Equal lengths of wire ?
King-01
Registered Users Posts: 28 ✭
All,
Must the positive and negative wiring be of equal length for a circuit? Reason I ask is the connection from my buss bar negative is going to be 12" longer than the buss bar positive. If this is a problem, would I be better served finding a place to have the extra 12" of positive in order to make the circuits equal length? Voltage is 13.2, amperage load is 60, 4/0 gauge wire running 90 feet. Thanks.
Re: Equal lengths of wire ?
No, the wires do not have to be of equal length.
That matters when a circuit is branched in parallel as in connecting two battery strings; you are trying to keep the resistance in the two parallel lines equal so that they will share current evenly.
Otherwise it is merely a loop and the current is even throughout: it does not matter where in the loop the power source or load demand is located. -
Many thanks, Cariboocoot