Considering downlead losses
65DegN
Solar Expert Posts: 109 ✭✭
Been thinking about this lately as I design a 3,750 watt array into a system that could require 500' (RT) of array downlead. I've come to the conclusion that there is going to be a curve associated with the inefficiencies of this system balanced between the number of panels and the percentage of losses in the wire. Generally speaking I think it is better to not dump a massive amount of money into heavy wire (in this case it would take 500' of 1/0 to provide for ~2.4% loss or 82 watts) Rather than invest ~$1,000 into downlead I would rather put more of that capital into more panels and maybe add a tad more, to make up for losses. With this arrangement the array will also have better cloudy day performance (particularly if the controller is maxed out on a sunny day) at lower current levels, and consequently less loss than on sunny days, and greater output due to increased surface area.
If #2 copper were used instead, the losses ( at the array's full rated output) would be about 3.5% for a total of 131 watts or an additional loss of 49 watts over using 1/0 wire and the savings in the cost of wire would be about 30% or $250.
With panels at ~$1 a watt and less it makes sense to go with another 250 watt panel, where technically and logistically feasible, as the system would gain roughly an additional 200 watts in full sun with 3.5% downlead losses. This could become more substantial as the system size increases. One variable that I can not absolutely quantify right now is exactly how this increase in downlead resistance would effect controller performance but it seems to me it should remain linear.
Granted there are many considerations including racking costs etc. But just something to think about.
As panel prices continue to remain low and even drop some, more panels are the answer to a lot of system design and system cost problems.
If #2 copper were used instead, the losses ( at the array's full rated output) would be about 3.5% for a total of 131 watts or an additional loss of 49 watts over using 1/0 wire and the savings in the cost of wire would be about 30% or $250.
With panels at ~$1 a watt and less it makes sense to go with another 250 watt panel, where technically and logistically feasible, as the system would gain roughly an additional 200 watts in full sun with 3.5% downlead losses. This could become more substantial as the system size increases. One variable that I can not absolutely quantify right now is exactly how this increase in downlead resistance would effect controller performance but it seems to me it should remain linear.
Granted there are many considerations including racking costs etc. But just something to think about.
As panel prices continue to remain low and even drop some, more panels are the answer to a lot of system design and system cost problems.
Comments
-
Re: Considering downlead losses
Smart analysis. I am very concerned that my electric consumption be as efficient as possible, but as production (solar panels) becomes cheaper and cheaper I have become less concerned with the efficiency of production.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Considering downlead losses
3,750 Watt array at what Voltage? Up the Voltage, lower the current, reduce the losses.
Up to the point where the array Voltage (especially Voc with cold temps) becomes too high for the controller and/or the down-conversion from a high Voltage reduces controller efficiency.
Without the Voltages involved the other numbers don't mean much. -
Re: Considering downlead losses
Caribou, array voltage is at ~112 VDC OC. Three poly REC 250 watt panels in series, five strings in parallel. So a few more panels would max out a Midnite 150 controller. Same situation I came up with as far as controller choice. I found I'm better off with more panels than using a 250V controller since it won't handle as much power out and is less effecient.
Seems the new Tristar 600V controller doesn't have adjustable current limiting and doesn't have any function to use excess solar power so I don't like that either. Worse, Morningstar hasn't repiled to any of my queries about the unit.
In short I believe the Midnite 150 is the most efficient way to go and instead of going to a 200 or 250 (except for small systems) I'm better off adding panels where applicable. -
Re: Considering downlead losses
Yep; that works.
And is better than paying $1,200 for the XW 600 Volt controller. You can buy a lot of panel for $600.
Of course the losses drop as the current demand goes down too, so they won't always bee there at the max all day every day. -
Re: Considering downlead losses
yeah but how much money in wire can you save by runnng a xw 600 volt controller? -
Re: Considering downlead lossesyeah but how much money in wire can you save by runnng a xw 600 volt controller?
Probably none.
The point here is you will have losses and how you make up for it: larger wire, higher Voltage charge controller, or add some panel so that there's more power to begin with and the loss at the other end no longer matters. With copper prices high, the XW 600 2X a standard controller, and panels being in the $1 per Watt range the additional panels may be the cheapest option. -
Re: Considering downlead lossesCariboocoot wrote: »Probably none.
The point here is you will have losses and how you make up for it: larger wire, higher Voltage charge controller, or add some panel so that there's more power to begin with and the loss at the other end no longer matters. With copper prices high, the XW 600 2X a standard controller, and panels being in the $1 per Watt range the additional panels may be the cheapest option. -
Re: Considering downlead losses
Yes, as you wrote it... Marc (Cariboocoot) was saying "or"... Heavier wire or higher voltage controller.
You can save a bunch of money on wiring with higher voltages for long runs.... But if you have nominal runs and are already using a MPPT controller that can take Vmp~100 VDC STC, then you are not too bad off (in general) when compared to somebody using a PWM controller on a 12 volt battery bank.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Considering downlead lossesIsn't it smaller wire and higher voltage charge controller?
It's a $1,200 charge controller originally designed to accommodate GT arrays for people who wanted to use them during power outages as a means of recharging 24 or 48 Volt back-up battery systems.
Whereas it is true that for any given amount of power (Watts) the current goes down as the Voltage goes up this only relieves one type of loss; the Voltage drop in the line between the array and the controller. It accentuates another type; the conversion efficiency of the controller from high array Voltage to lower system Voltage.
So where do you want to lose the power, how much do you want to lose, and for what price?
It is never as simple as "this solution is the best one for everyone". -
Re: Considering downlead losses
my point was 500 feet is alot of copper, two strands of 2 awg is around $1200 if you go with a 600v charge controller you could spend less than half on smaller wire with less line loss. -
Re: Considering downlead lossesmy point was 500 feet is alot of copper, two strands of 2 awg is around $1200 if you go with a 600v charge controller you could spend less than half on smaller wire with less line loss.
But don't forget... it's 500 ft round trip... really a 250 ft span for the 2 conductors. (and maybe a ground conductor?)
Spending a few hundred dollars on copper and an extra solar panel is probably a better investment than spending a few hundred on electronics.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Considering downlead losses
Sorry I thought it was 500 feet away -
Re: Considering downlead lossesSorry I thought it was 500 feet away
So did I.
If it's 250 feet away that's a big difference. -
Re: Considering downlead losses
More or less, the basic wiring differences between array voltages:
2x higher voltage and 1/2 the current:- 1/2 less current * 1/2 higher voltage drop allowed at higher voltage = 1/4 the thickness of wire
- Every 3 American wire gauge difference is 1/2 the surface area of copper: 1/4 thickness is 6 AWG smaller wire
- 1/4 current * 1/4 higher voltage drop allowed = 1/16 the thickness of wire
- 1/16 thickness of wire is 12 AWG smaller wire
- 3,750 Watts / 90 volts = 41.7 Amps
- 3,750 Watts / 390 volts = 9.62 Amps
- 90 volts * 0.03 drop = 2.7 volt drop
- 390 volts * 0.03 drop = 11.7 volt drop
- 41.7 amps, 250 foot round trip, 2.7 volt drop max = 3.1 volt drop @ 1 AWG cable
- 9.62 amps, 250 foot round trip, 11.7 volt drop max = 9.2 volt drop @ 12 AWG cable
Which is better for you.. Don't know. Either would work fine
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Considering downlead losses
Using the Xantrex 80-600 might be feasible if the system were designed specifically for it. Considering cold weather effects it drops the upper VOC limit to ~500 V or 13 panels. Cutting 500 watts off a 3,750 watt array. -
Re: Considering downlead losses
Max VOC is 600 VDC including temp compensation. Operating range is 195 to 550 VDC. MPPT range is 195 to 510 VDC. Shows start voltage at 230 VDC.
Schneider site is currently down for maintenance as I was going to check the numbers on the array to see what was panel configurations with temp and your REC panels. Assuming you get -40 C or colder.GT3.8 w/4600W Trina 230W, TX5000 w/5000W ET-250W, XW4024 w/1500W ET-250W, 4 L16, 5500W Gen. (never had to use) Yet!! -
Re: Considering downlead lossesUsing the Xantrex 80-600 might be feasible if the system were designed specifically for it.
One design change might be overcurrent protection... no 150 volt breakers .... 600 volt fuses AND disconnects. I guess that with a single string you won't need a combiner, but it would be nice to have a disconnect at or near the array to de-energize the line to the controller.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Considering downlead lossesThree poly REC 250 watt panels in series, five strings in parallel. So a few more panels would max out a Midnite 150 controller.
Another thought.... how about aiming part of the array SE and part of the array SW? This is often called virtual tracking. Because the two parts of the array are not giving maximum current at the same time, you don't have as much line loss on the 250 ft run. You can also 'over panel' your controller a bit more.
The panels in each string of a virtual tracker should have the same exposure. You may want some asymmetry... two strings facing east and one string facing west... depends on your climate and exposure and loads. e.g. southerners with air conditioning might want to have more strings facing west for the late afternoon load.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Considering downlead losses
vtmaps,Customer won't do that. The ice can build on roofs where he is to a couple feet thick and he is worried about it taking the array off the roof. So he only wants a top of pole mount.
SkiDoo, 550 V in to the controller would likely exceed input voltage on cold days. I figure about to 638 V.
Using a high voltage controller won't improve cloudy day performance like additional panels will.
The Midnite controller will handle 96 A @ 48V. Thats about another 500 watts over the Schneider at about half the price which pays for the additional 500 watts.
Granted wire costs are reduced with HV which would also pay for the panels but then another HV controller is needed and another run of wire.
Also a big consideration is the fact that the Midnite has a superior 'use it or lose it' function allowing for excess solar power to be metered off to perform other functions like heating water. Looks like the Schneider unit has simple relay closure based on battery voltage while the Midnite uses PWM output. -
Re: Considering downlead losses
"SkiDoo, 550 V in to the controller would likely exceed input voltage on cold days. I figure about to 638 V."
that is why I would recommend 2 srings of 9 series that would add panels keep cold VOC reasonable and within range. All are suggestions to a problem presented. XW MPPT 80 600 from sponsor with a ComBox would be about $1500 plus shipping.GT3.8 w/4600W Trina 230W, TX5000 w/5000W ET-250W, XW4024 w/1500W ET-250W, 4 L16, 5500W Gen. (never had to use) Yet!! -
Re: Considering downlead losses
SkiDoo, thats probably a workable solution. I was concerned about the lower end of the operating range but this seems to reasonably quite well at ~21.6 volts per panel(loaded ) to hit op range and a 30.5 V-MPP for these panels.
If the people at Morningstar would communicate, their HV offering might have merit with a boost function starting from 5 volts.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed