battery current ratings
Organic Farmer
Solar Expert Posts: 128 ✭✭
I was looking at golf-cart / floor sweeper batteries, and trying to compare numbers. It seems that the abilities of batteries are a wide spectrum.
So I looked at a few random Trojan batteries and I see that they do not have one single current rating, but a table of ratings over time.
To compare apples to apples, I need to first know which hour's rating for current is the one I should be looking at.
Can anyone explain how this system works, please?
So I looked at a few random Trojan batteries and I see that they do not have one single current rating, but a table of ratings over time.
To compare apples to apples, I need to first know which hour's rating for current is the one I should be looking at.
Can anyone explain how this system works, please?
Comments
-
Re: battery current ratings
The standard used for RE application is the "20 hour rate": how much it can managed discharged over a period of 20 hours. Some batteries will have a 24 hour rate, which can also be used as the difference between the two is fairly small.
The shorter the hour rate the higher the discharge rate and the lower the overall capacity. -
Re: battery current ratings
Okay, Thank you.
-
Re: battery current ratings
not to hijack your thread but I had a question to do with this,
I was looking at some Surette's this afternoon, they said 460 AH......but when I read the specs it said 460 @ 100hrs.....so does mean you would divide that by five? they're really 92HR?
Sorry this is something that was confusing me as well, as they didn't list a 20hr rating -
Re: battery current ratingsnot to hijack your thread but I had a question to do with this,
I was looking at some Surette's this afternoon, they said 460 AH......but when I read the specs it said 460 @ 100hrs.....so does mean you would divide that by five? they're really 92HR?
Sorry this is something that was confusing me as well, as they didn't list a 20hr rating
Unfortunately it is not linear. There is a quite complicated formula involving Peukart's Law for converting one "hour rating" to another. You can find info on it here: http://www.smartgauge.co.uk/technical1.html#peukert
Concorde has this chart which show the same batteries at various discharge rates: http://www.solar-electric.com/concorde-sun-xtender-pvx-solar-deep-cycle-batteries.html Alas not 20 hour or 100 hour. -
Re: battery current ratings
the muddle of hour rates, reminds me of 70's stereo power ratings. 385 peak watts into 3 ohms w/20% distortion (or 23 RMS watts) (or 5 pure sinewave watts) No brand matched any other brand.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: battery current ratings
And different types of batteries will have different 20 vs 100 Hour ratings...
AGM batteries have very low "internal resistance" so that the 20 hour vs 100 hour capacity ratings will be similar.
Flooded cell deep cycle batteries have more "internal resistance" and will have a wider spread between 20 hour and 100 hour ratings.
The Peukert number is an experimental value that takes into account both true electrical resistance and electro/chemical activity of the plates+acid+etc....
The "Hour Rate" is dependent on how fast you discharge (and recharge) the battery bank... 20 hours works out pretty well for Off Grid...
Assume 5 hours per night to 50% discharge. That is 10 hours to 50% or 20 hours to 100% discharge (aka 20 hour discharge rate).
C/20 is also the 5% "minimum" recharging rate we recommend. C/10 is the 10% rate--and as you can guess, it a little bit less efficient at charging (higher current means a little more waste heat being dissipated).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: battery current ratingsAssume 5 hours per night to 50% discharge. That is 10 hours to 50% or 20 hours to 100% discharge (aka 20 hour discharge rate).
typo: should be Assume 5 hours per night to 25% discharge.
Bill, please delete this post if you edit yours --vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: battery current ratings
Here are some of the Rolls that are for RE, they list the 100, 20 & 10 hour rates.
http://www.rolls-battery.com/content/specifications-renewable-flooded
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed