/cms/page.php?view=off-grid-solar -
Industry SOP is supposed to be to cover panels when working on the wiring, but SEIA lab I think it was did some testing and found that even really good tarps leave enough illumination to cause lethal voltages on high-voltage arrays. We still have the "cover array" note on our drawings to satisfy the ignorant authorities, but we always leave a break in the chain like zoneblue says to prevent shocks.
-
Like others I wired the array, but left the MC4 from the positive + side disconnected and the breakers off in the combiner box. After it was all wired up, I connected the positive side MC4 of the array, went over to the combiner box and turned on the breakers one at a time.
-
I suspect the cover the panels thing originated long ago when panels were expensive and hence small. Now, who the heck can lay there hands on a decent tarp the size of our arrays?1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
http://zoneblue.org/cms/page.php?view=off-grid-solar -
I just wired my array and combiner box and flipped the breaker ahead of the charge controller the next morning... Though the breaker would handle the load.
Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 622 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed