48V battery bank help
csspring
Registered Users Posts: 3 ✭
Re: 48V battery bank help
Welcome to the forum.
Your wiring is not optimal and will lead to charge imbalance in the batteries. You need bus bars.
Look at method #3 on this page: http://www.smartgauge.co.uk/batt_con.html
Also, you should read more about parallel batteries and buy a DC current clamp meter:
http://forum.solar-electric.com/showthread.php?14674
It should look more like this (at least electrically). -
It will be a little bit less messier if you orient all the batteries in the same direction. -
With 3 or more strings, I would highly suggest a series fuse or breaker per string. Like these Bluesea fuse holders (fuses extra) at a minimum (breakers are very nice because you can turn of power for servicing--but even more expensive):
Attachment not found.Attachment not found.
I would suggest that each string's wiring+fuse be rated for 100% of your expected maximum sustained current (note: actually 1.25*100% or 125% of maximum load--NEC derating for wiring and protective devices).
If you go with 4 or more parallel strings, You may get away with 50% of maximum bank rated current wiring (and fusing).
Also--Each cable that leaves the bus bar should have (for safety) a fuse or breaker to protect down stream wiring in the case of a fault/short down stream. Lead Acid batteries can output 100's to 10,000's of Amperes into a dead short.