Right Panels for RV Application
TaoJones
TaoJones Registered Users Posts: 18 ✭✭
I'm going to add solar charging to my 27' travel trailer so that I can do extensive boondocking starting next fall. I've been educating myself about adding solar online, mainly by reading HandyBob's website and accepting the wisdom of his point-of-view.
I'd like to use Bogart Engineering's TriMetric monitor and their new SC-2030 charge controller in either a 12v or 24v system. I've been advised to use a Magnum inverter/charger, but when it comes to panels I'm at a loss. NAWS has the Kyocera KD250GX-LFB2 250w panels at an attractive price, but I'm told that I would need an MPPT controller if I select those panels.
This would preclude the use of the Bogart PWM charge controller and the claimed synergistic effects of the Bogart charge controller and their TriMetric monitor working together in a single system. I don't understand why an MPPT charge controller is necessary with the above panel, as Bogart's site indicates, "The SC-2030 is designed for use with a 12V panel (36 cells) and a 12V battery, or a 24V panel (72 cells) and a 24V battery with efficiency comparable to that of MPPT charge controllers, but without the high cost of MPPT. The charger can handle solar currents up to 30A, and is ideally suited for RV and other small off-grid applications."
The specs on the Kyocera 250w panel show a Vmp of 29.8 volts and an Imp of 8.39 amps. Can someone help me understand why the SC-2030 can't work with that Kyocera panel, please? The alternative panel, I'm told, is Kyocera's KD140SX-UFBS, but where the 250w panel is just under $250, the 140w panel is a whopping $285! And the suggested MidNite Solar Classic 150 MPPT controller is $610 while the Bogart SC-2030 charge controller is only $122.
Thanks for any help you can provide.
TaoJones
    Re: Right Panels for RV Application
    It has to do with the charging voltage, a panels with a VMP of 29.8 volts will loose some of that while 'getting to' the batteries, through the wiring and the charge controller. even if it could deliver 29.8 volts, it would only do this in idea situations. If you check the Spec sheet You can note that the NOCT values (Normal Operating Cell Temperature) for the panel include a VMP of 26.8volts.
    If you have a 24 volt system, you will need to present to the batteries a voltage a bit above 29 volts during normal charging and around 31 volts to equalize the cells.
    Adding to Photowhit's post:
    For a 12 volt bank, you need around Vmp~17.5 to 19.0 volts array (STC--Standard Test Conditions) for optimum 12 volt battery bank charging with a PWM controller (also minimum voltage for a MPPT type charge controller).
    For a 24 volt bank, you need around 35-39 volts Vmp-array for a 12 volt lead acid battery bank (again minimum voltage for MPPT charge controller).
    You are seeing the tradeoffs between "cheap" PWM controllers and "expensive" 17.5 volt Vmp panels vs "expensive" MPPT controllers with "cheap" GT Solar panels.
    Some interesting MPPT controllers:
    MidNite Solar Classic 150 MPPT Charge Controller (80+ amp)
    MidNite Solar The Kid MPPT Solar Charge Controller (30 amp)
    MPT-3048 MPPT PV Charge Controller 30A - 12/24/36/48v
    Morningstar Advanced MPPT Charge Controllers (15-60 amp controllers)
    All are very nice controllers. The Midnite are working on an integrated Battery Monitor system--Battery Charging current parametric control with the integrated remote shunt monitor option.
    MidNite Solar Whiz Bang Jr Current Sense Module
    Lots of neat equipment to choose from. Depends on what you are looking for (size, options, data logging, etc.). Usually recommend getting the remote battery temperature sensor for any of the above controllers.
    Do a couple of paper designs and see what works out best for you.
    In general, MPPT controllers are really nice if you are going to use the less expensive GT type solar panels. They "match" the high voltage/low current of the panels and efficiently down convert to the low voltage/high current needed by the battery bank.
    If you have long wire run runs from the Array to the solar battery controller/charger, then MPPT can be very nice. Run Vmp array at 60-100 VDC (smaller wires needed). However, if your wire runs are short, then MPPT is really not a big savings (charge controller should always be near the battery bank).
    Do you have an AH rating (12/24 volt) and solar array Wattage estimate for your system yet?
    If you will be traveling up north during the winter months--A tilting array may be worth the hassles to catch the low angle winter sun.
  • Iceni John
    Iceni John Solar Expert Posts: 103 ✭✭
    You will get the most watts for the dollar by using big Grid-Tie panels that are typically about 30V, but for a 12V system you'll waste more power using a PWM controller than a MPPT. If you're planning a larger system, the benefits of MPPT outweigh the lower initial cost of PWM. Because nobody has ever complained about having too much solar power (or too much anything else) in an RV, I suggest covering the roof with as many GT panels as will fit without being shaded, get a good high-output MPPT controller, and have enough batteries to last for two or three days. Do it right, and you won't need a generator except for emergencies.
    Making a tilting mechanism for the panels is more useful the further north you go, especially in winter. However, don't underestimate the strength of desert winds, and make the panels easily and safely accessible for cleaning and maintenance. You're only doing this once, so do it right the first time, otherwise you'll be forever dinking around with upgrades and piecemeal changes as your needs outstrip your system's limitations. I'm building a 2kW system on my bus, using eight Sharp 255W panels hinged to a central walkway on my roof, and they'll feed two Morningstar 60A MPPT controllers and eight batteries. Devising a simple yet robust mechanism to raise the panels up to 50 degrees from horizontal is turning out to be the most challenging part of this project so far, but I've done crazier things so far for the rest of the conversion!
    Have fun, John
    40' Crown bus with 2kW of tiltable panels on the roof:
    Eight Sharp 255W, two Morningstar TS-MPPT-60, Magnum MS2000, Champion C46540 generator converted to propane, eight golfcart batteries, and maybe a small Exeltech inverter for the fridger.
    Southern California
  • TaoJones
    @Photowhit, Bill & John: Thank you all for the input . . . now I have even more to read and think about. :confused:
    On my 27' travel trailer, I have a wide-open space from the A/C cover forward that is approximately 8' wide x 9'8" long. Of course, I wouldn't want to use all of that space for PV panels and lose all walking space. I was originally thinking that three of the Kyocera 250w panels laid out edge-to-edge could cover ~5'6" x 9'9", but it forces the last panel right up to the A/C cover and/or over the front of the coach, slightly.
    Alternatively, I'd mount the panels parallel to the long dimension of the coach with the walkway up the middle. With just two panels, there would be no possibility of shading from the A/C cover. If I added panels three and four, however, it would become an issue with at least one of the panels, some of the time.
    I do intend to incorporate a tilting option into the build, but I do understand the concern with potentially high desert winds. It seems logical to have this option, though, as long as it's well-engineered and constructed.
    I spend summers in Colorado and winters in Arizona. If I do travel further north, it would only be during the summer. I was born and raised in Colorado and my enthusiasm for winter left me many years ago, so there's little prospect that I would ever venture north of, say, 35°N latitude. :cool:
    It seems I'll need to give up on the idea of using both a TriMetric monitor and a matching SC-2030 charge controller. That's OK, though, since I'm way too green at all this to be making hard and fast selections of equipment at this stage. Bill, I appreciate the links you provided to the various MPPT controllers. I'll do my best to read and retain as much of it as I can. I did look at the Rogue MPT-3048 you seemed to highlight and I'm impressed with what I've read so far.
    Since the solar panels will be mounted on the forward or "tongue-end" of the roof and the batteries will be located on the tongue, the separation is less than 10'. I was thinking of locating the charge controller in the pass-through bay that's at the very front of the coach (so less than two feet from the batteries). And I understand about using the appropriate wire gauge to minimize line loss.
    In that regard, however, I'm unclear on best location for the inverter/charger. Like most RVs, the shore power cord is located at the rear of the coach on the driver's side. The panel is on the other side of the coach, under the stove/oven, so it's about 18' from where the batteries and charge controller will be. I was considering locating the inverter/charger in the same storage bay at the front of the coach adjacent to the charge controller, shunt, etc. and running the wire from the inverter under the floor/frame through PVC conduit, then back up through the floor into the space under the stove where the present panel is located.
    I don't have an AH rating and wattage estimate yet, Bill, and while I know this will probably sound bass-ackwards, I intend to install a system that will generate the greatest amount of power for the most effective allocation of $, then adapt my off-grid lifestyle to the power available. For example, the laptop I use is on almost constantly and I display it on a 32" TV, but I intend to replace both before I go boondocking with an iPad mini. That represents a huge difference in power demand. And by changing the refrigerator and water heater to propane and dispensing with the microwave altogether, there's almost nothing else that requires power . . . but I want to have a respectable amount available anyway, just because. I also carry a Honda 1000w gas-fueled generator that I hope to never need.
    Again, I appreciate the input you've all been kind enough to post. I'm learning as quickly as I can, and I hope you'll bear with me as I get up to speed.
    TJ
    The Rogue has been a very good performing controller, and Marc (the owner of Rogue) has been posting here in the past (not recently? He has been pretty busy). I did not intend to highlight Rogue specifically--the was an editing goof on my part (dinner was just about ready).
    Read about the controllers and see which one "speaks" to you. The ones I linked to were models (and Mfg.) that had smaller MPPT charge controllers. There are others (like Outback) that have good product too.
    Pretty much, the battery bank will be the heart of your power system. It is is too small to support your loads, battery will die soon. If it is too large to be effectively charged by your solar array, you will be running the Honda more and/or, again, your batteries will have a short life.
    I really like to have a system that is "well balanced"--For the most part, that means it will perform well and have reasonable life and maintenance costs.
    Lead Acid batteries are sort of a necessary evil... Some Lithium battery chemisteries are starting to look very interesting and even cost competitive over the life of the batteries--Plus they weigh a whole bunch less.
    Anyway--Here you are and where do you go next. Since your loads are unknown--Some suggestions. No one right answer, but they will help you gauge your power needs/system capabilities.
    1) Know your loads--But it is hard to start from scratch
    2) Estimate your needs--]
    • 500 WH per day will power a low power laptop, lights, cell charger.
    • 1,000 kWH per day will power a laptop, electronics, DC water pump, etc. (LED TVs are pretty good these days)
    • 3,300 Watt*Hours per day will power a very energy efficient home with a refrigerator, well pump, electronics+lights, washing machine (probably way more power than you will need).
    3) How big of battery bank will you dedicate to your solar power. Battery bank helps size solar array/backup generator power needs and how long you can run without sun (1-2 days, 50% maximum discharge).
    4) How big of solar array will size the battery bank and loads that can be supported.
    So--Try and estimate each piece and see where your exceptions do not make sense (can't carry much in battery bank, then a huge solar array is not going to help much. Can't put much solar panels on RV, then a large battery bank is not going to work well unless you start burning more fuel for your Honda, etc.).
    Much of your daily power needs is going to be a laptop, lights, cell charger, DC water pump. You can get a Kill-a-Watt type meter and measure the first 3 loads at home, and estimate the water pumping needs (10-20 gallons per day?). You will come up with some pretty good numbers. The other stuff (propane refrigerator--you can estimate the control board power requirements).
    Space heater may be an issue--Many RV space heaters use a fan to operate the unit and run a fan to move air around. These "central heat type" RV heating units actually take a surprising amount of power. They may take 8 amps to run, and if you have poor insulation (common RV issue), you may see the thing running 50% duty cycle overnight/during the day... Say 6 hours * 8 amps = 48 AH of battery capacity. Not a small load on an RV system.
    Anyway, try approaching the solar power system from multiple angles (power needs, solar panel wattage, battery bank AH capacity, etc.) and see if they all meet in the middle--Or not. :p
    Please note that the rating for the charge controllers(CC) is for the output, so a 30 amp CC would be clipping a bit on 3 panels in a 12 volt system, even at NOCT values, 180 watts x 3 = 540watts/12v=45 amps.
  • rich
    rich Solar Expert Posts: 62 ✭✭✭✭
    Just thought about throwing in my 2 cent solution to tilt, I simply will be using hinges on-top of my z mounts that hinge them up in the landscape orientation..this plan came about after several prototype tilting frames ...they were all in my opinion far to heavy....anyway, hope that helps.
  • TaoJones
    rich wrote: »
    Thanks for your post, Rich. I've thought about how I want to mount the panels to incorporate the tilting option and I'm inclined to do it in a way that will allow me to tilt them in opposite directions. What I mean by that is I don't want to have to always face the rig in the same direction (typically east, so that the door is on the north side) to tilt the panels to the south, because there will undoubtedly be those times where that isn't possible. On those occasions when the rig is pointed west, I'd still like the option of tilting the panels to the south.
    I don't think this is a difficult problem to solve, though. As I see it, it will just be a matter of using different length flat metal arms on the north side of the panels to achieve the optimum tilt for the location and time of year, regardless of whether the rig faces east or west. Any other orientation would seem to dictate leaving the panels flat.
    The thing I'm struggling with is the advisability of ganging the panels together into a single panel-mounting frame. The likelihood of occasionally high desert winds threatening the panels, mentioned earlier in this thread, is real - and it seems logical that mounting the panels into a "uni-frame" structure would probably compound the danger.
    It's something I don't need to decide on right away, though, and I hope to get more information before a decision has to be made. Exactly how the panels are laid out on the RV's roof will have a lot to do with it, of course.
    TaoJones
  • TaoJones
    Photowhit wrote: »
    Thanks for your post, Photowhit. I understand what you're saying - the Bogart Engineering charge controller would be inadequate in those circumstances.
    On another point, I recently watched a YouTube series posted by Steve Robertson on Solar Design Considerations that it's better to install a 24v system than a 12v system, and a 48v system is better yet, but I am admittedly still a bit hazy on the concept and it may not even be applicable to an RV installation. If you could help me gain some clarity on this, I'd appreciate it. Or if, in your opinion, it just isn't true, I'd like to know why.
    I had come at this with the idea that I wanted to install the simplest, most cost-effective system I could. To me, that meant a 12v system with perhaps 500 or 600 watts of solar panels, a pair of 6v Crown golf cart batteries, a TriMetric monitor and matching SC-2030 charge controller, an appropriately-sized inverter or inverter/charger, 500amp/50mv shunt and all of the associated, properly-sized wiring, etc. to put it together myself, but I was never clear on which panels would best "fit" such a system.
    Then I saw Robertson's video on the preference of a 24v system over a 12v system and I'm more confused now than I was a few days ago. It's part of climbing the learning curve, of course, but I'm struggling to understand it all.
    TaoJones
    It depends on your loads and charging current. If your system is running 300 watt ac inverter, I would be very happy at 12 volts for a typical system.
    TaoJones wrote: »
    In essence the panel system operates on the amp running through it, Amps x Volts = Watts, so if you have a 30 amp Charge Controller, It will handle a (12v x 30 amps = ) 360 watt array in 12 volt system voltage, or a (24 x 30 =) 720watt array in a 24 volt system or a 1440 watt array in a 48 volt system. Same charge controller...different system voltages. Hope this helps.
    Another efficiency comes from wire heating:
    Power = I2R for self heating
    And P = I * V
    If you double V (12 to 24 volts), then current falls by 1/2.
    In the self heating equation, with the same resistance, 1/2x the current gives you 1/4x the self heating losses.... Or you can reduce the wire diameter by 1/4 for a 24 volt system (that turns out to be 6 AWG sizes) and you will get the same self heating as the heavier wire at 12 volts.
    There are other losses too... The higher the working voltage, the more stray capacitance losses you get from switching FETs (field effect transistors). So for a 24 volt inverter, there are additional losses when running at higher voltages.
    In the end, the differences (are far as we are concern) are usually only 1-2% change in losses between a properly designed higher or lower voltage system... And with solar power, if we are within ~10% between predicted and measured output--We are pretty much "dead on" (so many variable regarding losses, measurement errors, and variation in solar output--It just is not worth the "extra work" to be more accurate with sizing estimates).
    Just follow the design rule of thumbs, and everything works out pretty well for the typical system. Throw in a bit of over capacity to allow for aging and that loads typically grow a bit over time--And you should have a system that meets your needs for now and in the future.
    More or less, if you can keep the DC current at or below ~100 amps for your loads, and below ~80 amps for your charging current, the system is a bit cheaper to buy parts for and to install.
    For example, over 100 Amps and you have to get into very heavy (and expensive) copper wire. And over 80 amps, you have to have two or more MPPT charge controllers (under 80 amps you can use one).
    Other issues--Checking water in battery cells is a pain. A 12 volt system only has 6 cells (assuming one string of batteries). A 24 volt system has a minimum of 12 cells, and 48 volt has a minimum of 24 cells. It is easier to have fewer cells in larger (AH) batteries to check electrolyte levels/specific gravity on.
    On the other hand, if you are going to send larger amounts of power many 10's or hundreds of feet--You want to send that power at higher voltages. Sending 1,200 Watts at 12 volts, or 10 amps with only 1 volt drop for 10' would take around 3/O copper cable.
    To send 1,200 watts at 120 volts, or 10 amp with ~4 volt drop for 100', it would only take around 12 AWG cable...
    The right tools for the right job. We can help you with a couple paper designs and you will quickly see why we make the choices we do.
    At the moment, it is confusing because we really do not have a size for your RV's power system and your power needs.
    Usually, for smaller systems (what I think yours will be)--2-4 golf cart batteries wire as 12 volt battery bank with a 300 Watt (or a bit larger) 12 volt AC inverter will probably be plenty fine for your needs.
    If you were to add a full size refrigerator--You would be looking at a 1,200-1,500+ Watt AC inverter and either 24 or 48 volt battery bank. With a lot more batteries and solar panels.
  • Ralph Day
    Ralph Day Solar Expert Posts: 1,033 ✭✭✭✭
    Also not to forget how the weight of panels will affect the total weight of your trailer and the tongue weight. Don't want to over weight the trailer or the tow vehicle capacity. A couple of hundred pounds of panels and added battery weight will cut down your trailer cargo capacity, and the added tongue weight will reduce the tow vehicle's load capacity.
    Ralph
  • TaoJones
    Photowhit wrote: »
    Now that is clear . . . thank you for that, Photowhit.
  • TaoJones
    <snip>
    Thank you so much, Bill. I had originally thought I would first buy the TriMetric monitor and use it to determine exactly what my current power usage is, even though that includes air conditioning, water heating, refrigeration and a 32" HDTV serving as the display for my MacBook laptop. It will be good to know what that total load amounts to, even though I already know those items will change drastically in a boondocking situation. Would first installing a TriMetric monitor still be a good way to proceed, given the need to know what the load demand will be while boondocking so an appropriate system can be designed?
    I think I suffered a bit of sticker shock when I was initially advised to build a 1000w system with a MidNite Classic 150 charge controller and a MagnaSine 2812 inverter. It just seemed way beyond what I would ever need, but in fairness, that person had asked my present power demands and assumed I would be wanting to continue using the 32" HDTV and laptop about 15 hours a day. With that misunderstanding cleared up, I feel like my more modest expectations are now being met.
    This travel trailer is a 30 amp coach, and even with the A/C, refrigerator, water heater and microwave occasionally running at the same time, I can only recall one instance of a breaker tripping. At any rate, that sort of greedy power consumption is a thing of the past as I've gotten educated on all this. It's embarrassing to have been so ignorant about what I was doing, but I suppose it's common to not even think about it when you get used to plugging into an RV park's power pedestal and always having as much power as the coach needed.
    I agree that the system I'll need will probably be rather modest, Bill. I wouldn't be opposed to getting (4) 6w 260 Amp-hour Crown deep cycle batteries instead of 2, but staying with a 12v configuration. As I understand it, this would double the Amp-hour rating to 520.
    I've been completely satisfied with the Dometic refrigerator that came with this coach, but I've never run it extensively on propane. If it continues to perform as it has on 120v AC, I don't anticipate that I'd ever change it.
    Thanks again for your interest in what it is I'm trying to do.
    TJ
  • TaoJones
    Ralph Day wrote: »
    Ralph
    You're absolutely right about that, Ralph . . . weight considerations are always in the front of my mind whenever I think about adding something to my RV. Although this RV's tongue has carriers for a pair of Group 27s, I only use one. If I go with two 6v Crown batteries, the weight will be nearly identical. If I opt to go with 4, however, that will place twice the battery weight on the tongue. And as the charge controller, inverter, etc. will be just behind the tongue and the panels will be on the roof just behind the front of the trailer, all this added weight is being placed toward the front of the coach.
    I currently tow with a Chevy Silverado 3/4 ton HD pickup, but there may be a one-ton diesel in my future. I've always been careful about keeping the added cargo down, and I only make long passages with empty tanks. Each tank is 40 gallons, so that represents a potential 120 gallons x 8 1/3 pounds/gallon, or 1000 pounds. It's silly not to empty the tanks before setting out, then carrying that excess weight up some pretty steep hills here in the west.
    TJ
    TaoJones wrote: »
    If you are going to purchase a Battery Monitor anyway--Why not now. (if you get one of the Midnite controllers, there is the external battery monitor/shunt option--Close to battery monitor function, better charging control for the battery bank).
    For much of your equipment, you can do just about as well with a Kill-a-Watt type meter for less than $30 (just measure your AC loads in kWH and peak Watts--Just use a 1/0.85 AC Inverter factor for the DC power side).
    Yea--Knowing your loads and conservation are your friends when looking at off grid solar.
    Until you measure your loads--Most folks really have no idea of how "cheap" utility power is. More or less, assume your off grid power is 10x the cost of your grid power--And buy your appliances accordingly.
    If you ignore the refrigerator and microwave--You can probably everything else with a 300 Watt AC inverter. Add a refrigerator+microwave, you are looking at 1,500 Watt or larger AC inverter.
    2-4 series/parallel connected golf cart type batteries is probably "good enough" for now. Run them, measure loads and usage patterns and see what happens. Possibly add a solar panel or two and you will be fine.
    RV batteries typically die from age/tough usage (deep cycling, forgetting to recharge/check water levels, etc.). The cheap batteries, if you take somewhat good care of them, will last your 3+ years pretty easily. Pay 2x as much for batteries that may last you 2x longer (unless you "murder them" earlier), is not usually any advantage to you.
    Run it on propane if you do not have utility (or "fee" generator) power... Generally absorption type refrigerators are very (usually) inefficient on 120 VAC power. They are cheaper to run on propane when off grid. Use a Kill-a-Watt meter to see what amounts of power it takes.
    If you are running the fridge for 9+ months a year--Switching to a 120 VAC (or 12 VDC) compressor based RV fridge can make sense.
  • TaoJones
    Thank you for the tip on the Kill-A-Watt meter, Bill, and the link as well. It looks like an economical way to get a clear picture of what sort of power usage the current components are demanding.
    I had started this thread by noting that I had read all of HandyBob Shearer's blog . . . I was hoping (and maybe expecting) that someone might post an opinion on Mr. Shearer's strongly held point-of-view. His site is http://handybobsolar.wordpress.com/ and though he can seem cantankerous at times, I think he's just frustrated because he's seen so many installations that were all wrong and is of the opinion that many of the people who are doing those installations are either incompetent or intentionally leading trusting souls astray just so they can sell them more and more stuff that will never give them the power independence they're seeking.
    And where Mr. Shearer constantly advises those who ask that they should first get a TriMetric monitor, that doesn't seem to be the generally accepted view (if I'm reading this thread correctly). Is there something about the Bogart Engineering products that renders them less-than-adequate for their designed function? Am I just on the wrong track thinking I'd make the TriMetric the brain in my system? Are the Bogart Engineering products just OK, but there are other, better-suited or more cost-effective products I should be considering?
    Thanks again for all your in depth knowledge and willingness to share it, Bill.
    TJ
    This is a quote from our (now retired) Admin "WindSun" that started the forum:
    For 12 Volt & RV Systems - HandyBob's long discussion and rant is about 99% right on how to make RV and similar 12 volt systems work correctly. One of the few "non NAWS" articles that we recommend.
    The HandyBob person here is named "Cariboocoot" (Marc), one of the other volunteer moderators here.
    He spends much of his time redesigning/fixing systems for poor souls who have installed (or hired somebody to design and install) off grid solar power systems in his Neck of the frozen north.
    The Tri-Metric is a very popular Battery Monitor around here.
    Trimetric TM-2025-RV Battery Monitor System
    Very reasonable price and works well.
    The problems... 1) programming is not very user friendly. Some folks have no problems, other have pulled out their hair (if you still have the blinking 12:00 on your VCR--The Tri-metric may not be the best unit for you :roll:).
    The other... 2) Battery Monitors estimate the discharging and charging of the battery bank. Battery Monitors can "drift" over time. They "reset" to 100% full via something like seeing >14.5 volts for >2 hours (or similar--I do not have an off grid system, mine is Grid Tied).
    But for the most part, yes they are much easier to use day to day and by a spouse/kids/guests (if below 50% SOC, start the generator and turn off when >80%, if still heading to below 50% SOC, call the owner to see what is going on and turn off unneeded loads, etc.).
    The "issue" with using a Tri-metric--You already have an off grid power system, so you are already "committed" to the battery bank+solar array+charge controller.
    Using a Kill-a-Watt meter is an easy way to estimate your off grid usage before going off grid. Run the stuff "at home" or even for a few weeks on a small Honda eu2000i genset and see what your kWH usage per day works to be...
    One reason that the Kill-a-Watts work out well--Modern Energy Star rated appliances (for example Refrigerators, TVs, laptop computers, etc.) are just about as efficient as their DC counter parts--And frequent the AC versions are much cheaper and fewer problems/issues vs their DC counter parts.
    Toss in a reasonable size AC inverter and around 15-20% more solar panels plus increased battery bank AH capacity--And call it a day and skip most of the DC direct loads.
    Take that information to start designing your off grid power system. Do several designs on paper and figure out how well it will support your needs. Paper designs are a lot cheaper to tear up and toss out vs "real" solar hardware.
    Besides these battery monitors sold by our host:
    http://www.solar-electric.com/metersmonitors.html
    The Victron Battery Monitors have also had some good press on the forum.
    Clarification lest someone be confused: I am not the HandyBob of the RV forum.
  • Chris
    Chris Solar Expert Posts: 135 ✭✭
    LOL, I had wondered when I first signed up to the forum....then I realized he lived in a different country 8)
  • TaoJones
    Thank you for your thoughtful reply, as always, Bill. I think I understand your point regarding the TriMetric monitor . . . the programming of it can, perhaps, be a bit intimidating for some users. I carefully read the instructions online here: http://www.bogartengineering.com/sites/default/files/docs/TM-2030Install%20Instructions3-18-14%20%281%29.pdf . . . and while it's thorough, it didn't seem to be beyond my abilities.
