High DC voltage relays
lazza
Solar Expert Posts: 336 ✭✭✭
HI
This is linked to my posts on the net-metering problem in Spain. Where we have to avoid grid-feed at all costs (literally cos they charge you!)
So I'm thinking that maybe we could switch the PV system on and off with an in-line relay, depending on the sum of production minus consumption. The problem is that as the grid-tie inverters are high DC voltage, and any relay/switches, will have to work up to 400Vdc..
Does anyone know of high DC voltage relay and switching products/ manufacturers?
Thanks
Larry
This is linked to my posts on the net-metering problem in Spain. Where we have to avoid grid-feed at all costs (literally cos they charge you!)
So I'm thinking that maybe we could switch the PV system on and off with an in-line relay, depending on the sum of production minus consumption. The problem is that as the grid-tie inverters are high DC voltage, and any relay/switches, will have to work up to 400Vdc..
Does anyone know of high DC voltage relay and switching products/ manufacturers?
Thanks
Larry
Comments
-
-
Re: High DC voltage relaysThat's a 12 volt relay. The OP needs something in the 600 to 1,000VDC range.
12 VDC is a coil voltage.
This relay can switch up to 400 VDC. That is exactly what OP asked for. I don't know where you got 600 to 1,000 VDC range. -
Re: High DC voltage relays
Well if you're going to switch standard line power (240 VAC 60 Hz or 230 VAC 50 Hz) and meet code the contacts need to be rated for 600+ Volts just like wiring. They'd also have to be able to switch whatever current could be involved.
The relay NorthGuy linked to would work, but would it be code-compliant? Would that actually be necessary in this application? Good questions in search of answers. -
Re: High DC voltage relaysCariboocoot wrote: »... need to be rated for 600+ Volts just like wiring.
I looked at several ROMEX cables (14/2, 14/3, 10/3) that I had, which are all CSA listed, and they're all rated for 300V. I'm sure they meet the code for 240V wiring. -
Re: High DC voltage relaysI looked at several ROMEX cables (14/2, 14/3, 10/3) that I had, which are all CSA listed, and they're all rated for 300V. I'm sure they meet the code for 240V wiring.
I checked Southwire's website and the voltage rating for Romex wire is 600 volts. My NEC is at the office, but I seem to remember that NM has 600 volt insulation as a requirement. If someone can quote Code, that might help.
(And to answer the question about thinking the contacts were rated at 12 volts, I saw "automotive relay" and read no further. My bad.) -
Re: High DC voltage relays
Hmm. I have some cable here (standard 14 AWG wiring) and it's 600V rated (it's actually insulation rating of course). Never seen any with 300V rating.
NorthGuy, you've got to stop buying your wire from that guy on the corner in the trench coat. -
Re: High DC voltage relays
300v wire may break down under the peak ac voltage presented by 240vac as 240 x 1.414 = 339.36v. often times that 240vac is closer to 250vac anyway making the peak even higher. not sure if the voltage ratings are for rms or peak from nec, though the peak rating makes more sense to me. -
Re: High DC voltage relaysI checked Southwire's website and the voltage rating for Romex wire is 600 volts. My NEC is at the office, but I seem to remember that NM has 600 volt insulation as a requirement. If someone can quote Code, that might help.
The NMD90 cable that is sold here for residential wiring in all hardware stores made by Southwire and Nexan is rated for 300V. I'm totally incompetent in codes, but I don't think they would sell the wire if it was illegal. -
Re: High DC voltage relays300v wire may break down under the peak ac voltage presented by 240vac as 240 x 1.414 = 339.36v. often times that 240vac is closer to 250vac anyway making the peak even higher. not sure if the voltage ratings are for rms or peak from nec, though the peak rating makes more sense to me.
The 300 volt insulation is the nominal AC voltage rating and already takes into account the difference between nominal (RMS) and peak.SMA SB 3000, old BP panels. -
Re: High DC voltage relays
lazza, apologies if I've posted this already, but there is a commercial grid tie inverter available in Spain that will prevent grid feeding: http://powerrouter.com/products/powerrouter-solar-inverter
I can't remember whether you have to use the battery version if you don't want to grid feed... anyway they have a ton of docs on their download pages which describe the different configs.
With regards to your original question, why do you want to switch the high voltage DC instead of just switching the AC output of the inverter? -
Re: High DC voltage relaysI checked Southwire's website and the voltage rating for Romex wire is 600 volts. My NEC is at the office, but I seem to remember that NM has 600 volt insulation as a requirement. If someone can quote Code, that might help.
NM-B is 600 volt.
NMD90 ,"old Romex", is 300 volt.
Both types are recognized in the NEC.
Individual conductors and cables of various types are covered in Table 310.104(A) (2011) and are all 600 volt rated, and one of those types must be used for the insulated current carrying conductors in NM. And we have the lovely Informational note:
"Informational Note: Types NM, NMC, and NMS cable identified by the markings NM-B, NMC-B, and NMS-B meet this requirement."
This recognizes that NM produced before a certain date did not have to meet the 600 volt requirement.
Southwire's NMD90 does not have to meet the 600 volt requirement because it is not NM. (I know, your first guess would have been that NM90D would be a subtype of NM) And NMD90 cannot be used in all the places where the code allows use of NM.SMA SB 3000, old BP panels. -
Re: High DC voltage relays
Hi, thanks for the replies, but does anyone have any more links for those types of relays.
I also have had a couple of thoughts:
1. If I put a kind of by-pass with a relay for one panel in a series of 6 panels (i.e. it short-circuits only that panel in question.), what will happen to the current... i presume it will just cut out the production from that particular panel and the rest of the series will continue to operate normally?
2. If the aforementioned relay is a by-pass in the series for just that one panel... then will the voltage it needs to cope with be just the Voc for that panel, or will it need to cope with the whole string voltage??
Be very grateful for answers to these questions
Larry
ps in reply to Stephen, yes all these types of solutions are ok, but they push the financial viability for an installation out of the window--- the idea is to make systems financially feasible whilst avoiding any problem with the Family (Endesa). -
Re: High DC voltage relays
If you are bypassing one panel by shorting across it the relay has to carry the Voltage of the remainder of the string.
If you are bypassing one panel by switching it out of the string (using both NO and NC contacts) it has to carry the full Voltage of the string.
If you are bypassing one p0anel by switching it out of a parallel connection it has to carry the Voc of the single panel. -
Re: High DC voltage relaysNMD90 cannot be used in all the places where the code allows use of NM.
NMD90 is the only kind of ROMEX sold in Canada in Home Depot, Lowe's, Rona and by guys in trenchcoats.
Perhaps code requirements in Canada are different from the US. -
Re: High DC voltage relaysps in reply to Stephen, yes all these types of solutions are ok, but they push the financial viability for an installation out of the window--- the idea is to make systems financially feasible whilst avoiding any problem with the Family (Endesa).
Switching individual panels may be even more expensive. For every panel you would need a relay with MC4 connections and control wires. All this needs to be installed outside, which means you need weatherproof boxes. That's really expensive.
Using diversion load resistors, or even incandescent light bulbs (if they're not banned yet) on AC side is much cheaper than this. -
Re: High DC voltage relaysPerhaps code requirements in Canada are different from the US.SMA SB 3000, old BP panels.
-
Re: High DC voltage relaysThey definitely are, and they get updated out of sync with the NEC as well.
That's puzzling. How the same thing may be safe in Canada and unsafe in the US (and vice versa)?
Safety is in the eyes of the beholder -
Re: High DC voltage relaysThat's puzzling. How the same thing may be safe in Canada and unsafe in the US (and vice versa)?
Safety is in the eyes of the beholder
It sure is.
When the beholder is John Wiles, and we sometimes think he needs glasses. -
Re: High DC voltage relaysSafety is in the eyes of the beholder
Safety is from the eyes at the border
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: High DC voltage relaysNMD90 is the only kind of ROMEX sold in Canada in Home Depot, Lowe's, Rona and by guys in trenchcoats.
Perhaps code requirements in Canada are different from the US.
That's because Canada is not (yet) a part of the US.
(Canadians don't think this is funny. Many Americans don't think it's true.) -
Re: High DC voltage relays
The big box stores sell what is most often used. They can't stock everything. But we do have electrical supply stores that have a wider variety and greater range of product available.
When I was still working down on the coast I needed a particular, out-of-the-ordinary cover plate. HD and Revy didn't have it. Came home to 100 Mile and bought one at Garth's. Kind of added to the cost with that 850 km trip, but I was making that anyway.
In short, don't expect the Big Guys to be the ultimate source of everything. They're in business for volume sales. -
Re: High DC voltage relaysThat's because Canada is not (yet) a part of the US.
(Canadians don't think this is funny. Many Americans don't think it's true.)
Oddly enough (or maybe not given the state of our educational system) inhabitants of New Mexico have the exact opposite problem.
SMA SB 3000, old BP panels. -
Re: High DC voltage relays
Geesh, the War of 1812 is only 200 years ago, The anniversary is just over 8), (we endured a year long :grrset of TV ads about the battles) the Mint even stamped out a commemorative coin set to keep the memory alive, but it seems some ideas die hard.
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: High DC voltage relayswestbranch wrote: »Geesh, the War of 1812 is only 100 years ago ...
I think it's 200 years ago -
Re: High DC voltage relays
my bad...
the silence on the tube is great now!
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: High DC voltage relays
errr about High Voltage DC relays? -
Re: High DC voltage relays
I have to tell a story on myself. A while back I was touring an inverter company whose gear uses internal DC contactors, and when my guide pointed them out to me I remarked at how small they were. He told me that they were sealed and evacuated to prevent arcing. No arc in a vacuum. Duh. -
Re: High DC voltage relaysI have to tell a story on myself. A while back I was touring an inverter company whose gear uses internal DC contactors, and when my guide pointed them out to me I remarked at how small they were. He told me that they were sealed and evacuated to prevent arcing. No arc in a vacuum. Duh.
All you have to worry about is eroding some metal from the contacts (since at a short enough distance and high enough voltage you can have electrical conduction even in a vacuum) or creating an arc based on vaporized metal.SMA SB 3000, old BP panels. -
Re: High DC voltage relays
lazza, a Spanish company has built and is selling a device that will prevent grid feeding by diverting excess power into a resistive load: http://revosolar.com/solar-shop/es/accesorios-/188-inhibidor-inyectar-en-la-red.html The price to installers is about 150 euros.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 189 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed