Voltage Drop???
pabloesguapo
Solar Expert Posts: 116 ✭✭
I am designing an off-grid system. I am wondering about panel vs. battery placement.
The major components of the system are:
24 panels @ 210 Watts 18.70 Vmp
6 Volt deep cycle, 225 amp/hour wet cell batteries wired in series.
Xantrex Solar Charge Controller 60A MPPT-60
Xantrex Grid-Tie/Off-Grid Inverter/Charger 4500 Watts 48 Volts XW4548
I'm planning/hoping to mount these panels on a shed I'd like to build (a 30 degree slanted roof, facing due south) instead of on the roof of my house. The pitch of the house's roof is rather extreme, both sides face due east and west, not south, and I don't like the idea of having to get way up there to clean/maintain the panels. I'd rather do that on a shed roof 10-12 ft in the air set on a less sever angle.
I'd like to place the batteries in the shed (to provide electricity for the power tools) until we complete construction on the house. Then I'd like to permanently relocate them to the basement.
I have several questions:
1) Is it OK to have these batteries in the shed for the summer? Will the summer heat "kill" them?
2) Is it necessary to move them out of the shed and to the basement at all? Will the winter cold "kill" them?
3) Regardless of the location of my batteries (or charge controller or inverter, for that matter) what is the best way to avoid voltage drop? The shed will be located up to 50 ft. away from the house. (We plan on planting a few deciduous shade trees in between house and shed to aid in summertime cooling)
The major components of the system are:
24 panels @ 210 Watts 18.70 Vmp
6 Volt deep cycle, 225 amp/hour wet cell batteries wired in series.
Xantrex Solar Charge Controller 60A MPPT-60
Xantrex Grid-Tie/Off-Grid Inverter/Charger 4500 Watts 48 Volts XW4548
I'm planning/hoping to mount these panels on a shed I'd like to build (a 30 degree slanted roof, facing due south) instead of on the roof of my house. The pitch of the house's roof is rather extreme, both sides face due east and west, not south, and I don't like the idea of having to get way up there to clean/maintain the panels. I'd rather do that on a shed roof 10-12 ft in the air set on a less sever angle.
I'd like to place the batteries in the shed (to provide electricity for the power tools) until we complete construction on the house. Then I'd like to permanently relocate them to the basement.
I have several questions:
1) Is it OK to have these batteries in the shed for the summer? Will the summer heat "kill" them?
2) Is it necessary to move them out of the shed and to the basement at all? Will the winter cold "kill" them?
3) Regardless of the location of my batteries (or charge controller or inverter, for that matter) what is the best way to avoid voltage drop? The shed will be located up to 50 ft. away from the house. (We plan on planting a few deciduous shade trees in between house and shed to aid in summertime cooling)
27 Kyocera panels, 6,500w
24 CG2 6v batteries, 48v, 630Ah
Midnite Classic 150 & Classic 150 Lite in "follow me" mode
(2) Outback fx3648 inverters
Generac ecogen 6kw backup generator
24 CG2 6v batteries, 48v, 630Ah
Midnite Classic 150 & Classic 150 Lite in "follow me" mode
(2) Outback fx3648 inverters
Generac ecogen 6kw backup generator
Mate3s
Comments
-
Re: Voltage Drop???pabloesguapo wrote: »
1) Is it OK to have these batteries in the shed for the summer? Will the summer heat "kill" them?
Keep the shed ventilated, and below 100F if possible2) Is it necessary to move them out of the shed and to the basement at all? Will the winter cold "kill" them?3) Regardless of the location of my batteries (or charge controller or inverter, for that matter) what is the best way to avoid voltage drop? The shed will be located up to 50 ft. away from the house. (We plan on planting a few deciduous shade trees in between house and shed to aid in summertime cooling)Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Voltage Drop???
So, it seems that keeping the batteries, controller and inverter inside the house will be a wiser choice in the long run. Better safe than sorry. I'll still mount the panels on the shed, but run cable to the batteries in the basement in between foundation completion and the beginning of sub floor install...
But what about the string calculator? Where do I find?27 Kyocera panels, 6,500w
24 CG2 6v batteries, 48v, 630Ah
Midnite Classic 150 & Classic 150 Lite in "follow me" mode
(2) Outback fx3648 inverters
Generac ecogen 6kw backup generatorMate3s -
-
Re: Voltage Drop???
Called the company I''m planning on purchasing from, www sunelec.com. Anyone have any opinions or history with these guys? Their prices are really good...
I plan on buying this system.
They told me that for my long run, I should probably go with a #6 or a #4 cable between the combiner box (in the shed) and the voltage regulator (in the house). The length could possibly be between 50 and 70 feet. I used the following calculator to gauge voltage drop. http://www.stealth316.com/2-wire-resistance.htm Also, I found a good source for wire and cable. I can get #4 gauge wire for $1.61 a foot.
So, correct me if I'm wrong, please. The amperage of my panels (link), if wired in series, will be the same as the amp rating of one of the panels? So, that would be 11.23 amps. If run in series, the voltage of my panels will be 18.7 Vmp each, times 5 in a series, times 5 series? (Maximum power, I know...) That's 18.7Vmp x 5 x 5= 467.5 Volts? According to the aforementioned calculator, my voltage drop with 70 ft of #4 wire would be 0.1988 volts?
Their web site says the batteries would be run in series. (6v at 225 amp hours each). What would that get me in terms of voltage and amp hours?27 Kyocera panels, 6,500w
24 CG2 6v batteries, 48v, 630Ah
Midnite Classic 150 & Classic 150 Lite in "follow me" mode
(2) Outback fx3648 inverters
Generac ecogen 6kw backup generatorMate3s -
Re: Voltage Drop???
I am on my phone right now, but I think you are multiplying Vmp by one too many 5s.
Vmp x 5 for array voltage. And Imp x 5 if you have 5 parallel strings (for 25 series/parallel connected panels).
Now is the time to be very clear and exact about your system configuration.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Voltage Drop???
here's the link to the voltage drop calculator listed in the FAQ, it's a spreadsheet,
with instruction notes at the bottom
http://www.solar-guppy.com/download/voltage_drop_calculator.zip
What you want to do, is get your array voltage as high as possible, for the long cable distance, and let the MPPT downconvert it to amps at the battery.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Voltage Drop???
Just a quick look at those panels shows them to be blems and have no UL or other certifications. Are you ok with that? -
Re: Voltage Drop???
SEven: OK, try these:
http://www.sunelec.com/canadian-solar-panel-230-watts-2960-vmp-p-1399.html
More bang for the buck...
B.B. : Yes, 25 panels, so times 5 times 5.27 Kyocera panels, 6,500w
24 CG2 6v batteries, 48v, 630Ah
Midnite Classic 150 & Classic 150 Lite in "follow me" mode
(2) Outback fx3648 inverters
Generac ecogen 6kw backup generatorMate3s -
Re: Voltage Drop???pabloesguapo wrote: »SEven: OK, try these:
http://www.sunelec.com/canadian-solar-panel-230-watts-2960-vmp-p-1399.html
More bang for the buck...
B.B. : Yes, 25 panels, so times 5 times 5.
Ned -
Re: Voltage Drop???
@Offgrid Me: OK, got it. Since I'm going into a combiner box, I only multiply by 5 once, nand not multiply again for all 5 strings. Right?
Also, thanks for the heads up on Sunelec. I have noticed that about them, great prices, but hard to get a hold of, hard to get good answers out of them. I have started calling their Miami offices to get questions answered instead of calling their Phoenix warehouse.
BUT... Being the raging cheapskate that I am, I am drawn to low prices (like a moth to a bug zapper) and am willing to put myself through a steep learning curve in order to save a few bucks. I can't stand to pay extra $$$ to have someone do something for me that I could easily do with a little bit of homework and a drop or two of my own elbow grease.27 Kyocera panels, 6,500w
24 CG2 6v batteries, 48v, 630Ah
Midnite Classic 150 & Classic 150 Lite in "follow me" mode
(2) Outback fx3648 inverters
Generac ecogen 6kw backup generatorMate3s -
Re: Voltage Drop???
Right. You will probably need to run the voltage drop calculator again with the ISC value of 56 amp. Dont forget to use the total run there and back (140') in the calculator. You may find that 6 awg is not large enough to maintain the recommended 2% max voltage drop for this long a run. I understand the allure of cheap prices but some bargains are not bargains in the long run. Do a lot of research before purchasing anything and run your design by the people on this site. They are not trying to sell you anything and will not steer you wrong. -
Re: Voltage Drop???
Some very rough numbers:- Vmp-array = Vmp * panels in series = 18.7 volts * 5 series panels = 93.5 volts Vmp-Array
- Imp-array = Imp * panels or strings in parallel = 11.23 amps * 5 parallel strings = 56.15 amps Imp-array
- 93.5 volts * 1% drop = 0.935 volts drop (~cost effective minimum)
- 93.5 volts * 3% drop = 2.805 volts drop (~maximum recommended drop)
- 70' foot run, 56.15 amps, 0.935 volt drop => 1/0 gauge wire for ~0.9 volt drop
- 70' foot run, 56.15 amps, 2.805 volt drop => 4 gauge wire for ~2.4 volt drop
- 56.15 amps * 3.7 volts = 208 watts of wasted power (as heat with 6 awg)
- 56.15 amps * 2.4 amps = 135 watts of wasted power (with 4 awg)
- 56.15 amps * 0.9 amps = 50.5 watts of wasted power (with 1/0 awg)
You have to decide if 210 watts of "wasted panel" vs the cost of 4 awg (or even 1/0 awg) cable is worth it to you or not.
Please note, you do not need to carry all of the decimal places--I just included them so you can follow (and hopefully repeat) my math.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 887 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed