Electrolysis?
Out There
Solar Expert Posts: 96 ✭✭✭✭
Gentlemen,
I've a new problem: My house was built in 1987 and the plumbing is distributed, after the pressure tank, via rigid, thin-walled copper. In the last two weeks I've had three pinhole leaks develop. I put temporary patches on the first two, then called in a plumber. He replaced the two pieces of tubing. On the pieces he took out there is an obvious but extremely localized erosion visible on the inside of the tubing and relegated to a tiny area around the pinhole. The spot of erosion shows the green patina of oxidized copper but this is not spread anywhere else on the inside of the tubing. Within a couple hours of him having fixed those two leaks, we sprung another.
The plumber has suggested electrolysis as the culprit. He didn't think the system was grounded. Upon my investigation, I DO find a ground wire securely clamped to the fitting where my pressure gauge and switch are located. This ground is connected to the 110 volt distribution panel's ground/neutral bar.
I have read where systems like mine, being subjected to dissolved minerals in slightly acidic water left sitting in copper over long periods of time can create - in effect - many small "batteries", which would seem to support the extremely localized nature of my "erosions".
Any thoughts?
Brian
I've a new problem: My house was built in 1987 and the plumbing is distributed, after the pressure tank, via rigid, thin-walled copper. In the last two weeks I've had three pinhole leaks develop. I put temporary patches on the first two, then called in a plumber. He replaced the two pieces of tubing. On the pieces he took out there is an obvious but extremely localized erosion visible on the inside of the tubing and relegated to a tiny area around the pinhole. The spot of erosion shows the green patina of oxidized copper but this is not spread anywhere else on the inside of the tubing. Within a couple hours of him having fixed those two leaks, we sprung another.
The plumber has suggested electrolysis as the culprit. He didn't think the system was grounded. Upon my investigation, I DO find a ground wire securely clamped to the fitting where my pressure gauge and switch are located. This ground is connected to the 110 volt distribution panel's ground/neutral bar.
I have read where systems like mine, being subjected to dissolved minerals in slightly acidic water left sitting in copper over long periods of time can create - in effect - many small "batteries", which would seem to support the extremely localized nature of my "erosions".
Any thoughts?
Brian
Comments
-
Re: Electrolysis?
Try to find out if you have Chinese sheet rock. It was doing that type of thing to copper pipes IIRC in an article in the news. Do a search and find out more.
Good luck and let us know!
Skip12K asst panels charging through Midnite Classic 150's, powering Exeltechs and Outback VFX-3648 inverter at 12 and 48 volts. 2080 AH @ 48 VDC of Panasonic Stationary batteries (2 strings of 1040 AH each) purchased for slightly over scrap, installed August 2013. Outback PSX-240X for 220 volt duties. No genny usage since 2014. -
Re: Electrolysis?
Unfortunately, "thin wall" copper pipe tends to do this, particularly if the water is low ph or otherwise corrosive.
Traditionally, for this reason, only thick wall copper pipe was used in home plumbing. The thin was stuff was only used in residential hot water heating systems that were sealed from the atmosphere and didn't have it's water changed.
Some years ago however, due to copper's high price, the thin wall stuff became common in regular plumbing, and you are seeing the results.
Yesteryear's professional plumbers would never recommend thin wall copper.
Today, copper is more and more rare in new construction as new, very reliable substitutes are available. -
Re: Electrolysis?Try to find out if you have Chinese sheet rock. It was doing that type of thing to copper pipes IIRC in an article in the news. Do a search and find out more.
Good luck and let us know!
Skip -
Re: Electrolysis?
Some thoughts:
http://www.repairmyleak.com/about/failure-copper.htmCopper (Pitting) Corrosion
There are many forms of corrosion, but pitting corrosion is most likely to culminate in pinhole leaks in copper plumbing.
Pitting corrosion is the non-uniform localized attack of the wall of copper tube, pipe, or fittings initiated on the inside surface of copper water pipes. Usually only small areas of the metal surface are attacked.
Pitting corrosion can be classified into three types:Type IWater Velocity
cause: Hard Water
Type I pitting is associated with hard or moderately hard waters with a pH between 7 and 7.8, and it is most likely to occur in cold water. The pitting is deep and narrow, and results in pipe failure.
Type II
cause: Soft Water
Type II pitting occurs only in certain soft waters, with a pH below 7.2 and occurs rarely in temperatures below 140° F. The pitting that occurs is narrower than in Type I, but still results in pipe failure.
Type III
cause: Cold, Soft Water High PH
Type III pitting occurs in cold soft waters having a pH above 8.0. It is a more generalized form of pitting, which tends to be wide and shallow and results in blue water, byproduct releases, or pipe blockage.
When copper tubing is installed that is too small in diameter for the pressure and flow available, the resulting high flow rates can erode the protective coating creating areas of bare, unprotected copper. This effect can result in a high rate of corrosion wherever the protective coating is eroded.
The greatest effect of velocity occurs where the water is forced to change flow direction, such as at elbows and tees, but excessive water flow rates can be damaging to the entire plumbing system.
Here is a 2004 Maryland water company(ies?) report on a study of pin-hole leaks in copper plumbing:
http://www.wsscwater.com/file/EngAndConst/InfrastructSystems/Study%20of%20Pinhole%20leaks%20Report.pdf
In their report--They do not know is the simple answer. It appears that chlorination+aluminum solids are really hard on copper pipes. Electrolysis, grounding, lightning appeared to have no affect. If aluminum solids are a problem, I wonder of a whole house filter would help (nothing mentioned in report).
If your leaks are on the hot water side copper, I wonder if it is the Water Heater Anode Rod... Some are magnesium and others are aluminum (or aluminum/zinc).
http://www.waterheaterrescue.com/pages/WHRpages/English/Longevity/water-heater-anodes.html
Call your water company and report the problem. Replace bad pipe (or re-pipe whole home). Use alternative materials.
I have had issues where contractors (and homeowners) have used galvanized pipe in copper plumbing for the last 6" (instead of brass or copper). But the little I have seen that, the galvanized pipe is usually the loser.
Water heaters (steel tanks) usually used galvanic isolation couplings (to reduce corrosion in the steel tank). Normally not used on the rest of the copper to copper plumbing system.
Another cause of localized corrosion is the use of steel pipe hangers and Nailing Protectors (used under drywall over copper and electrical runs to stop drywall fasteners from causing damage in through stud piping/electrical) that rest directly against copper pipe--Need to have a piece of plastic insulation between steel and copper if there is physical contact.
There was a change from Chlorine treatment use by water companies to Chloramine based water treatment in over the last decade or so. There are lawsuits in recent years claiming that the change to Chloramine has caused pin-hole leaks in copper piping.
http://www.ocregister.com/articles/water-340682-leaks-copper.html
That is what I have read about the issue... Almost makes me want to change to PEX plastic piping instead.Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Electrolysis?Gentlemen,
I've a new problem: My house was built in 1987 and the plumbing is distributed, after the pressure tank, via rigid, thin-walled copper. In the last two weeks I've had three pinhole leaks develop. I put temporary patches on the first two, then called in a plumber. He replaced the two pieces of tubing. On the pieces he took out there is an obvious but extremely localized erosion visible on the inside of the tubing and relegated to a tiny area around the pinhole. The spot of erosion shows the green patina of oxidized copper but this is not spread anywhere else on the inside of the tubing. Within a couple hours of him having fixed those two leaks, we sprung another.
The plumber has suggested electrolysis as the culprit. He didn't think the system was grounded. Upon my investigation, I DO find a ground wire securely clamped to the fitting where my pressure gauge and switch are located. This ground is connected to the 110 volt distribution panel's ground/neutral bar.
I have read where systems like mine, being subjected to dissolved minerals in slightly acidic water left sitting in copper over long periods of time can create - in effect - many small "batteries", which would seem to support the extremely localized nature of my "erosions".
Any thoughts?
Brian
Brian,
I would look at the generator also. It sounds like you are offgrid and the generator could be defective. One neutral bond only correct?
--Dave"we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Re: Electrolysis?Dave Angelini wrote: »Brian,
I would look at the generator also. It sounds like you are offgrid and the generator could be defective. One neutral bond only correct?
--Dave
I do believe there is only one neutral. In this state, ground and neutral are tied, so that's how I'm set up. How does the generator create this problem?
Brian -
Re: Electrolysis?
All three leaks have formed on the cold water side. We have also detected ferrobacteria in the well water, which thrive in an acid environment. The house was also unoccupied for over a year. -
Re: Electrolysis?
Disinfecting the well? Hot water through cold water pipes? Flushing pipes on a regulator schedule?
http://www.lenntech.com/iron-bacteria.htm
Beyond my knowledge.
Good luck,
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Electrolysis?Disinfecting the well? Hot water through cold water pipes? Flushing pipes on a regulator schedule?
http://www.lenntech.com/iron-bacteria.htm
Beyond my knowledge.
Good luck,
-Bill -
Re: Electrolysis?I'm thinking of asking the seller to contribute to re-plumbing the house with PEX or CPVC.
Did you get a home-buyer insurance policy ? Does it cover pipes? Re-plumb is the only answer, likely all the pipe came from the same batch, and the rest is likely to quickly fail too. Electrolysis would be localized to near any metal interfaces.
I'd re-do it with PEXPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Electrolysis?
Look on the outside of the pipe for the makers name and other info. The name Wolverine was a brand found in the 80's to have a manufacturing defect that cause your problem.
hth
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: Electrolysis?westbranch wrote: »Look on the outside of the pipe for the makers name and other info. The name Wolverine was a brand found in the 80's to have a manufacturing defect that cause your problem.
hth
Thanks!
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed