4 KW PV in Alaska
Fullpower
Solar Expert Posts: 69 ✭✭
Battery bank 24 volts:
Deka L16 370AmpHour 6Volt x 4
Rolls S-1590 1200 AmpHour 2Volt x 12
Re: 4 KW PV in Alaska
East Array, SANYO 220 watt x 8
Love Pics !
How are you dealing with all the different panels as far as connecting them to charge controllers, etc ?
andy -
mixing different batteries can lead to problems. -
Re: 4 KW PV in Alaskamixing different batteries can lead to problems.
Especially if that's 370 Amp hours paralleled with 1200 Amp hours. I hope those are two separate battery banks, otherwise there is no way the charging will by right on either one. -
Awesome pics! Tell us a little more about how its wired? -
House Array, 2300 watts -
4 KW PV in Alaska
If you the lightning in the area and/or interference on radio receivers, take some time and reroute the DC power leads.
Ideally, they should run in pairs (+/-) and be bundle tied together from point to point (you can even twist them, but for large cables, not very practical to get tight twists).
What happens is the "loops" become quite good antennas... Both picking up interference (nearby lighting strikes) and transmitting (radio frequency interference).
Keep cables runs (signal, DC, AC) from running in parallel (coupling of RF noise) and cross the cables at 90 degrees.
Bus Bar, hammered copper tube, silver soldered solenoid studs, heavy brass hex nuts
Zero measurable voltage drop with 200 amp load.
The house array is a motley assortment of 12 volt nominal modules, in series pairs,
Open Circuit 42 Volts, peak output through one Outback FM-80 is 64 amps, at 29 volts.
The POLE array, nominally 1760 watts, is wired for open circuit 104 volts, and is wired with 2 gauge welding lead, 65 feet to a second FM-80 mppt controller, which steps voltage down to 29 volts, more on a cold day. Maximum from this array so far was 11 october, peaked at 62 amps.
Total input from both arrays on that day was 16.5 Kilowatt Hours. -
System has been growing in stages. Finally stuck the entire battery bank underground in september.
You can imagine the happy sound of 2 volt batteries, with 126 AMPS of pure solar charge, at 29.6 volts.
Two charge controllers, each wired to bus bars with 2 gauge welding lead, warm to the touch.
Bring on the AMPERES. -
the pipe acting as a busbar is insufficient and quite possibly a hazard with that kind of current passing through. -
the pipe acting as a bus bar in this case would be adequate, providing the wall thickness is at least 3/32as its less than 1/2 inch between each connection. Im interested about on the right there is a #4 ? black wire going to a little black"fuse" ?relay? but a #12 wire coming from it ??
I also think it is far from good to be using a mixture of black and red wires . -
Re: 4 KW PV in Alaskathe pipe acting as a busbar is insufficient and quite possibly a hazard with that kind of current passing through.
With 200 amperes DC load, there was no measurable voltage drop across the busbar,
the 2/0 battery series jumpers get slightly warm, the 200 Amp fuses get warmer yet,but busbar stays COLD.
Thank you for your concern with fire hazard.
You seem to be under-estimating the conductivity of clean copper. -
John, I concur re wire colours..
As well the mixing of cable colour and the shrink wrap could be a bit confusing. Same colour on both would eliminate any possible confusion.
Here is the FM-80 charge controlles, showing a combined peak of 132 AMPS charging. -
Re: 4 KW PV in AlaskaHouse Array, 2300 watts
Saves on painting ! Are the panels mounted onto Stucco ?? Anchor bolts ? Toggle bolts ??Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
re: cable crimps. Looks like a single crimp ring, like a drilled out bolt cutter. I thought there were supposed to be several crimps like that per lug, when using that style.
If your wires are getting warm from the amps, better check the lugs and make sure they are not heating up too. Better yet, reduce the losses and go with a larger wire.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
All lugs are soldered, after crimping.
- 228 Forum & Website
- 618 Discussion Forums/Café
