wire length
ws9876
Solar Expert Posts: 448 ✭✭✭
24 volt set up
would this work...?? the wire from the batteries to the inverter 26ft and from the inverter to the mains 26 ft..
and does it hurt an Outback inverter if it freezes once in a while when its not in use and unplugged in a winter season..??
would this work...?? the wire from the batteries to the inverter 26ft and from the inverter to the mains 26 ft..
and does it hurt an Outback inverter if it freezes once in a while when its not in use and unplugged in a winter season..??
Comments
-
Re: wire length
What size wire do you expect to use and at 24v? the line loss will be high at 26 feet x 2 (Pos and Neg)
Just off the top I would minimize the distance @ 24V and max the 110/220 V distance.
ps mine is measured in inches not feet... #OO welding cable
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: wire lengthwould this work...?? the wire from the batteries to the inverter 26ftand from the inverter to the mains 26 ft.and does it hurt an Outback inverter if it freezes once in a while when its not in use and unplugged in a winter season..??
-
Re: wire length
Would it not be possible to locate your inverter right beside the batteries, limiting the cable lengths to just 3 or 4 feet MAX, then run the high voltage AC the rest of the way? Would be hugely more efficient in more ways than one.
Re temp range, most if not all Outback inverters are rated to operate in temps at least as low as minus 25 C, that's well below Zero F ( -18C ). It may operate slightly out of spec at these low temps, but shouldn't hurt it whatever. I've got 4 different brands of inverters, and all have every Winter, to sometimes operate below zero F ( -18C ) and have never had a problem. -
Re: wire length
It all depends on the size of the system. What is the maximum current you expect? -
Re: wire lengthand does it hurt an Outback inverter if it freezes once in a while when its not in use and unplugged in a winter season..??
Since I disconnect mine every Winter and let it sit while the temps drop to as low as -40 I'd say no; it won't hurt it at all. Mine fires up fine every Spring.
As for the wire length, just what the others have said: make your longest run at the highest Voltage. -
Re: wire length
if it doesnt hurt the inverter to sit on or off in cold temps then I have no problem. When I do batteries here I want to put them in a lined sub terra hole
about 6 ft down so they dont freeze. With that in mind and because I wanted to mount an inverter in the next room it would be about 25 ft.I guess I wont do that.
Aside from all this..... what is the max wire distance to the mains from an Inverter 2500 watt ....and what size wire would you use for that if you were doing it?? -
Re: wire lengthwhat is the max wire distance to the mains from an Inverter 2500 watt ....and what size wire would you use for that if you were doing it??
You mean 120 VAC output @ 2500 Watts? That's roughly 20 Amps, so it should be 12 AWG minimum to handle the current. As for distance ... 12 AWG will be over 3% V-drop after about 55 feet. 10 AWG will do 'til around 90 feet. 8 AWG to 140 feet. 6 AWG to 220 feet.
The larger the wire size, the less V-drop over a given distance at the current. Likewise it can handle greater distance at the same V-drop and current, or the same V-drop and distance with greater current.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed