New to me 1040 AH stationary batteries
H2SO4_guy
Solar Expert Posts: 213 ✭✭✭
Panasonic MSE-1040AT 2 volt cells are $65 each, and I can trade in a bunch of my older batteries on these with the difference being $.14 per pound. The cells all read 2.15 or 2.16 volts so they are charged, and just pulled out of service I believe from a telco.
The goal is to get at least one string of 48 volts and have spare cells to replace the ones that will go bad in the future. At 1040 AH at the 8 hour rate, I shouldn’t have to cycle these too deeply. This should run the AC overnight!
There are many pallets of these and it seems such a shame to not get some more use out of them before recycling.
12K asst panels charging through Midnite Classic 150's, powering Exeltechs and Outback VFX-3648 inverter at 12 and 48 volts. 2080 AH @ 48 VDC of Panasonic Stationary batteries (2 strings of 1040 AH each) purchased for slightly over scrap, installed August 2013. Outback PSX-240X for 220 volt duties. No genny usage since 2014.
Re: New to me 1040 AH stationary batteries
that is the 8 hr rate so you will get more at the 20 hr rate. probably in the 1100Ah range if they are similar to mine, I gained about 100 Ah between 8 and 20 hrs. can't find a large table , so you might have to go to their web site and request it. here is a link https://panasonic.ca/english/batteries/industrialbatteries/mse1040_specs.asp
Interesting looking cells...
https://panasonic.ca/english/batteries/industrialbatteries/mse_1040.asp
Not sure why they give such a low charging voltage (2.25 volts per cell--13.5 volts @ 12 volt battery bank)... Maybe that is the float voltage:
MSE-1040AT VRLA Battery Specifications
Nominal Voltage
2 Vpc
Rated Capacity
(8 hr rate @ 1.75Vpc)
1040 Ahr
Dimensions
Height
580 mm (22.84 in)
Width
245 mm (9.65 in)
Length
183 mm (7.19 in)
Weight
66 Kg (146 lbs)
Material
Polypropylene
UL 94 V-0 > 28% LOICharacteristics:
Capacity
25ºC (77ºF ) 1.75V
8 hour
1040 A
6 hour
978 A
2 hour
698 A
1 hour
528 A
Self-Discharge
25ºC (77ºF)
3 months
91%
6 months
82%
12 months
64%
18 months
50%
Internal Impedance
Full charge @ 25ºC (77ºF)
0.33 milliohms
Max. Discharge
(1minute duration)
2CA
2080 A
Termination Type:
6 mm INSERT
Torque
41 in/lb
Charge Voltage @ 25ºC (77ºF)
2.23~2.25 Vpc
Max Charge Current
(0.3C-0.4C Recommended)
416 A
"Stationary" - as opposed to moving...:p
Seriously though - what do those guys weigh - 150lbs? Stationary indeed.(oh - I see Bill posted the specs, 146 lbs - i was close)
Voltage is somewhat helpful but load testing them would be the only way to really know their condition. -
I can't load test, but they all read between 2.15 and 2.17 volts. I committed to 54 cells, so there will be 2 48 volt strings and 1 12 volt string to keep on float to use as spare cells for when any die and need replacement. On other AGM batteries I have been using from the Telco I charge at 2.36 vpc, which is 14.2 per 12 volts. I just turned in a 115 AH 48 vdc pack that I could still get about 1 kwh usable and they were from 2000. Just wanted the weight to use for trade in to lessen the cash outlay somewhat.
Doing the math if I don't count the core charge, I am into these for about $1100 for 112 kwh of power. I can't buy 2 strings of golf cart batteries for that little and I hope to have power for many years, but I'll keep everyone posted. Lead tends to keep up with inflation, so I sure don't mind having 10,000 pounds of batteries laying around either.12K asst panels charging through Midnite Classic 150's, powering Exeltechs and Outback VFX-3648 inverter at 12 and 48 volts. 2080 AH @ 48 VDC of Panasonic Stationary batteries (2 strings of 1040 AH each) purchased for slightly over scrap, installed August 2013. Outback PSX-240X for 220 volt duties. No genny usage since 2014. -
Discounting the core charge, What was the core charge? To get out of the core charge did you need like size batteries?
gww
Ps Did you go through the pallets and pick and choose the batteries you wanted? -
Well, I used the phrase 'Core charge', but it is just really weight. It worked out to about 7,893 pounds of batteries that I paid for. There were tons (literally) of batteries traded in and I paid the difference. If I scrapped them tomorrow, the cost difference would be about $1100. So in reality, if the price of lead does not go down, I'm into 54 of the 1040 AH 2 volt cells for about $1100. I can't buy 2 48 volt strings of anyone's golf cart batteries for that kind of money. I thought it was a great deal, but I'll let you know. It is an $1100 gamble, but that is kind of the way life is. I have spares of the same type / brand / age to plug in if need be, so I hope to keep them going for awhile. As Vic says, YMMV!!!
I did go through the pallets, but ALL of them were within .02 volts. They are all likely in very good condition. It is sad to see the rest of them go to the smelter.12K asst panels charging through Midnite Classic 150's, powering Exeltechs and Outback VFX-3648 inverter at 12 and 48 volts. 2080 AH @ 48 VDC of Panasonic Stationary batteries (2 strings of 1040 AH each) purchased for slightly over scrap, installed August 2013. Outback PSX-240X for 220 volt duties. No genny usage since 2014. -
What town were they located in? 54 batteries at $65 ea no core charge if bought outright ($3500)? Maby I should consider 30 of them.
gww -
Hey all did anyone come to any conclusions on ideal charging voltage for these?
I am running 2 series of 6 at 12V on my system.
they seem to work great, I currently have my MPPT controller set for 14.5V absorption charge
I am curious though if these batteries should have an equalization charge or not? also if maybe my absorption charge is too high..
Thanks! -
Do NOT equalize. I can get you the charging parameters this weekend that I use if you like.12K asst panels charging through Midnite Classic 150's, powering Exeltechs and Outback VFX-3648 inverter at 12 and 48 volts. 2080 AH @ 48 VDC of Panasonic Stationary batteries (2 strings of 1040 AH each) purchased for slightly over scrap, installed August 2013. Outback PSX-240X for 220 volt duties. No genny usage since 2014. -
Re: New to me 1040 AH stationary batteriesDo NOT equalize. I can get you the charging parameters this weekend that I use if you like.
Great thanks, I'll turn of equalization tomorrow then..
Yeah those specs would be very helpful
I'm using an Morningstar MPPT 60Amp -
Which batteries do you have?
I have used these charging numbers for all of the lead-calcium AGM batteries that I have ever had. I got rid of a set that were still working that were 13 years old because I needed the trade-in weight for the current ones. They weighed 624 pounds for 115 AH @ 48 VDC. I did hate to get rid of them, but it would have required an additional charge controller and panels switched to them occasionally to charge them. Was running short on cash at the time and didn't want to make the additional investment in equipment at the time and I was getting tons (literally hehe) of new (Used) batteries. Now I even heat with those batteries sometimes! I'll bet not too many heat their living quarters with a $1300 battery pack.
I'll get back by next week with the charging specs I use. Keep in mind that YMMV (As Vic says).
Skip12K asst panels charging through Midnite Classic 150's, powering Exeltechs and Outback VFX-3648 inverter at 12 and 48 volts. 2080 AH @ 48 VDC of Panasonic Stationary batteries (2 strings of 1040 AH each) purchased for slightly over scrap, installed August 2013. Outback PSX-240X for 220 volt duties. No genny usage since 2014. -
I've got MSE 1040Ah in 2x series of 6 for 12V system..
Do you think 14.5 is an OK charging voltage?
I turned off equalization..
I have an Morningstar MPPT-60 and PWM T-60 -
I checked my numbers to be exact and I use 14.2 absorb (For 12 volts) for charging, 13.55 float, and 14.2 for EQ. That way if the batts are in float and I'm using quite a bit, I can set an EQ cycle and it is like some extra absorb time. It works for me and that is what I have done with several different AGM batteries, however, I am using used Lead-calcium batteries. I have had very good luck with them over the years. Right now my production sucks! Only 2.1 kwh total in 2 days! Not so much sun here, just cloudy and barely making any power. Conserve, conserve, conserve!12K asst panels charging through Midnite Classic 150's, powering Exeltechs and Outback VFX-3648 inverter at 12 and 48 volts. 2080 AH @ 48 VDC of Panasonic Stationary batteries (2 strings of 1040 AH each) purchased for slightly over scrap, installed August 2013. Outback PSX-240X for 220 volt duties. No genny usage since 2014.
- 651 Solar Water Pumping
- 611 Discussion Forums/Café
