Fuse/breaker location for inverter
westyd1982
Solar Expert Posts: 85 ✭✭
I have a Morningstar Suresine 300 inverter, and in its installation instructions it recommends a 100 amp fuse no further than 12" from the battery terminal. I'm looking at upgrading the charging capabilities of my system and am thinking about building the upgraded system around a Midnite Solar Mini DC Disconnect Power Center.
My question is do I need fuses in the battery box close to the positive battery terminal for each positive wire? Or can the disconnect with appropriate breakers handle the circuit protection correctly at the end of 5 feet of 2/0 wire? Or should I have a fuse larger than the disconnect breaker in the battery box to protect the wire in case of a catastrophic failure (earthquake or fire that damages the insulation on the 2/0 wire)?
I currently have fuses on each of the three positive wires attached to the battery: charge controller, Suresine, and a 1000W MSW inverter. With the Midnite Solar Mini DC Disconnect Power Center, I'd just have the 2/0 cables.
My question is do I need fuses in the battery box close to the positive battery terminal for each positive wire? Or can the disconnect with appropriate breakers handle the circuit protection correctly at the end of 5 feet of 2/0 wire? Or should I have a fuse larger than the disconnect breaker in the battery box to protect the wire in case of a catastrophic failure (earthquake or fire that damages the insulation on the 2/0 wire)?
I currently have fuses on each of the three positive wires attached to the battery: charge controller, Suresine, and a 1000W MSW inverter. With the Midnite Solar Mini DC Disconnect Power Center, I'd just have the 2/0 cables.
Comments
-
Re: Fuse/breaker location for inverterwestyd1982 wrote: »Or should I have a fuse larger than the disconnect breaker in the battery box the protect the wire in case of a catastrophic failure (earthquake or fire that damages the insulation on the 2/0 wire)?
--vtMaps4 X 235watt Samsung, Midnite ePanel, Outback VFX3524 FM60 & mate, 4 Interstate L16, trimetric, Honda eu2000i -
Re: Fuse/breaker location for inverter
The wires run through conduit from the battery box. -
Re: Fuse/breaker location for inverter
What size breaker came with your MNDC, and are you using it as the breaker for the inverters or as a battery disconnect with more fuses/breakers between it and the inverters and controller?4-Risen 320 watt in series/parallel, 8-215ah 6 volt GC2 batteries in series, Exeltech 1100 watt/48 volt inverter, Tristar 45 MPPT controller. -
Re: Fuse/breaker location for inverter
The idea of breakers/fuses is to protect the wiring from short circuits. And placing the breaker as close as practical to the source of energy keeps the "unprotected" wiring distance short too.
Personally, I would probably want a breaker before I put a pair of cables into a conduit. Yes, the conduit does protect against falling sharp objects and wear+tear--However, there have been shorts that develop inside conduit too (why? don't know--damage during installation, failure from chemicals, stress on wiring, pinched conduit???). Having an insulation failure in heavy cable with no breaker back to the battery bank--can be scary.
If possible, I would install the breaker on the outside of the battery box. Keep the unprotected cable short and the breaker/fuses outside of the box (away from acid mist and hydrogen gas).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Fuse/breaker location for inverter
BB -
Thanks. Right now, I have a 150 amp fuse on the 2/0 wire for the MSW inverter. I'll keep it in the upgraded system. Right now I have fuses close to where they attach to the battery terminal. Unfortunately, I don't have space to have them outside the battery box (see photo below). I occasionally look for signs of corrosion. So far after 3 years my battery box stays very clean inside and I haven't noticed anything.
Attachment not found. -
Re: Fuse/breaker location for inverter
Consider using a Bluesea battery terminal fuse system. Comparitively cheap, and easy to customized both for charge circuits and load circuits.
Tony -
Re: Fuse/breaker location for inverter
rgk1 -
I haven't purchased a MNDC yet. I was looking at the 125 or 175 amp versions. I'm thinking of having it as the battery disconnect with everything else on its own breaker after the main breaker. -
Re: Fuse/breaker location for inverter
This is the link to the BlueSea bus/fuse terminal (very neat device) that Tony typed about (two and one fuse devices are available):
http://bluesea.com/products/2151
Attachment not found.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Fuse/breaker location for inverter
Westyd1982, as everyone says, having a fuse on or at the batteries is a goood idea. I use a 110 amp class T fuse at the batteries as the first line of protection for all the wiring. I currently use Anderson connectors to disconnect the batteries, but will be removing that, running the battery leads in conduit into the MNDC and use the (175 amp) breaker as the disconnect. Then like you said, separate breakers to the other components. The MNDC is a great box to neatly connect everything and can hold 5 din breakers or 3 panel mount.4-Risen 320 watt in series/parallel, 8-215ah 6 volt GC2 batteries in series, Exeltech 1100 watt/48 volt inverter, Tristar 45 MPPT controller. -
Re: Fuse/breaker location for inverter
This Class T fuse (in a fuse holder block) is on the battery positive terminal. The cables than go to a Midnite Mini DC with a 250 amp breaker. Code wise, any fuse is supposed to have a means of de-energizing it so it will not have any voltage potential if you need to replace it. In this case I'd rather have the protection at the terminal than be to the letter of the code. The inspector agreed in this case.
Attachment not found. -
Re: Fuse/breaker location for inverterThis is the link to the BlueSea bus/fuse terminal (very neat device) that Tony typed about (two and one fuse devices are available):
http://bluesea.com/products/2151
Attachment not found.
G
-Bill
Thanks Bill, not a lot of time these days, and not too much bandwidth.
T -
Re: Fuse/breaker location for inverter
Tony--And I have, obviously, have too much time and bandwidth.
Love,
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed