Inverter Issue
GreenPowerManiac
Solar Expert Posts: 453 ✭✭✭
Having an issue with "Input too high" on voltage with this inverter: PE-4500PSW on TopSalesDepo.com
The voltage when erroring out reads 15.2-15.5v and the battery bank is about 14v. With 13 Gel SLA batteries, it doesn't give my charge controller (Morningstar ts-45) a chance to divert the load since it's dip-switch settings are at 14v. Won't set any lower that I know of. The issue is that the inverter voltage and readings are incorrect and need to be calibrated somehow. Is this inverter capable of firmware update? Something else was mentioned: "pot". Acronym for ??? NOT WEED, either.
The voltage when erroring out reads 15.2-15.5v and the battery bank is about 14v. With 13 Gel SLA batteries, it doesn't give my charge controller (Morningstar ts-45) a chance to divert the load since it's dip-switch settings are at 14v. Won't set any lower that I know of. The issue is that the inverter voltage and readings are incorrect and need to be calibrated somehow. Is this inverter capable of firmware update? Something else was mentioned: "pot". Acronym for ??? NOT WEED, either.
Nature's Design & Green Energy on FaceBook : Stop by and "Like" us anytime.. Many up-to-date articles about Renewables every day.
WWW.GreenAnything.Net Ad free website.
Lots of DIY Renewable Energy Projects on ETSY : Solar Panel builds, Wind Turbine builds, Rain Barrel build,etc.
WWW.GreenAnything.Net Ad free website.
Lots of DIY Renewable Energy Projects on ETSY : Solar Panel builds, Wind Turbine builds, Rain Barrel build,etc.
Comments
-
Re: Inverter Issue
POT =potentiometer .usually rotary a variable resistor "ie the volume control in a radio" -
Re: Inverter Issue
GPM, I hate to say it but this is a problem often found on inexpensive inverters. Usually it's the 15+ Volts of EQ that causes them to scream "over Voltage!" and shut down. In this case it seems it is calibrated wrong and thinks your 14 Volt Absorb level is a Volt higher than reality.
The pot (potentiometer as John explained) may be for adjusting that calibration so that the inverter detects correct Voltages. If you can't do that then you'll have to shut the thing off while the batteries charge. Major nuisance! Otherwise it looks like you've got a new doorstop. :roll: -
Re: Inverter Issue
A very common problem. Even my Morningstar SureSine inverters will shut down in Winter when the batteries are cold and the battery voltage sometimes exceeds 15.5 volts. Some inverters can handle 16, 16.5 or even 17 volts before they shut down. Check the specs before you purchase. Your batteries must be permitted to properly change, otherwise they will all too soon get ruined, so don't do like a friend? of mine did. Every time his battery voltage went above 12,5 he's turn on his inverter and load it up - - "to keep the batteries from overcharging". Now his batteries are useless after just 6 months and he just "knows" in his heart that it's his own fault for letting them overcharge. Hahahahaha -
Re: Inverter Issue
Hi GPM,
Well, before the inverter HVD issue, two other things come to mind:
1. Think that 14 volts is a bit hot for Gel charging. Deka considers this to be MAX, but do not know what Gel batts you have, and the charging specs. Too bad that you have only Dip Switches to set the crucial charge voltages for these sensitive and expensive batteries (IMHO). Know that you are using a Battery Temp Sensor on all charge sources.
2. Am sorry, did you say 13 batteries ???!!!?!..? Are these 13ea 12V batts? Or just what is the string config? Hope that it is not 13 parallel 12 V batts.
Whatta I know? Sjorry for the attitude, VicOff Grid - Two systems -- 4 SW+ 5548 Inverters, Surrette 4KS25 1280 AH X2@48V, 11.1 KW STC PV, 4X MidNite Classic 150 w/ WBjrs, Beta KID on S-530s, MX-60s, MN Bkrs/Boxes. 25 KVA Polyphase Kubota diesel, Honda Eu6500isa, Eu3000is-es, Eu2000, Eu1000 gensets. Thanks Wind-Sun for this great Forum. -
Re: Inverter Issue
Yes. 13 parallel batts.
Problem somewhat fixed. Did a Fonzerelli tap on the face of the digital display. Lol. Voltage came down half a volt! WTF? And put a 24 hour timer on it running a battery car charger during its peak production hours. Got lots of things to charge out there.Nature's Design & Green Energy on FaceBook : Stop by and "Like" us anytime.. Many up-to-date articles about Renewables every day.
WWW.GreenAnything.Net Ad free website.
Lots of DIY Renewable Energy Projects on ETSY : Solar Panel builds, Wind Turbine builds, Rain Barrel build,etc. -
Re: Inverter Issue
Ah, there's nothing like buying quality equipment! -
Re: Inverter Issue
Yes. 13 parallel batts.If that doesnt create enough heartache to send Dr Phil into a spin you are the luckiest battery owner in the world.
2 batteries in parallel = ok
3 batteries in parallel = just so so
4 batteries in parallel =problem
5 batteries in parallel = not good
6 batteries in parallel =big problems
7 batteries in parallel = huge problems
8 batteries in parallel = disaster
9 batteries in parallel = big disaster
10 batteries in parallel = train disaster
11 batteries in parallel = Chernobyl disaster
12 batteries in parallel = Japan Tsunami
13 batteries in parallel = bigger than Titanic disaster -
Re: Inverter Issue
wire the parallel batteries properly - on the diagonal:
http://www.smartgauge.co.uk/batt_con.html
But more than 4 parallel circuits, it really becomes un-predictable, even using buss bars & matched cables.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister ,
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed