Hi all,
We live in a small log cabin (1500 sqf) in the Gatineau Valley (Ottawa, CA) and I put together a small 12V system as a backup for the numerous power outages that we have every year and lasts an average of two to three days .....
My emergency needs are to supply some LEDs, TV, SAT receiver, laptop / modem ..... for a max. total draw of 300W/120V for about 6 hours/day
Living in the woods, heating and hot water is not a problem because we have a good old Iron-Cast kitchen stove , legacy from our grand-parents .
My only concern is the well pump (150 ft deep)...investigating on a manual pump...

So, I now have ( but not installed yet )

a small windmill 600W (12V AC)...(we live on top of a hill wich have 4.1 m/s average wind annually)
four 110W solar panels (12V DC)
one Solarwind Hybrid 40A Charge Controler (12V AC / DC)

What I need now is ,

Wires to go from panels and turbine to inside Charge Controler .....What size ?..is 8 AWG OK for a 40 ft run without too much lost.
maybe one rectifier 1000V/50A (to save one wire trip from turbine to controler wich accept both AC and DC )
two (225Ah) or four (450Ah) TrojanT-105 batteries ( is car booster cables cut to size ok for inter-connecting batteries ? )
A good inverter ( not decided yet ).
....maybe more solar panels ?

This intended small system will be my learning path to eventually construct a full off-grid new home ( in about 3years from now ).

Thank you for constructives comments....and this great informative site !

Comments

  • Photowhit
    Photowhit Solar Expert Posts: 6,006 ✭✭✭✭✭
    Re: Small is beautiful !

    4.1 m/s is about 9 mph so wind should be somewhat viable, usually you'll want to get that well above the tree line, what many fail to do with wind.

    150 feet deep is about what can be done on a hand pump but may not be the most fun you ever had, Here's a site that discribes the parts, While your well may be 150 feet deep your water table is likely not as deep so you might well be able to use a shorter draw.

    I'm fine with car booster cables used for battery interconnects and even connections to the inverter, but be aware of the size of the wires, some booster cables are pretty small. My first solar install I did in a van, I used some 4 gauge jumper cables cut down that a tow truck company sold me when they replaced them. The jumper cbles(booster cables) in my car are 8 gauge and too light for this.
    Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites,  Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
    - Assorted other systems, pieces and to many panels in the closet to not do more projects.
  • BB.
    BB. Super Moderators, Administrators Posts: 33,642 admin
    Re: Small is beautiful !

    Welcome to the Forum THC!

    Sounds like a neat place.
    THCanada wrote: »
    My only concern is the well pump (150 ft deep)...investigating on a manual pump...

    There are some nice water pumps out here that can work with solar panels, battery bank, and/or AC genset/utility power--All with the same pump in the case of the Grundfos SQ Flex series--Although they are not cheap (probably around $2,000 or more these days).

    You can go another way--A big old AC genset and standard well pump into a cistern--Then use a small AC or DC pump from your battery bank to pressurize the home (and run a Ozone Generator to keep the tank bug free).

    There are also VFD (variable frequency drives) which can be a nice cross between a $2,000 in-well German engineered pump and a standard AC pump that is "nicer" to an off grid power system.

    This thread has lots of information and random links to information on Solar RE, conservation, and other home related energy projects.
    a small windmill 600W (12V AC)...(we live on top of a hill which have 4.1 m/s average wind annually)
    four 110W solar panels (12V DC)
    one Solarwind Hybrid 40A Charge Controller (12V AC / DC)

    I don't know anything about the SolarWind controller--Go ahead and try it to see how well it works for you--But watch your battery bank voltage/state of charge to see if it is keeping your bank charged or not. I am a bit leery of it. I think it will prove to be too small for your needs (only 150 watt rated for 12 volt solar array???) and will not properly/fully recharge the battery bank (if 14.5 volts is maximum charging voltage, that is usually too low for flooded cell battery banks).
    Wires to go from panels and turbine to inside Charge Controler .....What size ?..is 8 AWG OK for a 40 ft run without too much lost.

    Using a basic voltage drop calculator and 1% to 3% maximum voltage drop, 14.5 volts and 50 amp current down two wires (three phase wiring can be a size smaller wire gauge):
    • 40', 50 amps, 8 awg => 3 volt drop

    For a wind turbine, you can probably stand a higher voltage drop is a ~23% drop--One of the big problems with 12 volt systems--You need very expensive copper wire to send power any distance with "reasonable" voltage drop.

    Also--you have a 40' run from the turbine to the home/battery bank--But you also should have a minimum of 60' tall tower (30' above obstructions, ~300-500 feet or more from those obstructions) for turbulence free air to run your turbine (which also adds to the wire length).

    Note that I am not a big fan of small wind--So take my opinion with a grain of salt.

    The 4.1 M/S (~9.2 MPH) is just at the floor of "enough wind" to get useful power from a typical wind turbine (usually need around 10-12 MPH minimum). And, many times, those measurements from wind maps are at 120 Feet or higher elevation--A 20-30 foot tower is not going to see those numbers (on average).

    Also, it is difficult to find a reliable "small wind" turbine (make sure it is installed a fair distance from the home/where kids play--There are enough examples of shedding blades and falling turbines that I would not want one next to the home--let alone the issues with noise in heavy winds).

    Anyway, if you need wind and it makes sense for your home--We can talk more about that later.
    maybe one rectifier 1000V/50A (to save one wire trip from turbine to controller which accept both AC and DC )

    In your case, I would stay with the three cables for the longer wire run--Will help reduce voltage drop a bit.
    two (225Ah) or four (450Ah) TrojanT-105 batteries ( is car booster cables cut to size ok for inter-connecting batteries ? )

    Car booster cables are questionable--Many in our area are just 8 awg cables. With a 300 watt 12 volt inverter, you need around 6 awg minimum. You have to go through the voltage drop calculator to find the right minimum AWG for your needs (wire length is important, as well as charging/discharging/surge current--you only have a about 0.5 to 1.0 volt maximum voltage drop from inverter to battery bank--And you want around 0.05 to 0.10 volt drop from charge controllers to battery bank).

    A lot of people use welding cable for battery connections--But the very find wire of welding cables makes it difficult to properly/securelly/safely terminate the cable ends. You might check with a battery distributor if they can make up cables for your needs. See this site for paralleling battery strings.

    I like to size the battery bank to the loads--Too large of battery bank is almost as much pain as too small of battery bank. A Kill-a-Watt type power meter can help you here a bunch.

    For example, sizing a solar array for the battery bank using the rule of thumb of 5% to 13% rate of charge for a 450 AH @ 12 volt battery bank:
    • 450 AH * 14.5 volts charging * 1/0.77 panel+controller deratings * 0.05 rate of charge = 424 Watt array minimum
    • 450 AH * 14.5 volts charging * 1/0.77 panel+controller deratings * 0.10 rate of charge = 847 Watt array nominal
    • 450 AH * 14.5 volts charging * 1/0.77 panel+controller deratings * 0.13 rate of charge = 1,102 Watt array "cost effective" maximum

    Note--the larger the battery bank, the larger the suggested solar array would be. In your case, since you are using this for backup power, you can probably get away with the 5% rate of charge as you have utility power to normally keep the batteries charged.

    However, you need to also size the array for the amount of sun you get in your region... Using PV Watts for Ottawa, fixed array tilted to latitude 45 degrees) (you can pick a site closer to your home):
    Month      Solar Radiation (kWh/m2/day)
    1      2.86     
    2      4.70     
    3      5.27     
    4      5.01     
    5      5.21     
    6      5.47     
    7      5.53     
    8      4.99     
    9      4.56     
    10      3.54     
    11      2.27     
    12      2.60     
    Year      4.33
    

    Tossing out the bottom three months, we get a minimum of 3.54 hours of sun for October--For an 847 watt "nominal" array:
    • 847 watt array * 0.52 end to end system eff * 3.54 hours of sun = 1,559 Watt*Hours per day...

    A 300 Watt AC load would last about:
    • 1,559 Watt*Hours per day * 0.85 inverter eff * 1/300 watts = 4.4 hours of "solar power" per average October day

    On a 450 AH battery bank, assuming 2 days of "no sun" and 50% maximum discharge for longer battery life (basically 1/4 of battery discharge per day):
    • 450 AH * 12 volt battery bank * 1/4 level of discharge * 0.85 inverter eff * 1/300 watts = 3.8 hours per day of "battery power"

    As you can see--when we add all of of the basic rules of thumb, it takes a fairly large system to power even a "nominal" of 300 watts * 6 hours per day. Accurate measurements and "extreme" conservation will be your friend.
    A good inverter ( not decided yet ).

    Hands down, a MorningStar TSW 12 volt 300 watt (600 watts for 10 minutes) AC inverter is ideal for your needs as stated.
    ....maybe more solar panels ?

    It depends--For emergency/backup power for a few days at a time--An small/efficient genset may be a better (more cost effective) option. A Honda eu2000i (1,600 watt) with an 120 VAC 40 amp or so battery charger (pull start) to a Honda EM4000SX (electric start/auto start compatible) or similar would be a good match for your home/loads (gasoline may be your best option for cold weather operation).

    If you decide to run other appliances (fridge/well pump/etc.) from your battery system--Then we are talking about a much larger system (24 or 48 volt battery bank, a much more expensive inverter, etc.).

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • THCanada
    THCanada Registered Users Posts: 2
    Re: Small is beautiful !

    Thank's for the fast input !

    The manual deep well pump link provided by photowhit , is the one I was considering for emergency ! (as we do have the 40 Gal. hot water tank as a reserve ).

    The Charge Controler ( max. input is 30V and 40A , max. out is 37.5A) is in continuous charging mode when battery is under 14.6V until 14.7V when it start pulsing mode (30 sec. on /30 sec. off) , when voltage is at 14.8V and above it will go on Trickling mode ( charging 10 sec. and pause 50 sec. and so on... ) , looks good to me... and will see with usage .

    So , as per recomendations ,

    will come with the 3 wires (6 AWG 40ft run) from AC turbine ( on a 30 ft tower) to Charge Controler (witch have built in rectifier already ! ),
    will come with 2 wires (6 AWG 40ft run ) from 4*110W panels to Charge Controler
    Will go from Charger Controler to 4*T-105 (450 Ah) wired with #4 booster cables as per method 3 from SmartGauge site.
    will feed MorningStar 300W inverter with #4 wires from Charge Controler then feed AC apps .

    And , NO , I'm not going to have a Genset of any kind.... I HATE them. period.

    You know, we have been through 7 days of black-out at times (remember 98 ice storm?) with 4 kids at home , only the wood stove, oil lamps and candels and all was fine .
    When I say 300W/6hrs day , it is just to please my wife !.. that way , she can watch the news , have a good movie (100W), and read few hours(10W) , use the laptop(90W) ...the basic things!

    Our kids are (most of the time ) gone now !.. We maybe see them twice a week .
    So make things a lot easier... and with way less waste of energy !..

    See , even 200 watts for 4hrs/day for the two of us is plenty !..
    So, in regard of that , I will stick to my budget and will fine tune and improve it with time .

    I will now have to look for those #6 wires.........
  • Photowhit
    Photowhit Solar Expert Posts: 6,006 ✭✭✭✭✭
    Re: Small is beautiful !

    While booster cable are fine, if the gauge is right, you will want to cut them up and use proper lugs to the batteries.
    Home system 4000 watt (Evergreen) array standing, with 2 Midnite Classic Lites,  Midnite E-panel, Magnum MS4024, Prosine 1800(now backup) and Exeltech 1100(former backup...lol), 660 ah 24v Forklift battery(now 10 years old). Off grid for 20 years (if I include 8 months on a bicycle).
    - Assorted other systems, pieces and to many panels in the closet to not do more projects.
  • waynefromnscanada
    waynefromnscanada Solar Expert Posts: 3,009 ✭✭✭✭
    Re: Small is beautiful !

    Unless you are getting one heck of a good deal on that wind turbine, leave it where it is and put the money into more solar. Been there, done that, just like thousands of others who have wasted their money on these mini wind turbines, sucked in by the sales hype. In my case though it wasn't a total waste, I was able to use the alternator on my mini hydro project that's been working awesome for about 4 years now :)
  • inetdog
    inetdog Solar Expert Posts: 3,123 ✭✭✭✭
    Re: Small is beautiful !
    THCanada wrote: »
    Thank's for the fast input !

    The manual deep well pump link provided by photowhit , is the one I was considering for emergency ! (as we do have the 40 Gal. hot water tank as a reserve ).

    Take a look at this one, for a significantly higher priced but incredibly overengineered manual pump. They offer a DC motor option that would allow you to use it as your primary pump with solar input instead of just a backup. The backup would then be to take the motor off and put the handle back on.
    It uses a fiberglass pump rod so that you do not waste as much energy lifting the pump rod along with the water.

    They do recommend pulling the pump annually to do maintenance on the seals at the bottom, so depending on your depth to standing water that could be quite a pain.
    SMA SB 3000, old BP panels.
  • Ralph Day
    Ralph Day Solar Expert Posts: 1,023 ✭✭✭✭
    Re: Small is beautiful !

    If you never plan to have a generator you better buy stock in a battery company for the owner discount. Without a generator in eastern Ontario you'll be going through batteries, garanteed. Inverter generators are quiet and fuel efficient. Put in an appropriate sound attenuating shed you will hardly hear them when they run.

    It's just about impossible to get enough wind and sun to keep your loads and batteries healthy alone. Having a generator around will remove the panic factor when you haven't seen the sun for 5 days. Yes, 3600rpm construction generators you don't want to have around, but an inverter type will change your mind.

    My 10kw diesel set is heard less in my house (130feet away) than the neighbour's lawn tractor (500feet away). If i were to do it again I'd put in an inverter genset for all it run/ran. When off-grid about 100hours per year, mostly from Nov to Feb.

    Please, check around and see how noisy good gensets are before you commit to living without one. We'd surely be hearing back from you in a few months with batteries in deficit charging condition $$$.

    Ralph