72 volt systems?
khotton
Solar Expert Posts: 38 ✭
It seems to me that with the high cost of copper, that there would be a move to higher voltage "off-grid" systems. Currently, the top voltage is 48VDC. I am hoping that systems will move up to 72VDC. Do the experts on this forum have any insight into this? An additional advantange to this higher voltage system is that many "NEV's" neighborhood electric vehicles - could be directly charged with a charge controler for a 72VDC system.
Thanks,
Kevin
Thanks,
Kevin
Comments
-
Re: 72 volt systems?
Above 50V, is the magic realm of "high voltage" and I think something in the NEC makes it non-trival to make a "hi-voltage" battery bank, where a 48 volt bank is just fine. Your mileage may varyPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: 72 volt systems?
it seems to me that if all you are doing is charging an ev then do it as the nec won't worry about it much and the only batteries involved are in the ev. the mx60 controller could handle this 72vdc output, but the input is a bit trickier. i don't know the current max if it has changed at all, but i believe it was around 125vdc for the cutoff. jim, would you verify this? -
Re: 72 volt systems?
I think the mx60 is 140 vdc but the problem is going above the 48 volt nominal battery bank oppens a huge can of worms within the NEC -
Re: 72 volt systems?
"72 V" systems are problematic. Worst case, using 14.4 V / 15.5 V to charge /equalize a "12 V" battery as a reference, ~93 V would be required to equalize a flooded-cell bank. Allowing for losses due to hot ambient temperatures, cabling loss, and converter loss, a target STC Vmp would be ~93 V / 85% = ~109 Vmp. Since Vmp is ~80% of Voc, STC Voc would be ~136 V.
The operational limit for the MX60 is 141 Voc, and it's 140 Voc for the T-80. The small difference between 136 V and 140 V leaves no room for the NEC's ambient temperature voltage correction factors, so a "72 V" system is therefore not practical with present products. In fact, even a "60 V" system can be difficult to spec.
HTH,
Jim / crewzer
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed