AGM Battery Exercise

stmar
Solar Expert Posts: 373 ✭✭✭
What should you do with a new AGM battery bank? I have had mine in place for a few months now, we have had a few grid outages from a few minutes to a few hours. System is functioning properly as far as I can tell. During a sunny day the bank gets up to the 28 volt range and at night it is in Float at 26.8. Is the fluctuation in charging enough or should I be doing additional exercises?
Comments
-
Re: AGM Battery Exercise
it needs to go to float during the daytime as there's no sun at night. should i ask? -
Re: AGM Battery Exerciseit needs to go to float during the daytime as there's no sun at night. should i ask?
I guess I don't understand. It goes to Float at night because it is on grid and the grid charges it as needed to keep it to 26.8 volts. It is functioning properly as far as I can tell. My question is should I be doing anything different or is the solar array charging it during the day to a higher voltage and then having it drop to Float at night good enough exercise for the new battery bank to get it to it's full potential? -
Re: AGM Battery Exercise
Exercise the battery bank with a 25% or so discharge once per month... If it is a critical application, run it once a month (or at least several times a year) as much as you expect it to supply in a true power outage. If it cannot support your needs, it needs replacing.
Floating a battery for several years (unless it was designed for float service)--It is (probably) not going to last as long, and if/when you need it, you might find it only has 1/4 or less of its capacity.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: AGM Battery Exercise
Thanks, that is what I was looking for. I think with our grid outages it discharged and recovered a few cycles since I installed them. How do you know when you get to 25% discharge? Is there a formula that you use or a value displayed on the inverter's meter? These are Lifeline AGMs and my Xantrex has readouts for most critical elements. -
Re: AGM Battery Exercise
Assuming 4x6 volt @ 400 Amp*Hour capacity for a 24 volt @ 400 AH battery bank...
If you can measure current, then you want to discharge ~100 Amp*Hours for 25% discharge...
That can be:- 100 AH / 5 hours = 20 amp rate
- 100 AH / 10 hours = 10 amp rate
- 100 AH * 24 volts = ~2,400 Watt*Hours capacity
- 2,400 WH * 0.85 inverter eff = 2,040 WH for 1/4 or 25% battery discharge of 120 VAC loading
- 2,040 WH / 5 hours = 425 Watt AC load for ~5 hours
- 2,040 WH / 10 hours = 204 Watt AC load for ~10 hours
The above are very gentle discharge rates. AGMs can take higher discharge rates--But I would avoid going much more than C/5 just to keep things from getting crazy. They should be able to discharge (if I recall correctly) as fast as C*4 rate (discharge bank 100% to 0% in 15 minutes)--But that would be very stressful and could severely damage the battery bank.
In the end, if you have a common set of loads you want to support--Measure those and then plug them back into one of the equations above.
I.e., if you need 500 Watt average load:- 2,040 WH (25% of battery capacity to discharge) / 500 watt AC load = 4.08 hour of run time minimum
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: AGM Battery Exercise
I would check with your battery manufacturer. For my Odyssey AGMs- they are designed for a 15 yr float life. That said - me thinks there is no harm in occasional exercise! -
Re: AGM Battery Exercise
So if I get my load to about 4 amps AC, that would be 480 watts give or take. On the DC side I have a 24 volt frige so will have to take that into consideration. Of course the 4 amps AC load will not be constant. I think I can do that with no problem so thanks again for the input.
I do think the Lifelines (hence their name) are designed for float so that they will be ready for emergencies, that being said I agree with you that exercise is good and should make them even better.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2.1K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 652 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 612 Discussion Forums/Café
- 305 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed