Who makes the most compatable PV charge controller for a Magnum Energy Inverter?
Re: Who makes the most compatable PV charge controller for a Magnum Energy Inverter?If it has to be 10, then I personally would probably go with two strings of 5 and a Classic 200 (assuming it's not really cold where you live). I know vtmaps will disagree with me here
Maybe. As far as I know Midnite has not published their efficiency curves. The recommendations I make are based on the Outback curves. They may or may not be similar to Midnite's curves. From what I can glean over at Midnite's forum, the Midnite curves are not too dissimilar to Outback's efficiency curves, and the Midnite folks recommend that for best efficiency and coolest running controller, the Vmp should not be too much more than twice the nominal battery voltage.
Eric-
To my inexperienced knowledge and with the battery bank I have, This configuration seems to be balanced OK and only pushing the boundary of my budget a little. I understand your point about odd numbers. When I do an upgrade, either way, I'll need to add another charge controller. As long as my understanding is correct, I should be able to run this system until my batteries fail. It would then be a good time to upgrade the whole pv system provided I need the extra power. -
Re: Who makes the most compatable PV charge controller for a Magnum Energy Inverter?OK, using your value (120 ft) x (0.395 ohms) ÷ 1000 ft = 0.0474 ohms
(38.9 amps) x (0.0474 ohms) = 1.844 voltage drop
(1.844 volts) ÷ (59.2 volts) = 3.12% voltage drop
Does this fall within the guidelines or would it be worth the added expense of bigger wire?
Thanks for all the help! -
Re: Who makes the most compatable PV charge controller for a Magnum Energy Inverter?Hi all,
Still figuring this out-
Here is what I'm looking at. Am I sizing this right?
Charge controller= Midnight Solar Classic Lite 150
60' foot run using #6AWG Copper wire shows 2.4% line loss.
PV specs from Midnight's sizing calculator-
PV Array 230watt
Number Of Modules In Series: 2
Number Of Parallel Strings: 5
Total Modules 10
Rated PV Array Power: 2300Watts
Anticipated Array Power @ 110F: 2119Watts
Rated PV Array Current: 38.9 Amps
Battery Charging Current @ 28.8 V: 79.9 Amps
VMP (Maximum Power Point Voltage) : 59.2 Volts
VOC (Open Circuit Voltage): 73.6 Volts
VMP @ 20 F°: 67.2 Volts
VOC @ 20 F°: 81.6 Volts
If I am understanding this correctly, based on my battery bank, I have the 10% rate of charge and the 2x volts mentioned earlier.
Have I found the middle?:D
It's fine. It will work. You've only got 60' from array to controller so there's no reason to go with very high array Voltage and reduce the controller's efficiency (they all function about the same, btw).
- 234 Forum & Website