    I suppose it's a bit like your observation about creating system designs on paper, though . . . intellectual concepts and hard reality don't always sync up perfectly. ;)
    I served as a moderator and admin on a sailing forum a few years ago and hate online misunderstandings, so to the extent my bringing HandyBob into the conversation created some confusion, maybe the following will help clear things up:
    Bob Shearer (aka HandyBob, a name others gave him that stuck) is a former full-time RVer who had formerly worked as an electrical engineer and in electrical equipment sales before he retired. When he and his wife began full-timing and moved up to a 31' fifth-wheel, he was determined to figure out why it was that the coach had 345 watts of solar panels, but the batteries quickly went dead if they ran anything beyond a few lights - forcing them to head to an RV park to recharge. All that was in the 2000-2003 period.
    Because the system that was already on their coach was installed by the "Grandfather of RV solar power," the first thing Bob learned was that the man who literally wrote the book on RV solar was clueless about how to make solar charging work and didn't actually live full-time in an RV himself. After he did solve the problem, though, the Shearers never used an RV park again and never bought a generator, either.
    HandyBob has since stopped full-timing to build a home in Montana, also fully-dependent on solar. They continue to live in their fifth-wheel while they build up their mountaintop property to meet their needs. Somewhere in his blog, HandyBob put in a good word for NAWS. Because he is so acutely aware of the charlatans who seem to outnumber the honest people in the solar industry, his recommendation carried a lot of weight with me and indirectly led me to this forum.
    I'll order a Kill-A-Watt meter, Bill, and note what the readings indicate. I do understand, though, that conserving energy is a far-better solution than buying and installing a system that will generate all the voltage a thoughtless energy user could ask for.
    TJ
    TJ,
    Not problem with HandyBob discussion. He is pretty well known (through his writtings) here. We where just having a little fun (does not always translate well on an Internet Forum through the written word).
    And then you get the stupid typos, no proof reading:
    Forget one tiny little word--And the meaning is 180 degrees off.
    -Bill "more :blush:" B.
    To add:
    I really try to avoid anything like "...thoughtless energy user..." on the forum.
    Energy usage is a highly personal set of choices. What one person may choose will be different from my choices/needs.
    What most of us here are... Is CHEAP. We want to see people get the best bang for the buck (and have a reliable power system that meets their needs too). Aka an "optimum" solution.
    And conservation is one of those tools that really can help keep costs down.
  • AuricTech
    AuricTech Solar Expert Posts: 140 ✭✭
    Heck, if you change one tiny little letter (not to now), you can reverse the meaning.... ;)
  • Plowman
    Plowman Solar Expert Posts: 203 ✭✭✭✭✭
    TaoJones wrote: »
    I wrote this is another thread yesterday, but it might be useful for you (I'm living off-grid in a stationary RV):
    Re. refrigeration, I use an RV propane fridge, works quite well despite being 18 years old. I only started using it on propane a month or so ago, still figuring out exactly how much propane it burns, but the last tank I measured I was using almost exactly 0.25 gals/day to run the fridge and the stove. Not sure how much propane each appliance is using since they're on the same tank.
    The 12V draw of the fridge is minimal, it draws 0.3 amps, but not continuously. Roughly 4.5 amp-hours per day. I measured how much it draws when plugged into grid power last year, it's crazy inefficient when run on AC (147.3kWh/month).
    I had been running the fridge on grid power for a couple years with no problem, but when I moved to a spot with no access to grid power I started using propane. At first the fridge got too cold, somewhere in the 20s. After much googling it turned out to be an easy fix, just had to move the sensor, now it holds steady around 35.
    I've obsessively measured all the loads in my RV, I can share them if you want. But my old RV may be different than your (presumably) newer one.