System going to crap - help
kirbinster
Registered Users Posts: 4
I've got a nine year old system that consists of 54 Sharp 185W panels connected to 3 Sunnyboy 2500U inverters and one 1100U inverter. I started having problems with one 2500 unit that would only stay online when my A/C was running, typically days when the power company was running lower voltage. Otherwise that unit show (on my sunny control) that it is at 261 volts and trips off line). I have a second 2500U that currently shows MPP but has 0 watt output and one that is only running at half capacity. The only one that is fully working is my 1100
Any suggestions on what I should check out to see if these are really inverter issues or problems from the panels.
Re: System going to crap - help
Welcome to the forum.
It's bad news time: It's probably down to repair/replace the inverter. The Sunny Boy 2500U's are no longer serviced by SMA. As you might guess they're failing too. The latest incidence: http://forum.solar-electric.com/showthread.php?23173-need-repair-ideas-for-a-sma-sunnyboy-2500U Note the link provided in Post #2. A comparable new unit is about $1,700 just so you know. -
Re: System going to crap - helpCariboocoot wrote: »Welcome to the forum.
I don't know on the SMA's but 261 Volts sounds like a grid tie cut off voltage on the high side. Is the utility driving the line voltage like that most of the time?
You can get a DC clamp meter and check the panel output voltage and amperage. -
Silly me; I was assuming the inverters were connected to the same grid. Therefor if the grid was really at 261 and tripping one off-line due to high Voltage it should trip both. And when neither was tripped the one shouldn't be showing zero output either. The one 1100 unit seems to stay running. Sounds like defective 2500U GTI's to me. -
Re: System going to crap - helpsolar_dave wrote: »I don't know on the SMA's but 261 Volts sounds like a grid tie cut off voltage on the high side. Is the utility driving the line voltage like that most of the time?
No its an issue with the inverter some how measuring the voltage wrong and tripping at the 260v high limit because of it. Right now that inverter says 261 while the other three all say that the voltage is 245. If I go out with a meter I measure just about what the other three say at any given time. -
Check the wires and connections on the 261v inverter. It may be that a poor connection is causing the voltage to not get exported, and it rises above the HV disconnect setpoint.only stay online when my A/C was runningPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
Re: System going to crap - helpCheck the wires and connections on the 261v inverter. It may be that a poor connection is causing the voltage to not get exported, and it rises above the HV disconnect setpoint.
Thanks. I actually opened up the connections and checked for corrosion and reinstalled. Still no difference. When I put a meter on it I get the correct reading which matches what the other inverters are telling me
- 227 Forum & Website
- 617 Discussion Forums/Café