My new experiment plan

Options
UAE_Boy
UAE_Boy Registered Users Posts: 20
Hi I am planning to do my second experiment ,

my equipment's are The Sukam 10KVA inverter is a 180V inverter, which means that it requires a battery bank of 15 units of 12V batteries 200Ah

15 units of 12V batteries 200Ah for my battery bank


three charge controller MPPT (The MidNite Solar Classic MPPT charge controller Classic 150 )

250 watt solar panel mono type (3500 watt) 14 units

how many circuit breaker do I need and how many fuse breaker and what is the value of it

does Northern Arizona Wind & sun do shipping via UPS if I buy online to UAE

Thank you

Comments

  • waynefromnscanada
    waynefromnscanada Solar Expert Posts: 3,009 ✭✭✭✭
    Options
    Re: My new experiment plan

    Other than a photo and a very brief description giving no useful information, here is their site. Wonder what it's all about?

    http://www.mygadgetsmall.com/shopping/power-inverters/su-kam-inverters/su-kam-inverter-10kva-180v-digital-pure-sine-wave-inverter/prod_38.html
  • UAE_Boy
    UAE_Boy Registered Users Posts: 20
    Options
  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Options
    Re: My new experiment plan

    Fuses or circuit breaker sizes are all determined by the same rules.
    The first of the rules is "one per circuit". So for the output of three charge controllers you have three circuits and thus need three fuses or breakers.
    The second rule is the wire size used. This has two requirements; handling the amount of current expected and keeping Voltage drop to minimum. Usually this means the wire will be larger than needed for the expected current. For example a MidNite Classic 150 can output 90+ Amps on a 12 Volt system and has a maximum wire size of 4 AWG which can just about manage 100 Amps maximum. It also has an 80 Amp rating for 48 Volts, which is probably what you will be using.
    Third rule is to size the fuse or breaker according to the wire gauge. The idea is that the circuit protection 'gives up' before the wire does.

    So for the Classic 150 output we have a maximum of 4 AWG wire and a 100 Amp fuse or breaker.

    If you expect less current then smaller wire and circuit protection can be used. For example in charging a 200 Amp hour battery you will be using current less than 40 Amps because the battery probably will not take that much without overheating.

    You seem to have divided the system into three segments of 60 Volts each, so you are looking at each controller producing 20 Amps peak @ 60 Volts needing approximately 1558 Watts on the input. Your fourteen 250 Watt panels will be a bit on the light side with approximately 7% peak charge rate. I suggest adding four more panels for three arrays of six panels each (1500 Watts). Then each array will be two parallel strings of three in series, requiring no fuses or breakers on the array side and providing Vmp around 90 which should work for a 60 Volt nominal system.

    You will have to contact NAWS directly to ask about shipping considerations: we do not work for them, they just pay for the forum space.
  • BB.
    BB. Super Moderators, Administrators Posts: 33,457 admin
    Options
    Re: My new experiment plan

    Wayne was just interested in the 180 VAC inverter. These high voltage AC inverters are not very standard around here and Wayne was trying to find out the details about the UPS.

    With 3 Midnite controllers, you will be looking at 3 banks of 60 VDC battery connections (you will have to program the Midnite that this are 60 VDC battery banks and the appropriate charge parameters).

    So, you are going to have 4 "taps" coming off of the battery bank. One at zero volts, a second at 60 VDC, a third at 120 VAC, and the fourth at 180 VDC.

    Assuming that the battery bank is negative grounded to your building's green wire ground/safety ground system, then each tap will need a 100 amp breaker/fuse, other than the zero volt first tap.

    Note, I am guessing that the battery bank is negative grounded. With a UPS, it may actually not be negative ground, and if not, then you should put a fourth breaker/fuse on the "zero volt" line too (because it is floating and not at zero volts).

    Most sine wave AC inverters have isolated AC output voltage and can have the DC input ground referenced--But you need to verify that this UPS can have the negative battery bus grounded. Do not assume anything without doing the research--This is a lot of power/current/large battery bank and it can be very easy to end up with a lap full of red hot copper and battery parts+sulfuric acid embedded in the walls and inside you too.

    Another note--DC current is much more difficult for a switch/fuse/circuit breaker to "open" or "turn off". AC current switches polarity 50/60 times per second. So, you will find that the DC versions of switches/breakers are much larger/heavier construction vs their AC counter part.

    For example, in the US we have a line of house hold circuit breakers that are rated for 240 VAC operation (really 600 VAC) on 60 Hz AC. The same breaker is rated for a maximum of 48 VDC.

    In the US/Solar RE market, the largest "standard" DC rated breakers (from Midnite) are marked to a maximum of 150 VDC. Your battery bank runs >200 VDC. The standard solar/RE breakers will not be safe for use on your high 180 VDC battery tap. You will have to find properly rated DC breakers/fuses/switches for this system.

    Remember that most solar charge controllers will have their internal electronics connected directly to the "negative battery terminal" inside the charge controller. Any communication ports (like RS 232, RS 422, etc.) will be at your "negative tap" voltage (the Ethernet connection is isolated by a transformer--But you are pushing the isolation voltage ratings of these transformers).

    Why are you looking at this sort of power system? Is it to save money, emergency backup power, or a full off grid power system?

    There is another possibility that may end up being easier and safer, and possibly less expensive.

    Many Sine Wave type AC inverters are actually bi-directional power devices. We are used to the DC Battery bank supplying power through the AC inverter to the AC loads.

    However, many AC sine wave inverters can also be driven backwards. You can put the proper type of AC power source on the output of the sine wave inverter and actually push energy "backwards" through the sine wave inverter and recharge your DC battery bank.

    Two things... The "proper" AC power source is a Grid Tied type AC inverter (solar panels>GT Inverter>AC sine wave inverter's AC input>DC Battery bank).

    Second thing... Most "off the self" UPS and Off Grid AC Sine Wave Inverters are not designed to manage the backwards current flow. If you connect a Solar Array + GT inverter to the Sine Wave OG AC inverter, it can/will overcharge the DC battery bank. You need to control this current flow.

    Two basic methods, one is to put a DC shunt load (resistor load bank/electric heater) on the battery bank that can absorb excess charging energy (once the battery bank is full). You could also put the dump load on the AC output side of the sine wave inverter too (i.e., an 8kWatt heater, turn on for 10s of seconds to minutes or more to dump excess energy. Battery becomes discharged a bit, and the dump load is turned off for a bit).

    A second method is to put a "relay" in the AC output of the GT Inverter... When the battery bank is full, the battery voltage monitor simply turns off the GT inverter's AC output (through the relay, some GT inverters also have an "inhibit" input too). GT inverter will turn off and wait for 5 minutes of AC power, then turn on again.

    If you are "serious" about using the 180 VDC inverter system--I would look very closely at purchasing a GT inverter (230 VAC 50 Hz for UAE?). Just one GT inverter connected to the AC OG Inverter's AC output (~10,000 watts of solar array and ~7.700 Watt worth of GT inverter maximum for your 10 kWatt system using "nominal numbers). The GT inverter's output cannot exceed the OG inverter's AC input power.

    Note--Many devices are rated at very high power levels, but when the actual demand (or back driving of power) at rated power--They can overheat/fail. You might want to limit power used/generated to 80% of name plate until you do some experimenting to make sure they do not overheat/fail. Many devices if operated at 100% rated power for 5 hours (such as recharging the battery bank through the sine wave inverter during the day) will overheat.

    "AC Coupling" has been done on some OG AC Inverters and is known to work--And may be easier/safer than using the three Midnite charge controllers on the DC side. You need to do your own research and make sure that your installation is safe (and you have battery charging limit hardware reliably installed and maintained). In the US electrical code, that would mean there would be two independent methods of controlling the charging current (such as two battery charge monitors and two AC relays to turn off the GT inverter).

    Shunt controller type battery charging is less than ideal (series charge controllers such as the Midnite on the DC side is better). But shunt control of battery charging is done all the time.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • UAE_Boy
    UAE_Boy Registered Users Posts: 20
    Options
    Re: My new experiment plan

    Hi

    the reason that I planning to buy 10kav inverter is I am going to install Water desalination plant 10.000 gallon per day , and the power that the system consume is 6 KWh and the water pump that pump the water from the well is 3hp

    so I plan to use 10kav because I found it in the market . because I am interesting to buy breaker and fuse I don't know how many I should to use ?

    this is my small drawing . I put another 15 battery to have more power
    the charge controller is 150V 96A


    78e9cf3e030bd6b.png

    BB. wrote: »
    Wayne was just interested in the 180 VAC inverter. These high voltage AC inverters are not very standard around here and Wayne was trying to find out the details about the UPS.

    With 3 Midnite controllers, you will be looking at 3 banks of 60 VDC battery connections (you will have to program the Midnite that this are 60 VDC battery banks and the appropriate charge parameters).

    So, you are going to have 4 "taps" coming off of the battery bank. One at zero volts, a second at 60 VDC, a third at 120 VAC, and the fourth at 180 VDC.

    Assuming that the battery bank is negative grounded to your building's green wire ground/safety ground system, then each tap will need a 100 amp breaker/fuse, other than the zero volt first tap.

    Note, I am guessing that the battery bank is negative grounded. With a UPS, it may actually not be negative ground, and if not, then you should put a fourth breaker/fuse on the "zero volt" line too (because it is floating and not at zero volts).

    Most sine wave AC inverters have isolated AC output voltage and can have the DC input ground referenced--But you need to verify that this UPS can have the negative battery bus grounded. Do not assume anything without doing the research--This is a lot of power/current/large battery bank and it can be very easy to end up with a lap full of red hot copper and battery parts+sulfuric acid embedded in the walls and inside you too.

    Another note--DC current is much more difficult for a switch/fuse/circuit breaker to "open" or "turn off". AC current switches polarity 50/60 times per second. So, you will find that the DC versions of switches/breakers are much larger/heavier construction vs their AC counter part.

    For example, in the US we have a line of house hold circuit breakers that are rated for 240 VAC operation (really 600 VAC) on 60 Hz AC. The same breaker is rated for a maximum of 48 VDC.

    In the US/Solar RE market, the largest "standard" DC rated breakers (from Midnite) are marked to a maximum of 150 VDC. Your battery bank runs >200 VDC. The standard solar/RE breakers will not be safe for use on your high 180 VDC battery tap. You will have to find properly rated DC breakers/fuses/switches for this system.

    Remember that most solar charge controllers will have their internal electronics connected directly to the "negative battery terminal" inside the charge controller. Any communication ports (like RS 232, RS 422, etc.) will be at your "negative tap" voltage (the Ethernet connection is isolated by a transformer--But you are pushing the isolation voltage ratings of these transformers).

    Why are you looking at this sort of power system? Is it to save money, emergency backup power, or a full off grid power system?

    There is another possibility that may end up being easier and safer, and possibly less expensive.

    Many Sine Wave type AC inverters are actually bi-directional power devices. We are used to the DC Battery bank supplying power through the AC inverter to the AC loads.

    However, many AC sine wave inverters can also be driven backwards. You can put the proper type of AC power source on the output of the sine wave inverter and actually push energy "backwards" through the sine wave inverter and recharge your DC battery bank.

    Two things... The "proper" AC power source is a Grid Tied type AC inverter (solar panels>GT Inverter>AC sine wave inverter's AC input>DC Battery bank).

    Second thing... Most "off the self" UPS and Off Grid AC Sine Wave Inverters are not designed to manage the backwards current flow. If you connect a Solar Array + GT inverter to the Sine Wave OG AC inverter, it can/will overcharge the DC battery bank. You need to control this current flow.

    Two basic methods, one is to put a DC shunt load (resistor load bank/electric heater) on the battery bank that can absorb excess charging energy (once the battery bank is full). You could also put the dump load on the AC output side of the sine wave inverter too (i.e., an 8kWatt heater, turn on for 10s of seconds to minutes or more to dump excess energy. Battery becomes discharged a bit, and the dump load is turned off for a bit).

    A second method is to put a "relay" in the AC output of the GT Inverter... When the battery bank is full, the battery voltage monitor simply turns off the GT inverter's AC output (through the relay, some GT inverters also have an "inhibit" input too). GT inverter will turn off and wait for 5 minutes of AC power, then turn on again.

    If you are "serious" about using the 180 VDC inverter system--I would look very closely at purchasing a GT inverter (230 VAC 50 Hz for UAE?). Just one GT inverter connected to the AC OG Inverter's AC output (~10,000 watts of solar array and ~7.700 Watt worth of GT inverter maximum for your 10 kWatt system using "nominal numbers). The GT inverter's output cannot exceed the OG inverter's AC input power.

    Note--Many devices are rated at very high power levels, but when the actual demand (or back driving of power) at rated power--They can overheat/fail. You might want to limit power used/generated to 80% of name plate until you do some experimenting to make sure they do not overheat/fail. Many devices if operated at 100% rated power for 5 hours (such as recharging the battery bank through the sine wave inverter during the day) will overheat.

    "AC Coupling" has been done on some OG AC Inverters and is known to work--And may be easier/safer than using the three Midnite charge controllers on the DC side. You need to do your own research and make sure that your installation is safe (and you have battery charging limit hardware reliably installed and maintained). In the US electrical code, that would mean there would be two independent methods of controlling the charging current (such as two battery charge monitors and two AC relays to turn off the GT inverter).

    Shunt controller type battery charging is less than ideal (series charge controllers such as the Midnite on the DC side is better). But shunt control of battery charging is done all the time.

    -Bill
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Options
    Re: My new experiment plan
    UAE_Boy wrote: »
    Hi

    the reason that I planning to buy 10kav inverter is I am going to install Water desalination plant 10.000 gallon per day , and the power that the system consume is 6 KWh and the water pump that pump the water from the well is 3hp ....

    Do you know how much power your 3hp pump consumes ? Voltage ? 3phase ? Do you have a 3 phase inverter ? I'd be pretty sure the desalination plant is poly phase too.

    Better check it out first before you purchase anything....
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Options
    Re: My new experiment plan

    In addition to what Mike said about making sure you have all the specs on the AC side of things ...
    UAE_Boy wrote: »
    Hi

    the reason that I planning to buy 10kav inverter is I am going to install Water desalination plant 10.000 gallon per day , and the power that the system consume is 6 KWh and the water pump that pump the water from the well is 3hp

    so I plan to use 10kav because I found it in the market . because I am interesting to buy breaker and fuse I don't know how many I should to use ?

    this is my small drawing . I put another 15 battery to have more power
    the charge controller is 150V 96A


    78e9cf3e030bd6b.png

    Each of those controller outputs needs at least a fuse or breaker on the positive side for safety. As Bill mentioned if it is 'floating' then a double poll breaker disconnecting both positive and negative is safest.

    Will you actually be using two parallel strings of batteries? I thought you indicated before that they were 200 Amp hour 12 Volt units all in one series string.
  • UAE_Boy
    UAE_Boy Registered Users Posts: 20
    Options
    Re: My new experiment plan

    3hp 3300 watt , 220v ,15 A 3phase

    mike95490 wrote: »
    Do you know how much power your 3hp pump consumes ? Voltage ? 3phase ? Do you have a 3 phase inverter ? I'd be pretty sure the desalination plant is poly phase too.

    Better check it out first before you purchase anything....
  • UAE_Boy
    UAE_Boy Registered Users Posts: 20
    Options
    Re: My new experiment plan

    This is my new plan 180VDC 200Ah , if its wrong to add another string parallel please tell me
    In addition to what Mike said about making sure you have all the specs on the AC side of things ...



    Each of those controller outputs needs at least a fuse or breaker on the positive side for safety. As Bill mentioned if it is 'floating' then a double poll breaker disconnecting both positive and negative is safest.

    Will you actually be using two parallel strings of batteries? I thought you indicated before that they were 200 Amp hour 12 Volt units all in one series string.
  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Options
    Re: My new experiment plan
    UAE_Boy wrote: »
    This is my new plan 180VDC 200Ah , if its wrong to add another string parallel please tell me

    Not necessarily wrong, but is it needed to have the 200 Amp hours?
    In other words what are the specifications on the individual batteries?
  • UAE_Boy
    UAE_Boy Registered Users Posts: 20
    Options
    Re: My new experiment plan

    The Sukam 10KVA inverter is a 180V inverter, which means that it requires a battery bank of 15 units of 12V batteries. Recommended batteries are ideally up to 200Ah for optimum backup capacity, though lower capacities can be used. Again, deep discharge (deep cycle) batteries are best for power backup systems, to achieve satisfactory performance
    Not necessarily wrong, but is it needed to have the 200 Amp hours?
    In other words what are the specifications on the individual batteries?
  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Options
    Re: My new experiment plan
    UAE_Boy wrote: »
    The Sukam 10KVA inverter is a 180V inverter, which means that it requires a battery bank of 15 units of 12V batteries. Recommended batteries are ideally up to 200Ah for optimum backup capacity, though lower capacities can be used. Again, deep discharge (deep cycle) batteries are best for power backup systems, to achieve satisfactory performance

    Yes, but what batteries are you actually proposing to use?

    For example you could use these 12 Volt 115 Amp hour batteries http://www.solar-electric.com/repoba12vo11.html and need two parallel strings to get to 230 Amp hours capacity.

    Or you could use these 12 Volt 530 Amp hour batteries http://www.solar-electric.com/crinba6.html and have more than double your desired capacity on one string.

    There are many variations between those two examples. Including 24 Volt industrial, 6 Volt cells (220 Amp hour common GC2's), and 2 Volt cells. It is best to have only one string of batteries if possible: fewer connections to go wrong and fewer cells to check.
  • UAE_Boy
    UAE_Boy Registered Users Posts: 20
    Options
    Re: My new experiment plan

    The battery that I found in our market 12v 200Ah it will cost me 280$ but if I buy the one that you mentioned the pries is fair but the shipping will cost me more than the cost of the batteries http://www.solar-electric.com/crinba6.html no dealer for this brand in my country even for the fuse and breakers I will order it from outside ,when I went to asked for the Dc fuser/breaker just the seller here said you can use an AC breaker .

    Yes, but what batteries are you actually proposing to use?

    For example you could use these 12 Volt 115 Amp hour batteries http://www.solar-electric.com/repoba12vo11.html and need two parallel strings to get to 230 Amp hours capacity.

    Or you could use these 12 Volt 530 Amp hour batteries http://www.solar-electric.com/crinba6.html and have more than double your desired capacity on one string.

    There are many variations between those two examples. Including 24 Volt industrial, 6 Volt cells (220 Amp hour common GC2's), and 2 Volt cells. It is best to have only one string of batteries if possible: fewer connections to go wrong and fewer cells to check.
  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Options
    Re: My new experiment plan
    UAE_Boy wrote: »
    The battery that I found in our market 12v 200Ah it will cost me 280$ but if I buy the one that you mentioned the pries is fair but the shipping will cost me more than the cost of the batteries http://www.solar-electric.com/crinba6.html no dealer for this brand in my country even for the fuse and breakers I will order it from outside ,when I went to asked for the Dc fuser/breaker just the seller here said you can use an AC breaker .

    I wasn't suggesting you buy those batteries; merely using them as examples to explain the different possibilities. Shipping on batteries is a huge cost so it is nearly always best to buy them locally.

    If you've got 200 Amp hour 12 Volt batteries and only need 200 Amp hours then you only need one string of them. At 180 Volts that is a whopping 18kW hours of stored power. Your proposed 6kW hour load need is well below that.

    You're quite right to distrust someone selling you AC rated breakers for DC as they won't work. At least not at the same Voltage level. You actually need breakers like this for the controller outputs: http://www.solar-electric.com/misomn150vdc.html Notice the smallest of these is 80 Amps so the wire should be sized accordingly. Note too that they are not double pole breakers.

    For the inverter input you would need something like this: http://www.solar-electric.com/miso30dccibr.html
  • UAE_Boy
    UAE_Boy Registered Users Posts: 20
    Options
    Re: My new experiment plan

    power isn't 36KW 180x200
    I wasn't suggesting you buy those batteries; merely using them as examples to explain the different possibilities. Shipping on batteries is a huge cost so it is nearly always best to buy them locally.

    If you've got 200 Amp hour 12 Volt batteries and only need 200 Amp hours then you only need one string of them. At 180 Volts that is a whopping 18kW hours of stored power. Your proposed 6kW hour load need is well below that.

    You're quite right to distrust someone selling you AC rated breakers for DC as they won't work. At least not at the same Voltage level. You actually need breakers like this for the controller outputs: http://www.solar-electric.com/misomn150vdc.html Notice the smallest of these is 80 Amps so the wire should be sized accordingly. Note too that they are not double pole breakers.

    For the inverter input you would need something like this: http://www.solar-electric.com/miso30dccibr.html
  • solar_dave
    solar_dave Solar Expert Posts: 2,397 ✭✭✭✭
    Options
    Re: My new experiment plan

    How about taking a different tack, and run the desalination only in daylight hours, should cut you battery requirements quite a lot.
  • UAE_Boy
    UAE_Boy Registered Users Posts: 20
    Options
    Re: My new experiment plan

    how? in the daylight no need for the batteries
    solar_dave wrote: »
    How about taking a different tack, and run the desalination only in daylight hours, should cut you battery requirements quite a lot.
  • solar_dave
    solar_dave Solar Expert Posts: 2,397 ✭✭✭✭
    Options
    Re: My new experiment plan
    UAE_Boy wrote: »
    how? in the daylight no need for the batteries

    Exactly, the water is durable and perhaps doing most of it just off panels is much more effective. The battery bank you propose is pretty huge. If the location is truly off grid you would only need enough battery to buffer the daytime solar variability.
  • UAE_Boy
    UAE_Boy Registered Users Posts: 20
    Options
    Re: My new experiment plan

    this mean I will get only 4200 galloon during the daylight
    so I will go with one string battery bank
    solar_dave wrote: »
    Exactly, the water is durable and perhaps doing most of it just off panels is much more effective. The battery bank you propose is pretty huge. If the location is truly off grid you would only need enough battery to buffer the daytime solar variability.
  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Options
    Re: My new experiment plan
    UAE_Boy wrote: »
    power isn't 36KW 180x200

    18 kW hours: 180 Volts * 100 Amp hours (50% DOD).
  • solar_dave
    solar_dave Solar Expert Posts: 2,397 ✭✭✭✭
    Options
    Re: My new experiment plan
    UAE_Boy wrote: »
    this mean I will get only 4200 galloon during the daylight
    so I will go with one string battery bank

    So what is more cost effective? Small battery with lots of solar X 2 desalination plants running part of the day? Or huge battery with all the issues to get 7X24 operation. Do these desalination plants need down time for maintenance?
  • UAE_Boy
    UAE_Boy Registered Users Posts: 20
    Options
    Re: My new experiment plan

    how I size the wire with the breaker

    I will buy Midnite Solar
    MNPV Combiner BoxesMNPV3 Din Rail Circuit Breakers, 125VDC PV Array Breakers 10A for each string

    from the output of the controller is 80Amps enough to 16mm copper cable but do I need to buy a box as well to hock the breaker
    for the inverter how many amperes breaker I should to buy .Is Breaker Size(MNEPV50-300) 50 Amp right one ?


    I wasn't suggesting you buy those batteries; merely using them as examples to explain the different possibilities. Shipping on batteries is a huge cost so it is nearly always best to buy them locally.

    If you've got 200 Amp hour 12 Volt batteries and only need 200 Amp hours then you only need one string of them. At 180 Volts that is a whopping 18kW hours of stored power. Your proposed 6kW hour load need is well below that.

    You're quite right to distrust someone selling you AC rated breakers for DC as they won't work. At least not at the same Voltage level. You actually need breakers like this for the controller outputs: http://www.solar-electric.com/misomn150vdc.html Notice the smallest of these is 80 Amps so the wire should be sized accordingly. Note too that they are not double pole breakers.

    For the inverter input you would need something like this: http://www.solar-electric.com/miso30dccibr.html
  • UAE_Boy
    UAE_Boy Registered Users Posts: 20
    Options
    Re: My new experiment plan

    I don't know if the desalination plant need down time for the maintenance ,just I know it consume 6kwh with 10,000 gallon per day


    solar_dave wrote: »
    So what is more cost effective? Small battery with lots of solar X 2 desalination plants running part of the day? Or huge battery with all the issues to get 7X24 operation. Do these desalination plants need down time for maintenance?
  • pleppik
    pleppik Solar Expert Posts: 62 ✭✭✭✭
    Options
    Re: My new experiment plan
    UAE_Boy wrote: »
    I don't know if the desalination plant need down time for the maintenance ,just I know it consume 6kwh with 10,000 gallon per day

    Where are you getting the power consumption number? Ten thousand gallons of water per day is enough for 20 houses (I assume this is for irrigation or something similar), and 6kWh doesn't seem like even remotely enough power to desalinate using conventional techniques like reverse osmosis.

    I did find this article, though, about a demonstration solar desalination plant in California. It looks like it's basically a giant solar still.

    If that's what you want to attempt, then the plant will only desalinate water while the sun in shining anyway, so there's no point in pumping at night. The energy to actually desalinate the water is coming from the sunlight, and I would assume the 6kWh/day is what's required to operate pumps and fans to keep the whole thing running.

    Edited to add: According to the company's website, they use thermal storage to allow 24/7 operation, so you can still pump at night. Buying batteries to allow 24/7 operation off-grid will be more expensive, though, so with a major capital purchase like this it probably warrants a more careful cost analysis.
  • UAE_Boy
    UAE_Boy Registered Users Posts: 20
    Options
    Re: My new experiment plan

    This is for the farm ,I got the power consumption from the manufacture
    pleppik wrote: »
    Where are you getting the power consumption number? Ten thousand gallons of water per day is enough for 20 houses (I assume this is for irrigation or something similar), and 6kWh doesn't seem like even remotely enough power to desalinate using conventional techniques like reverse osmosis.

    I did find this article, though, about a demonstration solar desalination plant in California. It looks like it's basically a giant solar still.

    If that's what you want to attempt, then the plant will only desalinate water while the sun in shining anyway, so there's no point in pumping at night. The energy to actually desalinate the water is coming from the sunlight, and I would assume the 6kWh/day is what's required to operate pumps and fans to keep the whole thing running.

    Edited to add: According to the company's website, they use thermal storage to allow 24/7 operation, so you can still pump at night. Buying batteries to allow 24/7 operation off-grid will be more expensive, though, so with a major capital purchase like this it probably warrants a more careful cost analysis.