Gulf Island Off-Grid System - Part 5 (Surge Suppression)
David and Laura
Solar Expert Posts: 139 ✭
One of the remaining items on the list for our new solar system is surge suppression. We rarely have lightning, but when it happens, it can be quite spectacular and intense.
We figure that we're at risk of transient surges due to two factors:
Here's what we're looking at installing, and we wanted some feedback to see if this is sufficient levels of protection.
Still "yet-to-spec" is a phone line surge suppressor.
So, our questions are:
Thanks!
- Our solar array is on a ridge at a high point.
- We have some pretty long AC cable runs (500 feet to building 1, 500 feet to building 2, and 250 feet to the array)
- To protect the solar panels, both strings will be connected to ground through a Midnight MNSPD600.
- To protect the AC side of the inverters located under the panels, a Midnight MNSPD300 will be installed into the panel AC load centre.
- To protect the AC systems in the container (Sunny Island, etc), a Square D TVSS will be installed connected to the main AC load centre.
- To protect the AC systems in each of the two buildings, a MNSPD300 will be installed at the service panel of each building.
- For data communication, Ethernet cable is protected using a B&B Ethernet Surge Suppressor, and RS-485 runs will be protected using a B&B RS-485 Surge Suppressor.
- Is this sufficient? There will be a SPD at each end of each long cable run.
- Do we need protection at each end of each data run? In the past, I've typically seen it only installed on the "more expensive" end of each run.
- Anything else that we might be missing?
Thanks!
House: 2x SMA SI 6048 w 24x 2V DEKA Unigy II; 2x SMA SB 3000TL-US w 24x Sharp ND-H235Q2
Cabin: 1x Magnum MS4024 w 24x 2V DEKA Unigy II; 1x Morningstar TS-MPPT-60 w 6x Sharp ND-H235Q2; 1x 200 Watt Harris microhydro
Intertie: 1x SMA WB 3800; 1x Lambda GEN-600 DC Supply; 2x PSL pQube
Re: Gulf Island Off-Grid System - Part 5 (Surge Suppression)
Not my wallet--But I would install suppressors on both sides of long wire runs where they enter the buildings. You have the equipment you are protecting--And the people in the area too.
there are some threads over on the MidNIte site on SPD's and their choice and placement.
http://midniteforum.com/index.php?board=13.0
Re: Gulf Island Off-Grid System - Part 5 (Surge Suppression)David & Laura wrote: »[*] Do we need protection at each end of each data run? In the past, I've typically seen it only installed on the "more expensive" end of each run.
[*] Anything else that we might be missing?
[/LIST]
Thanks!
Well, depends on how expensive the "less expensive" end is. A surge protector at the far end of a long data line will not protect semiconductors at the near end from pulse type surges.
So if the equipment directly connected to the data line costs more than the surge suppressor, OR will be hard to replace and is critical to the operation of the system, go ahead and add suppressor to both ends.SMA SB 3000, old BP panels. -
For the phone surge suppression, we're leaning towards this Sixnet product:
http://www.sixnet.com/dist/SP-TELCO_datasheet.pdf
They run for around $50 each.
Re #2, #4 - Given the feedback, we're also going to put protection on both ends of our RS-485 runs. Replacing an inverter isn't something that we'd like to do...
Re #3 - Not too much there that isn't already well covered on the NAWS forums...House: 2x SMA SI 6048 w 24x 2V DEKA Unigy II; 2x SMA SB 3000TL-US w 24x Sharp ND-H235Q2
Intertie: 1x SMA WB 3800; 1x Lambda GEN-600 DC Supply; 2x PSL pQube -
The RS-485 surge suppressor is now installed, so our Sunny Island Inverters are protected.
We also added a little box up at the solar array to hold the RS-485 and Ethernet protector that we will be installing.
There is also a Midnight MNSPD300 installed in the load centre (but not visible in the photo).
Next trip: Installing the remainder of the Midnight SPDs, and the Square D TVSS.
Attachment not found. Attachment not found.House: 2x SMA SI 6048 w 24x 2V DEKA Unigy II; 2x SMA SB 3000TL-US w 24x Sharp ND-H235Q2
The Square D TVSS panel came in the mail, and it looks like the USPS dropped it! The upper flange is bent almost 90 degrees.
Drat.
Now I'm having to deal with their damaged shipment bureaucracy.House: 2x SMA SI 6048 w 24x 2V DEKA Unigy II; 2x SMA SB 3000TL-US w 24x Sharp ND-H235Q2
Theres a little Heizenberg uncertainty principle image forming in my mind when i look inside that box. Out of curiousity how much power does all that monitering gear actually draw?1.8kWp CSUN, 10kWh AGM, Midnite Classic 150, Outback VFX3024E,
Re #8 - Very very little, under 1/3 of an amp at 48 volts. I'll clamp it and get you an exact measurement, as it's something on the to-do list.House: 2x SMA SI 6048 w 24x 2V DEKA Unigy II; 2x SMA SB 3000TL-US w 24x Sharp ND-H235Q2
Hi D&L,
Very well researched project you have in motion.
Re. lightning surge protection, have you installed your hydro and if so, how do you protect your (presumably long) Hydro cable run? How has your experience with Hydro been in general?Outback Flexpower 1 (FM80, VFX3048E-230v, Mate, FlexNetDC) 2,730watts of "Grid-type" PV, 370 AmpHrs Trojan RE-B's, Honda 2000 watt genny, 100% off grid. -
Re #10 - Our cabin system has a small Harris waterwheel connected with a very long power cable. The waterwheel puts out around a hundred volts, which is stepped down to close to 24 volts, regulated, and connected to the battery. It's part of an older setup that we inherited when we purchased the property, and isn't very well protected. But because it is connected to the battery, it does have a (slightly) higher ability to withstand a surge.
Since that's on our smaller system, we haven't done a full lightning surge assessment like we have with our new system. It has some older Delta protectors that we may want to replace with Midnite SPCs too.
Our existing wheel puts out 200 watts 24/7 during the winter months, and really helps keep the battery topped up when we have weeks (or months) of clouds and rain). We're looking at replacing it with a PowerSpout ME 250 or PowerSpout GE400, but that would be a project for the next year or the year after. This winter, when we have water again, we'll measure the pressure so that we know exactly how much power potential we actually have.House: 2x SMA SI 6048 w 24x 2V DEKA Unigy II; 2x SMA SB 3000TL-US w 24x Sharp ND-H235Q2
We weren't too happy with the B&B RS-485 surge protector we have installed, so we ordered a set of Dehn BLITZDUCTOR BVT RS485 SPDs to replace it and provide protection on both ends of the RS-485 line.
http://www.dehn-usa.com/pdf/Cat2005/pgs%20176-181%20Blitzductor%20VT.pdf
This is a much nicer product from a mounting and termination standpoint, and has better specs.House: 2x SMA SI 6048 w 24x 2V DEKA Unigy II; 2x SMA SB 3000TL-US w 24x Sharp ND-H235Q2
The Square D TVSS is now installed and operational:
We also have DC protection installed at the solar array:
That completes the installation of the surge suppression equipment. While this won't help us if there is a direct lightning strike to our system, it should reduce the probability of damage from a nearby strike.