Smoking
techcord
Registered Users Posts: 15 ✭
I bought two solar panels and a grid tie invertor from ebay, when I hooked it all up the inverted made a crack noise and smoked and got hot. What did I do wrong? I bought two Uni-Solar PVL-116 116 Watt 24 Volt panels wired them and tested to make sure that they where only putting out around 24v, they where puting out 37v; I also tested twice to make sure that I hooked up the positive and negative to the right sides. The grid tie inverter I bought was rated from 24v to 60v, it was the sun-500g 24v-6ov.
Any ideas?
Thanks in advance,
Landon
Any ideas?
Thanks in advance,
Landon
Re: SmokingAny ideas?
Next time ask your power company to come out and inspect your setup!Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites, Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
Re: Smoking
If you did something wrong... It would be the input (solar panel) polarity or flipped the GT inverter between input and output (i.e., grid on solar panel input, GT output to panels).
Assuming you did not do anything like that--The only other thing I can think of is the wrong output voltage of GT inverter. Typical "smaller" EBay GT inverters are usually 120 VAC @ 60 Hz output. Whereas the typical "higher end" GT Inverters are split phase 120/240 VAC 60 Hz grid (i.e., hooked 120 VAC GT Inverter to 240 VAC power line).
Otherwise, GT Inverters should be "plug and play". No configuration required. And no requirements that utility power or solar panels be connected first. If you are not used to working on "hot circuits", it is usually better to connect the solar panels at night (or covered with cardboard so there is not output voltage/current), then connect the AC power to the breaker/AC outlet.
If you followed instructions correctly, you probably can return it. -
Re: Smokingit was the sun-500g 24v-6ov.
Any ideas?
I would try to get my money back under warranty, and I would consider very seriously not continuing to try to use a unit like this.SMA SB 3000, old BP panels. -
Re: Smoking
sadly its mostly junk and illegal junk at that sold on ebay for grid tie. I have seen a lot of it and give same advice to all DONT CONNECT IT TO ANYTHING. ITS illegal where Ilive in Aus and most likely dangerous.
It most likely does NOT have any type approval marked on it for use in your country,and on this basis you are entitled to a refund,. -
Re: Smoking
In short, what you did wrong was use a non UL listed inverter, instlled without permits, inspections, and the results were predictably near disastrous. If you read through a number of threads in this forum you will see lot and lots that has been written on the subject.
Tony -
Re: SmokingIn short, what you did wrong was use a non UL listed inverter, instlled without permits, inspections, and the results were predictably near disastrous. If you read through a number of threads in this forum you will see lot and lots that has been written on the subject.
http://forum.solar-electric.com/showthread.php?11000-Power-Jack-grid-tie-inverters -
Re: Smoking
Well don’t know if you guys want an update or not. I have returned the grid tie inverter, did not know they were illegal. I had done resource and I did not see one thing that told me they were illegal. I have ordered a charge controller from this website and also a power inverter and some batteries. My plan is to run the lights in my living room with this setup. I was hoping not to have a total waste of money with the solar panels I bought. Do you guys have any tips for a newb? It will all be 24V, I am currently waiting on the inverter, I have the rest but do not have anything hooked up. -
Re: Smoking
Generally:- measure the loads you want to drive (peak watts, Watts*Hours per day, etc.)
- define the battery bank (typically ~4x your average daily load--2 days of no sun, 50% max discharge for longer life)
- size the solar array to both support your loads and properly recharge the battery bank (~5-13% with 10-13% being really nice)
- Then start picking equipment to support your needs.
In this case, you already have equipment. So, we need to hook it up in such away to give you a reliable and safe system that will meet your expectations.
So, what is your hardware:- Batteries, voltage/Amp*Hour rating, flooded cell/agm/etc. (hopefully deep cycle type)
- Number and brand/model of solar panels (Voc/Vmp/Imp if you have it handy)
- What is the charge controller
- What is the inverter
- Roughly, where will the system be installed (figure out how much sun you will get per day/by season)
In general, I suggest sizing everything to the battery bank (voltage and Amp*Hour capacity). The typical rate of charge of 5% to 13% is a good point to aim for. Less than 5%, you really don't have enough power to quickly and fully recharge the battery bank. Over 13% is a lot of solar panels (expense) and you should have a solar charge controller that supports a Remote Battery Temperature Sensor (it is possible for a battery bank to get hot from high charging current and thermally "run-away"). etc...
Let us know what you have, and possibly how much power you expect to use (a Kill-a-Watt type power meter is great for this job--and handy for understanding power usage in the home and how to best tackle conservation projects).
Enough hand waving on my part--With a list of your current hardware, this will all make a lot more sense as we go through the design cycle.
Re: Smoking
Sometimes it's a technical thing: the inverters themselves may not be illegal, but the installation would be. The inverter itself may have certification such as UL listing, but that doesn't mean anything other than that the unit meets specs. Connecting it up is a whole 'nother ball game.
So now you're going to use your panels to charge some batteries and take a few circuits off grid or use for standby power? It helps to know where you're trying to go when you want to find the right route.
You've got 232 Watts of panel. Not sure what the exact specs are on those ("24 Volt" can be highly misleading) but could be enough for about 75 Amp hours @ 24 Volts, maybe 150 in a stand-by application. This is not going to be a lot of power. Perhaps 600 Watt hours per day. -
Re: Smoking
Thanks for the reply,
2 X 12v Deep cycle 92 amp batterys, they have caps with water in them, that would mean flooded, correct?
2 X Uni-Solar PVL-116 116 Watt 24 Volt panels
ProStar ps-30
300w 24v inverter
I live in nashoba OK
I would like to run two 60w light bulbs 24 hours a day -
Re: SmokingThanks for the reply,
Yes. About 1kW hour maximum power there.2 X Uni-Solar PVL-116 116 Watt 24 Volt panels
ProStar ps-30
Try to find the Vmp & Imp for those panels; they may not work will with a PWM controller on a 24 Volt system. I think those are the flexible ones with a Vmp of 30, which is really too low for proper charging.300w 24v inverter
Two 60W = 120 Watt * 24 hours = 2880 Watt hours. This will not work. Replace those incandescents with CFL's and save a lot of power: 26W * 24 hours = 624 Watt hours. -
Re: Smoking2 X 12v Deep cycle 92 amp batterys, they have caps with water in them, that would mean flooded, correct?
Ok--Yep, they are "flooded cell". So you need to check the electrolyte levels about once a month and probably need to add distilled water every couple of months (if everything is going well). Make sure to only fill after a day of charging and don't over fill (or you will have electrolyte spilling out all over your battery top). Make sure to never the the plates be exposed to air.
The "optimal" size of solar array for this battery bank would be (assuming 24 volt battery bank connetion):- 29 volts charging * 92 AH capacity * 1/0.77 panel+controller deratings * 0.05 rate of charge = 172 watt minimum array
- 29 volts charging * 92 AH capacity * 1/0.77 panel+controller deratings * 0.10 rate of charge = 346 watt nominal array
- 29 volts charging * 92 AH capacity * 1/0.77 panel+controller deratings * 0.13 rate of charge = 450 watt "cost effective maximum" array
I am not entirely sure what the ratings of these panels are... But if this website is correct:Uni-Solar PVL-116 116 Watt 24 Volt Brand New Flexible Amorphous Solar Panel with MC3 Connectors Maximum Power (Pmax): 116 Watts
Nominal Operating Voltage: 24 Volts
Peak Power (Volts): 30 Volts
Peak Power (Amps): 3.88 Amps
Open Circuit Volts: 43.2 Volts
Short Circuit Amps: 4.8 Amps
They are a bit low in operating voltage (Vmp~30 volts). For a 24 volt battery bank, you should be looking at Vmp in the range of ~35-38 volts (STC--standard test conditions). On hot days and with cool batteries, your array many not generate enough voltage to reach maximum power (i.e., voltage of array falls, and current from array will be less).
At this point, if they are as listed--And you have a PWM charge controller, just put the two panels in series and monitor what happens (i.e., does the battery bank get "quickly" and fully charged).ProStar ps-30
The Prostar (MorningStar) 30 amp 12/24 volt charge controller is a good controller... However, depending on what your Uni-Solar panel ratings/performance actually is--It may not be the "optimum" controller for this application (if you want to keep the solar panels).
If you keep these panels, the "optimum" performance would be to connect the two panels in series and then use a MPPT type solar charge controller (Maximum Power Point Tracking) to down convert from high voltage/low current of the solar array to low voltage/high current required to charge the battery bank (sort of like how a transformer works for AC voltage/current/systems).
You are sort of between a rock and a hard spot here... A MPPT charge controller that meets these panel specs (two panels in series) would be a full sized 45+ amp MPPT type charge controller because you need one with a Vpanel input voltage of >~100 VDC. And these are not cheap (at least the current brands/models that I am aware of--you might find some less expensive MPPT charge controllers out there--I am not in the solar business).300w 24v inverter
That is nice--A lot of people try to put 2kW or larger inverters on a "small" battery bank--Yours is sized nicely for your present battery bank (not too large/wasteful of energy).I live in nashoba OK
Using PV Watts for Fort Smith AK (you can pick which city is closer in weather for your place if Fort Smith is not good). An array tilted at latitude (~35 degrees from horizontal), fixed position would "see" around this many hours of sun per day, by month:Month Solar Radiation (kWh/m 2/day) 1 4.13 2 4.84 3 5.13 4 5.67 5 5.77 6 5.97 7 5.85 8 6.08 9 5.34 10 5.07 11 4.42 12 3.62 Year 5.16
So, if I pick 4 hours per day to cover 10 months or so of the year:- 116 watts * 2 arrays * 0.52 system efficiency * 4 hours of sun per day = 483 Watt*Hours per day of 120 VAC power
4 hours of sun would power two*60 watt bulbs:- 483 WH per day / 120 Watt load = 4 hours per day (ignoring AC inverter tare losses if left on 24 hours per day)
So--Now look at the loads. If you need 2x 60 watt loads to keep eggs warm--Then this system would not meet your needs. It would need to be, very roughly 6x larger.
At best, if you want "light" 24 hours per day:
483 WH / 24 hours = 20 watt average load
Now, two 9 watt LED lights can supply a fair amount of lighting--especially if you get focused LED type bulbs. It all depends on your needs.
But--We also have the problem of the Uni-Solar panels and their less than ideal Vmp output voltage which very likely could negatively impact the output of the above system (as I have guessed at its design).
Re: Smoking
Wow, thank you.
I never dreamed of so much great information.
If I added two more panels, that would put me in the optimal range in Bill's example, correct?
What gauge wire should I use to connect everything? -
Re: Smoking
How do you want to address the questions of the miss-match between the solar panels and the battery voltage?
We need to know that before we can finish the design.
Unfortunately, there is a lot of miss match right now. Your options:- You could purchase different brand/model of solar panels (Vmp~17.5 or ~35+ volts) and match your 24 volt balance of system.
- You could put the batteries in parallel and buy a new 12 volt inverter (this MorningStar 300 watt TSW 12 volt inverter is quite nice) and a lower voltage MPPT controller (a bit cheaper than high voltage/power MPPT controllers--but there is not a lot of choices out there for lower power MPPT controllers--For example, if you do not go with more panels is this 15 amp MPPT 12/24 volt controller from MorningStar).
Other than above, it is pretty difficult to make "reliable" system with the components you have at the moment.
If you are trying to optimally use your money--You might have to pencil out several designs and figure out which one offers the best value for your needs.
Re: Smoking
Bill, Thanks for your input,
I was going to wire the battery's in series to get the 24v to match the system, would this not work?
When you say reliable what exactly are you referring to?
If I buy the two items your are referring to, what gauge wire would I need to hook it all up? Would I hook the panels in series or paralleled for this to work? -
Re: Smoking
The problem is that the Uni-Solar panels do not have the "standard" output voltage(s) used for 12 volt (or 24/48 volt) battery banks and PWM (the less expensive type) of solar charge controllers.
For example, a 24 volt battery bank needs about 29 volts to charge quickly/fully (and around 30-32 volts to equalize charge every month or three). A 30 volt Vmp panel will only output "rated voltage" in fairly cold weather (near freezing). In warm/hot weather, the Vmp voltage will fall by upwards of 20% as the sun heats up the panels (i.e., 30 volts Vmp in STC standard test conditions can fall to near 24 VDC in hot weather). And not have high enough voltage to fully/quickly recharge your battery bank (plus the losses from wiring and controller voltage drops too).
With such a configuration, the battery bank will slowly (or quickly) be discharged over the days/weeks until the batteries are eventually damaged and/or killed (sulfated/damaged from discharging to near zero state of charge).
If you put the two panels in series, the Vmp-array would be around 60 volts Vmp... And you would only have around (35 vmp/60 vmp=) 58% efficiency from your solar panels (i.e., lose almost 1/2 of their output energy because of voltage miss-match).
Unless you change to "12/24 volt friendly" solar panels or use much more expensive MPPT type charge controllers (with your present solar panels in series for Vmp-array of ~60-90 volts), your system will have very poor performance.
One option being changing solar panels, the other is changing to a MPPT type solar charge controller. Larger or smaller versions are available--which depends on your eventual system size.
And if you are OK with smaller inverter sizes (i.e., 300 watt), you could drop to a 12 volt battery bank and use a 300 watt 12 volt TSW AC inverter pretty nicely with your present pair of panels on the smaller MPPT charge controller.
Until you make these choices, wire sizing is not possible.
Re: Smoking
Thanks Bill,
Thinking I will start over or from scratch, picking my solar panels and charge controller to match, and thinking about the future adding to the system. I think I will start a new thread for that.
If I did wire the present solar panels in series to get 60v would that not blow up my PS-30 charge controller?
Thank you,
Landon -
Re: Smoking
It depends, I don't remember the maximum input voltage for that PWM controller. There are PWM controllers with upwards of 125 Volt inputs--but even it if worked, your system would be (on average) only ~58% efficient vs the "100%" of the right panel to battery match...
Note, the overall end to end off grid AC system efficiency of a "properly" designed solar system (from solar panel input to AC power output) is only around 52% (nominal) anyway... Add another 50% loss just on the panels, and you can see it will cut your available power dramatically.
Re: Smoking
Other than the possibility that the input Voltage might be too high (most PWM controllers only expect 'typical' Voc input for the system Voltage, i.e. ~44-50 Volts for a 24 Volt system) what basically happens is that the panel Voltage will be "pulled down" to the system Voltage while the current remains the same and the power from that difference in Voltage is lost.
So two panels with 30 Vmp and 4 Imp (120 Watts) put in series on a 24 Volt system will deliver at most the power equivalent of only one of those panels as the system Voltage will peak around 30. In essence you use one whole panel just to make up the Voltage losses caused by temperature and wiring. -
Re: Smoking
But it will not blow up my charge controller, just 50% loss?
Thanks,
Landon -
Re: SmokingBut it will not blow up my charge controller, just 50% loss?
Thanks,
Landon
That would depend on the input max of the particular charger. Morningstar doesn't list a number for this in their specifications so you'd have to contact them. Keep in mind the maximum is actually limited by the panel Voc, which is higher than Vmp. If the 'front end' has been design with components meant to take only 50 Volts, a quick jolt with a high Voc can cause instant failure. If they didn't scrimp and the capacitors for example have a 100 or 200 Volt rating there would be no trouble. But you have to ask them. -
Re: Smoking
Will do, Thank you, Landon -
Re: SmokingCariboocoot wrote: »That would depend on the input max of the particular charger.
What really surprised me was the spec for MPPT range which was like 150 - 600 volts. But the next line said Maximum Input Voltage 560V. :-)SMA SB 3000, old BP panels. -
Re: SmokingSaw a quote about a high voltage input CC, not the original document.
Sometimes the specs get a little peculiar. Like the venerable MX60 with its 150 Volt input limit. Depending on which revision you had it would shut down before that Voltage (mine does so at 141). Above that - it could fry.
GT inverters often have in input max of 600, but a functioning range limit of 560 - and an optimum MPPT range limit lower than that.
Got to look at all the numbers. Even then it may not make sense. :roll: -
Re: SmokingCariboocoot wrote: »Sometimes the specs get a little peculiar. Like the venerable MX60 with its 150 Volt input limit. Depending on which revision you had it would shut down before that Voltage (mine does so at 141). Above that - it could fry.
This particular new CC seems to have a GTI-scale input side combined with a battery CC output side.SMA SB 3000, old BP panels. -
Re: Smoking
Had another question about my panels only putting out 30v and them needing more volts to be able to charge my 24v battery's better. Could I add a panel to the system that has more volts in parallel would adding that help or would I still be kicking a dead horse? -
Re: Smoking
More or less, you add panels in series to add voltage. And add panels in parallel to add current.
To get ~35-40 volts Vmp from a 30 Vmp panel, you would need to add a 5-10 volt Vmp panel in series (rated at the same current). It is usually very difficult to find pre-made panels that would match your requirements.
In fact, it is getting more and more difficult to find "cheap" (low $$$/watt cost) panels in larger sizes that are anywhere near the needed voltages to "match" a PWM controller + 12/24/48 volt battery bank.
The large panels are primarily used with Grid Tied systems that (typically) need working Vmp-array voltages in the ~250-400 volt range... So, the designer/installer simply adds panels in series string + paralleling those strings to match the inverter's optimum input requirements (and the needs/spending limits of the home owner).
People with older systems (both Grid Tied and Off Grid) are finding it difficult to find "matching" panels to upgrade/repair their systems and sometimes it is better to add a second GT Inverter/MPPT Charge controller to add the new panels... Older panels cost $5-$10 per Watt, and new panels are in the $2-$1 per watt range, so even if they can find a "match", it may be way too expensive vs a new/non-matching set of panels.
Note, ideally you want to match Vmp (parallel connections) in the ~5% to 10% maximum difference between panels range.
And for series connections, you want to match Imp to within 5%-10% miss-match.
Over 10% miss-match, and you can end up with poor performance or even damage/fire hazards (in some cases--it all depends...).
Re: Smoking
I should add/clarify--It is not that you cannot ever use those panels for your needs--It is just they are (probably) not optimum. It would cost you more money to use a MPPT charge controller to match the panels to the batteries, or use a cheaper PWM controller and lose much of the energy rating from those panels.
It is one of the major issues that we work with here for many people on an ongoing basis. It is a real pain in the behind and there is, usually, no simple/easy/cheap solution (short of selling your hardware on Ebay/Craig's List and using the money to address your needs).
Re: SmokingI should add/clarify--It is not that you cannot ever use those panels for your needs--It is just they are (probably) not optimum. It would cost you more money to use a MPPT charge controller to match the panels to the batteries, or use a cheaper PWM controller and lose much of the energy rating from those panels.
Thanks Bill,
I am in IT and I know how irritating the users can be asking dumb questions, sorry for being that guy. I would like to thank you from the bottom of my heart for all the information you have provided me with, it has helped. I will be buying panels to match the controller I bought and doing thing optimal. Again thank you for sharing your knowledge, and I hope to get to talk with you again.