Can AC neutral and ground wire share the same bus?
Comments
-
Re: Can AC neutral and ground wire share the same bus?
The thing is, I think if you buy the Power Distribution Panel for the XW (or the equivalent for the Outback system) that is already properly labeled or marked. Being I wanted to do it with the QO Load Centers the inspector looked it over and even made me take the covers off the boxes so he could see how it was wired inside. I had completely forgotten about the labeling requirement until he pointed it out - and the stickers came with the new box when I bought it.
--
Chris -
Re: Can AC neutral and ground wire share the same bus?And that would be lethal, right, if the GFCI didn't trip?
-
Re: Can AC neutral and ground wire share the same bus?
Quote Originally Posted by inetdog View Post
What a lot of people do not realize is that a GFCI wired onto a two wire circuit will still give you the same protection ...If the energy source is not grounded, there's no alternative route for the current. All current will always go through GFCI, so it'll never trip. In fact, if there's no ground, it's nothing that GFCI can protect you from. -
Re: Can AC neutral and ground wire share the same bus?That is not correct. If a two pronged appliance has a current path to ground exterior to its conductors, the current in the neutral will be different from that in the hot, and the GFCI will trip. I have some Christmas lights in the trees in front of my house that are on two conductor wiring and on a GFCI outlet, and when it rains when they are on, the GFCI trips.
In order for current to flow, you need a closed circuit.
Normal circuit: Source - Hot wire - GFCI - Load - GFCI - Neutral wire - Source. GFCI does not trip because current is the same in and out
Danger: Source - Hot wire - GFCI - you - Ground - Neutral wire - Source. GFCI trips because there's more current in than out.
If Neutral is not connected to the Ground, you don't get zapped because the circuit is not completee:
Source - Hot wire - GFCI - you - Ground --- broken here --- Neutral wire - Source. GFCI doesn't trip because current doesn't flow.
As to your Christmas lights, the neutral is definitely connected to the ground (or at least must be by codes). If Neutral were left floating, GFCI wouldn't trip. -
Re: Can AC neutral and ground wire share the same bus?No. Since the plastic bucket is not grounded, the current path of the short would be entirely within the hair dryer and the conductors connected to it.
But if you are in the bucket with the hair dryer, the voltage gradient in the water around the dryer may still be enough to harm you. I do not intend to perform that experiment. :-) And if instead of an isolated plastic bucket, you are in a fiberglass tub with a grounded metal drain pipe, the GFCI will blow and you will also be a likely part of the current path.SMA SB 3000, old BP panels. -
Re: Can AC neutral and ground wire share the same bus?
Might be a good time to put in the electrician 'trick' of working on things one handed or keeping a glove on the non primary hand and insulated shoes/boots, so if you are part of a curcuit, the current doesn't run across your heart...Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
- Assorted other systems, pieces and to many panels in the closet to not do more projects. -
Re: Can AC neutral and ground wire share the same bus?In order for current to flow, you need a closed circuit.
Normal circuit: Source - Hot wire - GFCI - Load - GFCI - Neutral wire - Source. GFCI does not trip because current is the same in and out
Danger: Source - Hot wire - GFCI - you - Ground - Neutral wire - Source. GFCI trips because there's more current in than out.
If Neutral is not connected to the Ground, you don't get zapped because the circuit is not completee:
Source - Hot wire - GFCI - you - Ground --- broken here --- Neutral wire - Source. GFCI doesn't trip because current doesn't flow.
As to your Christmas lights, the neutral is definitely connected to the ground (or at least must be by codes). If Neutral were left floating, GFCI wouldn't trip.
Quote Originally Posted by inetdog View Post
What a lot of people do not realize is that a GFCI wired onto a two wire circuit will still give you the same protection
A two wire circuit has the neutral tied to ground at the service. A leakage path to earth ground completes a circuit and the GFCI will trip.
No one said anything about a floating neutral. If the neutral were floating, then the GFCI would not trip, but neither would it shock you if there were no other paths to ground. Of course, your home system would have other problems if it were 240V split phase. -
Re: Can AC neutral and ground wire share the same bus?No one said anything about a floating neutral. If the neutral were floating, then the GFCI would not trip, but neither would it shock you if there were no other paths to ground. Of course, your home system would have other problems if it were 240V split phase.
Floating neutral is common with small portable generators and mobile inverters for the reasons mentioned. However, it is not legal in a residence in the US or Canada.
--
Chris -
Re: Can AC neutral and ground wire share the same bus?No one said anything about a floating neutral. If the neutral were floating, then the GFCI would not trip, but neither would it shock you if there were no other paths to ground.
I did say about floating neutral. That's what I said:If the energy source is not grounded, there's no alternative route for the current. All current will always go through GFCI, so it'll never trip. In fact, if there's no ground, it's nothing that GFCI can protect you from.
In my mind, it has exactly the same meaning as your sentence above.
For some reason, you quoted my words and said:That is not correct ...
So, I just tried to explain in more details ... -
Re: Can AC neutral and ground wire share the same bus?
I think this dead horse has been flayed sufficiently. -
Re: Can AC neutral and ground wire share the same bus?Cariboocoot wrote: »I think this dead horse has been flayed sufficiently.
-
Re: Can AC neutral and ground wire share the same bus?Cariboocoot wrote: »I think this dead horse has been flayed sufficiently.SMA SB 3000, old BP panels.
-
Re: Can AC neutral and ground wire share the same bus?
only if he is wearing metal horseshoes.:roll: -
Re: Can AC neutral and ground wire share the same bus?
when at the water trough there is usually water on the ground, making a good bit of mud... great ground...
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed