Why does this Shurflo pump seem so great? Will it work for my house with my EU2000i?
jeffkruse
Solar Expert Posts: 205 ✭✭✭
Searching through this forum I found a Shurflo water pump http://www.solar-electric.com/2088-594-154.html
This pump seems like it will work for me. I currently am using a 1/2HP pump to take water from my cistern and pump it up to my house. My pump sits outside of the cistern at the bottom. The cistern is about 20’ lower than the top of the house. Pipes are ½” and we only take one shower at a time. There is a 20 or 40 gallon pressure tank connected near the pump. The pressure is 60psi off and 20 on. 45-50 psi off would be great but I would like the on pressure set at 30.
My current pump will not work with my Honda EU2000i. I was able to get the pump to start a few times from the generator but I had to plug it directly into the generator and start the generator with it connected. If the generator was on when the pump tried to start it wouldn’t work.
This Shurflo pump seems to draw so little current. Its flow would be about 2 GPM. Would this be enough? Is there another model that could provide 3GPM at 30PSI?
What kind of maintenance am I looking at for a pump like this?
This pump seems like it will work for me. I currently am using a 1/2HP pump to take water from my cistern and pump it up to my house. My pump sits outside of the cistern at the bottom. The cistern is about 20’ lower than the top of the house. Pipes are ½” and we only take one shower at a time. There is a 20 or 40 gallon pressure tank connected near the pump. The pressure is 60psi off and 20 on. 45-50 psi off would be great but I would like the on pressure set at 30.
My current pump will not work with my Honda EU2000i. I was able to get the pump to start a few times from the generator but I had to plug it directly into the generator and start the generator with it connected. If the generator was on when the pump tried to start it wouldn’t work.
This Shurflo pump seems to draw so little current. Its flow would be about 2 GPM. Would this be enough? Is there another model that could provide 3GPM at 30PSI?
What kind of maintenance am I looking at for a pump like this?
Comments
-
Re: Why does this Shurflo pump seem so great? Will it work for my house with my EU20
Perhaps you should consider a 12 volt pump such as: http://www.solar-electric.com/5904-1211.html
You can power it from your generator using this: http://www.solar-electric.com/ioen12vo15am.html
This extreme sensor pump needs no pressure tank.
Another possibility is to use a lower capacity 12 volt pump such as: http://www.solar-electric.com/8000-443-136.html which, I believe can be powered directly by the 12 volt output of the honda eu2000 generator.
An advantage of using a 12 volt pump is that someday you can set up a modest solar system that will power the pump, and free yourself from the generator.
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Why does this Shurflo pump seem so great? Will it work for my house with my EU20
Jeff the specs for that pump are
PSI 10 20 30 40
BAR .7 1.4 2.1 2.8
GPM 2.6 2.34 2.08 1.85
L/MIN 9.8 8.8 7.9 6.2
AMPS .58 .67 .76 .94
There is no way that your 2000w gen at ~13.3 A should not be able to run the pump.. it is listed @ drawing 113 W.
That gen puts out 2000max and 16000W continuous.
Re the old pump: are you trying to start it in ECONO mode. My 1000 has problems with inrush if in Econo mode.
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: Why does this Shurflo pump seem so great? Will it work for my house with my EU20
Non submersible shurflos are good pumps. That said, they won't pull water very far. (suction side) but they will push water up to ~60 psi, so if you locate the pump at the cistern, with all the wiring loses associated with that it should work, but if you expect to ump from the cistern up 20' is won't.
Tony -
Re: Why does this Shurflo pump seem so great? Will it work for my house with my EU20I currently am using a 1/2HP pump to take water from my cistern and pump it up to my house.
-
My Honda EU2000i wont power this tiny Shurflo pump
Well, I finally needed to use my Shurflo 2088-492-444 water pump. It did not work with my Honda EU2000i! :grr
I even made a short electrical cord of no more than 5' and pluged only it into my generator. I tried in Eco Mode and not in Eco mode. I even removed any output pressure on the pump.
My EU2000i goes into overload in less than a second and only a few spits of water comes out. This pump runs fine on my household AC.
Also, I can get my Honda EU2000i to start my old 1/2HP waterpump if that pump has less than 10 PSI on it. The Honda powers my microwave and in sink garbage disposal (one at a time). Everything else in the house can be run at the same time off of the EU2000i just fine.
This doesnt make sense! -
Re: My Honda EU2000i wont power this tiny Shurflo pumpWell, I finally needed to use my Shurflo 2088-492-444 water pump. It did not work with my Honda EU2000i! :grr
I even made a short electrical cord of no more than 5' and pluged only it into my generator. I tried in Eco Mode and not in Eco mode. I even removed any output pressure on the pump.
My EU2000i goes into overload in less than a second and only a few spits of water comes out. This pump runs fine on my household AC.
Also, I can get my Honda EU2000i to start my old 1/2HP waterpump if that pump has less than 10 PSI on it. The Honda powers my microwave and in sink garbage disposal (one at a time). Everything else in the house can be run at the same time off of the EU2000i just fine.
This doesnt make sense! -
Re: My Honda EU2000i wont power this tiny Shurflo pumpMy EU2000i goes into overload in less than a second and only a few spits of water comes out. This pump runs fine on my household AC.
Also, I can get my Honda EU2000i to start my old 1/2HP waterpump if that pump has less than 10 PSI on it. The Honda powers my microwave and in sink garbage disposal (one at a time). Everything else in the house can be run at the same time off of the EU2000i just fine.
This doesnt make sense!
How fast is the pump spinning at the time the inverter shuts down? If it is not anywhere near full speed, you are still in the starting surge region of its power consumption, and that may be just too much for the Honda to handle.
According to the specification sheet (http://legacy.shurflo.com/pdf/rv/product_data_sheets/pds-2088-492-144.pdf) this pump is not intended for use IN an RV but rather as a shore-side pump. As such it assumes that it will have full shore power available for starting and no effort was made to make it easy to start. (In fact, the descriptive name for it elsewhere on the site is "Park Model Pump.")
The recommended fuse is 1 AMP time-delay which also suggests a high starting surge.
There are threads about starting surge and ways to reduce the surge, some of which may apply to your pump, but you may be better off replacing it with a pump that is better designed for your circumstances.
The Honda EU20001 has good surge power capabilities for an inverter model generator, but a traditional generator can often have larger surge ratings because it can suck power from the energy of the spinning "flywheel" and deliver current even as it slows down under the load.SMA SB 3000, old BP panels. -
Re: My Honda EU2000i wont power this tiny Shurflo pump
If the pump itself is working too hard (undersized) it will remain in start-up too long like inetdog said. In general it's not a direct replacement for a 1/2 HP centri-pump; you'd have to change a lot more (the plumbing). -
Re: Why does this Shurflo pump seem so great? Will it work for my house with my EU2000i
If a Honda EU 2000 won't start a pump that takes .9 amps, Honda is in trouble. I agree it has a starting surge, it still should start that pump.
115 VAC, 3.3 GPM, 45 PSI, .9 Amps Open Flow
This quiet pump is self priming and can run dry without damage
Built-in check valve
Thermally Protected & Installs Easily
2 Year Limited Warranty -
Re: Why does this Shurflo pump seem so great? Will it work for my house with my EU2000iBlackcherry04 wrote: »If a Honda EU 2000 won't start a pump that takes .9 amps, Honda is in trouble. I agree it has a starting surge, it still should start that pump.
115 VAC, 3.3 GPM, 45 PSI, .9 Amps Open Flow
This quiet pump is self priming and can run dry without damage
Built-in check valve
Thermally Protected & Installs Easily
2 Year Limited Warranty
Good point. Another interesting test to make, since the pump can run dry, is to disconnect the inlet water. This is a diaphragm pump and so there is a displacement load on the motor immediately during startup, unlike a centrifugal pump which is not really loaded until it builds up speed.... and only a few spits of water comes out.
I cannot think of any way to miswire the pump to the inverter that would cause it to behave as reported.SMA SB 3000, old BP panels. -
Re: Why does this Shurflo pump seem so great? Will it work for my house with my EU2000iGood point. Another interesting test to make, since the pump can run dry, is to disconnect the inlet water. This is a diaphragm pump and so there is a displacement load on the motor immediately during startup, unlike a centrifugal pump which is not really loaded until it builds up speed.
I cannot think of any way to miswire the pump to the inverter that would cause it to behave as reported. -
Re: Why does this Shurflo pump seem so great? Will it work for my house with my EU2000iBlackcherry04 wrote: »What I was thinking is that the the hot is connected to the pump windings and the neutral is running through the switch. Don't know if that would make a difference, I guess it depends on how the ground is hooked to the pump.
Since both hot and neutral are isolated from ground, it should not make any difference electrically. The reason people always say to put the switch in the hot and not the neutral is that if you put the switch in the neutral and turn it off, there is still full voltage on the wiring of the load and you could get hurt thinking that it is "turned off".
If there is a short circuit between some part of the motor winding and ground (defective pump) then the way the three wires are hooked up could make a difference. But an ohmmeter will allow you to test for that.SMA SB 3000, old BP panels. -
Re: Why does this Shurflo pump seem so great? Will it work for my house with my EU2000i
I can not understand why it won't start. It's such a tiny pump. All I can think of is that the diaphram action keeps spiking the current (even though it should be small) and the electronics of the Honda don't like it. -
Re: Why does this Shurflo pump seem so great? Will it work for my house with my EU2000i
Try placing a 100 watt bulb on parallel with the pump.
An old trick to stabilize a generator or inverter with sensitive loads.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Why does this Shurflo pump seem so great? Will it work for my house with my EU2000i
Just a precautionary remark on the generator usage. I believe that it is quite rough on the generators to start and stop the engines under load. Also I don't quite understand how the EU2000 can cope better with the load this way. Sounds to me as if there is a maladjustment in your generator.
What height do you live in? I got clients here in the Sierra Nevada in Spain who has to turn up the rev's on their generators to cope with the height. Problem seems to start around 1200m8 x 250Wp Suntech (wife insisted on a dish washer), Outback VFX 3024, Midnite Classic 150, 4 Rolls 6CS25p. Solar installer in Southern Spain. -
Re: Why does this Shurflo pump seem so great? Will it work for my house with my EU2000i
True, mine uses under 100 watts. if you can run a lightbulb it should start if its wired correctly. I have been having problems with mine, but not getting it to run. I keep loosing prime or something. I must find out where air is entering my line. bummer! -
Re: Why does this Shurflo pump seem so great? Will it work for my house with my EU2000i
You could always replace that pump with on old Duro piston.
They happily start with the EU 1000i.Island cottage solar system with appriximately 2500 watts of panels, 1kw facing southeast 1.3kw facing southwest 170watt ancient Arco's facing due south. All panels in parallel for a 24 volt system. Trace DR1524 MSW inverter which has performed flawlessly since 1994. Outback Flexmax 80 MPPT charge controller four 467A-h AGM batteries. Insignia 11.5 cubic foot electric fridge 1/4hp GSW piston pump. My 31st year.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed