Gulf Island Off-Grid System - Part 5 (Surge Suppression)

One of the remaining items on the list for our new solar system is surge suppression. We rarely have lightning, but when it happens, it can be quite spectacular and intense.

We figure that we're at risk of transient surges due to two factors:
  1. Our solar array is on a ridge at a high point.
  2. We have some pretty long AC cable runs (500 feet to building 1, 500 feet to building 2, and 250 feet to the array)

Here's what we're looking at installing, and we wanted some feedback to see if this is sufficient levels of protection.
  • To protect the solar panels, both strings will be connected to ground through a Midnight MNSPD600.
  • To protect the AC side of the inverters located under the panels, a Midnight MNSPD300 will be installed into the panel AC load centre.
  • To protect the AC systems in the container (Sunny Island, etc), a Square D TVSS will be installed connected to the main AC load centre.
  • To protect the AC systems in each of the two buildings, a MNSPD300 will be installed at the service panel of each building.
  • For data communication, Ethernet cable is protected using a B&B Ethernet Surge Suppressor, and RS-485 runs will be protected using a B&B RS-485 Surge Suppressor.

Still "yet-to-spec" is a phone line surge suppressor.

So, our questions are:
  1. Is this sufficient? There will be a SPD at each end of each long cable run.
  2. Do we need protection at each end of each data run? In the past, I've typically seen it only installed on the "more expensive" end of each run.
  3. Anything else that we might be missing?

Thanks!
House: 2x SMA SI 6048 w 24x 2V DEKA Unigy II; 2x SMA SB 3000TL-US w 24x Sharp ND-H235Q2
Cabin: 1x Magnum MS4024 w 24x 2V DEKA Unigy II; 1x Morningstar TS-MPPT-60 w 6x Sharp ND-H235Q2; 1x 200 Watt Harris microhydro
Intertie: 1x SMA WB 3800; 1x Lambda GEN-600 DC Supply; 2x PSL pQube