AGM Battery Exercise
stmar
stmar Solar Expert Posts: 373 ✭✭✭
What should you do with a new AGM battery bank? I have had mine in place for a few months now, we have had a few grid outages from a few minutes to a few hours. System is functioning properly as far as I can tell. During a sunny day the bank gets up to the 28 volt range and at night it is in Float at 26.8. Is the fluctuation in charging enough or should I be doing additional exercises?
    Re: AGM Battery Exercise
    it needs to go to float during the daytime as there's no sun at night. should i ask?
  • stmar
    niel wrote: »
    I guess I don't understand. It goes to Float at night because it is on grid and the grid charges it as needed to keep it to 26.8 volts. It is functioning properly as far as I can tell. My question is should I be doing anything different or is the solar array charging it during the day to a higher voltage and then having it drop to Float at night good enough exercise for the new battery bank to get it to it's full potential?
    BB. Super Moderators, Administrators Posts: 33,734 admin
    Exercise the battery bank with a 25% or so discharge once per month... If it is a critical application, run it once a month (or at least several times a year) as much as you expect it to supply in a true power outage. If it cannot support your needs, it needs replacing.
    Floating a battery for several years (unless it was designed for float service)--It is (probably) not going to last as long, and if/when you need it, you might find it only has 1/4 or less of its capacity.
  • stmar
    Thanks, that is what I was looking for. I think with our grid outages it discharged and recovered a few cycles since I installed them. How do you know when you get to 25% discharge? Is there a formula that you use or a value displayed on the inverter's meter? These are Lifeline AGMs and my Xantrex has readouts for most critical elements.
    Assuming 4x6 volt @ 400 Amp*Hour capacity for a 24 volt @ 400 AH battery bank...
    If you can measure current, then you want to discharge ~100 Amp*Hours for 25% discharge...
    That can be:
    • 100 AH / 5 hours = 20 amp rate
    • 100 AH / 10 hours = 10 amp rate
    Or for AC loads:
    • 100 AH * 24 volts = ~2,400 Watt*Hours capacity
    • 2,400 WH * 0.85 inverter eff = 2,040 WH for 1/4 or 25% battery discharge of 120 VAC loading
    • 2,040 WH / 5 hours = 425 Watt AC load for ~5 hours
    • 2,040 WH / 10 hours = 204 Watt AC load for ~10 hours
    Some examples....
    The above are very gentle discharge rates. AGMs can take higher discharge rates--But I would avoid going much more than C/5 just to keep things from getting crazy. They should be able to discharge (if I recall correctly) as fast as C*4 rate (discharge bank 100% to 0% in 15 minutes)--But that would be very stressful and could severely damage the battery bank.
    In the end, if you have a common set of loads you want to support--Measure those and then plug them back into one of the equations above.
    I.e., if you need 500 Watt average load:
    • 2,040 WH (25% of battery capacity to discharge) / 500 watt AC load = 4.08 hour of run time minimum
    The backup system is only good for you--If it supports your needed loads (plus a bit for aging/emergency use).
  • mtdoc
    mtdoc Solar Expert Posts: 600 ✭✭
    I would check with your battery manufacturer. For my Odyssey AGMs- they are designed for a 15 yr float life. That said - me thinks there is no harm in occasional exercise!
  • stmar
    So if I get my load to about 4 amps AC, that would be 480 watts give or take. On the DC side I have a 24 volt frige so will have to take that into consideration. Of course the 4 amps AC load will not be constant. I think I can do that with no problem so thanks again for the input.
    I do think the Lifelines (hence their name) are designed for float so that they will be ready for emergencies, that being said I agree with you that exercise is good and should make them even better.