wire sizing issues
Shawn-H
Solar Expert Posts: 107 ✭✭
my well is 350 feet from my inverters. the well is another 300 feet deep the wire leading to the well pump from the cap is 8 gauge. what size wire do I need to run from my inverters to my well. the well pump is a two horse 240v 2000w run 7500w spike.
100% Off-grid in the White Mountains of Arizona. 36 Kyocera 265w mounted on four DPW 9 module pole top mounts, midnite solar combiners, breakers, & lightning arresters, 1 midnight solar classic 150, & 3 classic 150 lights, 3 x 1574 AH GB Industries forklift batteries total of 4722 AH @24v. Feeding a Outback power systems FW500 with 2 x VFX 3624, with the x240. 2 Honda EU3000is gensets with the 240 combiner and control box running LP, and 1 Honda EU2000is Gas.
System #2 is a off grid water system @ 1590w (6 Kyocera 265's) on a 6 module DPW top of pole mount. Feeding a Granfas deep well pump and pump controller at 580 feet. 2 x 2800 gallon above ground poly storage tanks, and 1 x 1200 gallon underground cistern and a Granfas 24v booster pump feeding a 90 gallon carbon fiber pressure tank.
Vag woodstove for heat.
Follow our journey at
https://www.facebook.com/ShawnpHarvey
System #2 is a off grid water system @ 1590w (6 Kyocera 265's) on a 6 module DPW top of pole mount. Feeding a Granfas deep well pump and pump controller at 580 feet. 2 x 2800 gallon above ground poly storage tanks, and 1 x 1200 gallon underground cistern and a Granfas 24v booster pump feeding a 90 gallon carbon fiber pressure tank.
Vag woodstove for heat.
Follow our journey at
https://www.facebook.com/ShawnpHarvey
Comments
-
Shawn, I will give it a shot--But this is something you may need to talk with a well person/licensed electrician (familiar with well installations) about.
First, the needs of the motor. AC power is actually quite complex in its application to induction motors (vector math, inductors/capacitors, etc.). But the basics work out like this.- 2 HP * ~746 Watts per HP = 1,492 Watts of power
- 1,492 Watts / 2,000 Watts = 0.746 ~ 75% efficiency (seems reasonable).
Next, is another set of "losses". With AC power, the Voltage Sine Wave is not always "in phase" with the Current Sine Wave... For induction motors, the current wave "lags" the voltage sine wave... The end result is that the motor "Takes more current" to run than you would expect from the "simple" power equation:- 2,000 Watts / 240 VAC = 8.33 Amps (@ 240 VAC).
For induction motors, this can be talked about as VA (Volt Amps) -- The amount of current and voltage needed to make the motor run at full output power--And you need to size the wiring, transformers, AC inverter, etc. to this required current flow.
For a typical induction motor, roughly the Cos (phase angle) = ~0.70 (~70% of the current is used to turn the motor, the other 30% is "wasted" doing nothing other than pulling more current in the wiring).
If you motor is a 2,000 Watt input, then its "VA" rating would be (roughly):- 2,000 Watts / 0.70 = 2,857 VA
- 2,857 VA / 240 VAC = 11.9 Amps
Now, lets say you want a 3% maximum voltage drop (240 VAC * 3% = 7.2 volt drop) when running (you may need to run 5% drop--We will see what the math looks like):- 7.2 volt drop, 11.9 amps, 650 feet
- http://www.calculator.net/voltage-drop-calculator.html
Voltage drop: 6.11
Voltage drop percentage: 2.55%
Voltage at the end: 233.89
So, a 650 foot 6 AWG copper cable wire run would seem to be a good starting point.
If you cannot fit 6 AWG down to the pump, perhaps you use a smaller AWG in the well, and a larger AWG from the house to the well.
In your cause 300 feet of 8 AWG in well:
Voltage drop: 4.49
Voltage drop percentage: 1.87%
Voltage at the end: 235.51
and that leaves 7.2 volts - 4.5 volt 8 awg drop = 2.7 volt drop for the 350 foot run:
4 AWG (350 foot from inverter to well):
Voltage drop: 2.07
Voltage drop percentage: 0.86%
Voltage at the end: 237.93
I have to go right now--But that is where I would start.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Shawn, I will give it a shot--But this is something you may need to talk with a well person/licensed electrician (familiar with well installations) about.
First, the needs of the motor. AC power is actually quite complex in its application to induction motors (vector math, inductors/capacitors, etc.). But the basics work out like this.- 2 HP * ~746 Watts per HP = 1,492 Watts of power
- 1,492 Watts / 2,000 Watts = 0.746 ~ 75% efficiency (seems reasonable).
Next, is another set of "losses". With AC power, the Voltage Sine Wave is not always "in phase" with the Current Sine Wave... For induction motors, the current wave "lags" the voltage sine wave... The end result is that the motor "Takes more current" to run than you would expect from the "simple" power equation:- 2,000 Watts / 240 VAC = 8.33 Amps (@ 240 VAC).
For induction motors, this can be talked about as VA (Volt Amps) -- The amount of current and voltage needed to make the motor run at full output power--And you need to size the wiring, transformers, AC inverter, etc. to this required current flow.
For a typical induction motor, roughly the Cos (phase angle) = ~0.70 (~70% of the current is used to turn the motor, the other 30% is "wasted" doing nothing other than pulling more current in the wiring).
If you motor is a 2,000 Watt input, then its "VA" rating would be (roughly):- 2,000 Watts / 0.70 = 2,857 VA
- 2,857 VA / 240 VAC = 11.9 Amps
Now, lets say you want a 3% maximum voltage drop (240 VAC * 3% = 7.2 volt drop) when running (you may need to run 5% drop--We will see what the math looks like):- 7.2 volt drop, 11.9 amps, 650 feet
- http://www.calculator.net/voltage-drop-calculator.html
Voltage drop: 6.11
Voltage drop percentage: 2.55%
Voltage at the end: 233.89
So, a 650 foot 6 AWG copper cable wire run would seem to be a good starting point.
If you cannot fit 6 AWG down to the pump, perhaps you use a smaller AWG in the well, and a larger AWG from the house to the well.
In your cause 300 feet of 8 AWG in well:
Voltage drop: 4.49
Voltage drop percentage: 1.87%
Voltage at the end: 235.51
and that leaves 7.2 volts - 4.5 volt 8 awg drop = 2.7 volt drop for the 350 foot run:
4 AWG (350 foot from inverter to well):
Voltage drop: 2.07
Voltage drop percentage: 0.86%
Voltage at the end: 237.93
I have to go right now--But that is where I would start.
-Bill
Thank you bill I did talk to the well company that put in the pump back in 1992 and they told me 6AWG would do it. I would just rather a second opinion if you know what I mean. expecially since that sounds too small for me I did the same Math as you and think it should be 4 AWG or larger expecially since I would rather not change out the wire that is already in the well.
again thank you for the info and taking the time to give the reply.100% Off-grid in the White Mountains of Arizona. 36 Kyocera 265w mounted on four DPW 9 module pole top mounts, midnite solar combiners, breakers, & lightning arresters, 1 midnight solar classic 150, & 3 classic 150 lights, 3 x 1574 AH GB Industries forklift batteries total of 4722 AH @24v. Feeding a Outback power systems FW500 with 2 x VFX 3624, with the x240. 2 Honda EU3000is gensets with the 240 combiner and control box running LP, and 1 Honda EU2000is Gas.
System #2 is a off grid water system @ 1590w (6 Kyocera 265's) on a 6 module DPW top of pole mount. Feeding a Granfas deep well pump and pump controller at 580 feet. 2 x 2800 gallon above ground poly storage tanks, and 1 x 1200 gallon underground cistern and a Granfas 24v booster pump feeding a 90 gallon carbon fiber pressure tank.
Vag woodstove for heat.
Follow our journey at
https://www.facebook.com/ShawnpHarvey -
Not a bad stab BB, the only way to get it closer would be pull the pump and hope the pf is stamped on the name plate data.
-
I suspect your 2Kw consumption estimate. But maybe with a larger motor, you have less overall losses. My 240VAC 1/2 hp pump logs 1Kw consumption, which includes the poor power factor of the average pump motor. I have about 300' of 6ga from the inverter to the controller, and then 100' #10 submarine cable from there to the pump.
It may be worthwhile to have an electrictian use a peak reading meter to get your accurate starting amps. because your transformer has a hard limit of what it can pass till the core shuts down on you. You can have all the power in the world, but an undersize transformer will not let it start.
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
It may be worthwhile to have an electrictian use a peak reading meter to get your accurate starting amps. because your transformer has a hard limit of what it can pass till the core shuts down on you. You can have all the power in the world, but an undersize transformer will not let it start.
All that happens when you draw excess current from a transformer is that the resistance of the primary and secondary winding cause the voltage to drop and the temperature of the transformer core to increase. In the short term heating is not an issue, and in the event of a short circuit the short circuit current is determined by the available POCO current at the primary and the impedance of the transformer windings. The secondary current will be modified from the POCO available current by the turns ratio of the transformer.
SMA SB 3000, old BP panels.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed