Good wire gone bad
mike95490
Solar Expert Posts: 9,583 ✭✭✭✭✭
Been getting high battery voltage alarms from the charge controller, and I went over all the battery interconnects and the terminals in the charge controller with an IR thermometer.
Then, when getting into the ePanel, to prep for the Midnight Controller for the new array, I saw the cause. And all the screws seem tight. Putting in new #4 wire (55A) and buss bar, and that should fix it up. Yow!
Fried Buss Bar Album
Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048
inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A
NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole |
Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor
(1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
Re: Good wire gone bad
That would concern me. Usually that happens if the connection was not tight or the wire was undersized. I saw that same thing at a friends and the connection was tight also but what I figured happened was that it WAS loose at one point, and the constant overheating caused it to expand and somehow tighten back up. He was using the proper sized wire also.
Now I always tend to oversize wires by 1 or 2 sizes anyways just in case. And the cost difference is not that much in the smaller gauges. I used #4 for everything in my new ePanel.
But glad you found it now before more of that insulation melted away and then the conductor shorted out to the enclosure!Off-Grid in Central Florida since 2005, Full-Time since June 2014 | 12 X Sovello 205w panels, 9 X ToPoint 220w panels, 36x ToPoint 225w panels (12,525 watts total) | Custom built single-axis ground mounts | Complete FP2 Outback System: 3 x FM80, 2 x VFX3648, X240 Transformer, FLEXnet-DC, Mate-3, Hub-10, FW500 AC/DC | 24 x Trojan L16RE-B Batteries 1110ah @ 48v | Honda EU7000is Generator and a pile of "other" Generators | Home-Made PVC solar hot water collector | Custom data logging software http://www.somewhatcrookedcamp.com/monitormate.html -
Looks like both wires are overheating, must have underestimated the current draw overtime. As said, it's to easy to upsize high current wires. -
something...?? If those were right sized for the anticipated amperage and are tight, did you have an over amperage event(s)???
Wires are from a 3Kw PV array - about 55amps on a 60A controller.
From further chatting with the electrician who installed it (before I moved here) I think he had a old, lugged, battery cable, and cut it in half. If it was not new pristine copper, then it would have been prone to have contact go bad with the obvious result. The tinned lug is NOT pristine and new like the other lugs in the chassis. That's my bet. And now I know to re-torque the setscrews at least 1x.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
if you can find them the best bus bars are ones with solid base but saddle clips for each wire this way the cable is not held by the screw but by 2 screws holding down each cable saddle. The connection is far superior as its held by a thick solid u shape piece of metal.. .