Blown Outback Charge Controller
Alright Experts I need some help.
I have two trailers with identical systems.
30 Trina PA05-225W Modules in 3 modules x 5 strings per charge controller
2 FM 60 Charge Controllers
2 Outback 3648 in a Flexpower 2 FP-29 Package
per trailer.
For some reason one of the FM60s keeps blowing.
I have had service calls twice to replace this same charge controller over the last 6 months.
I have checked groundfaults, breakers, grounding on the DC and AC sides to no avail. I have also changed the gfdi breaker on this unit and added a second breaker between the gfdi and the battery to act as a load break switch.
I am totally baffled why this may be occuring.
The other trailer's system has had no problems.
Any advice would be most appreciated
    Re: Blown Outback Charge Controller
    re array, whats the :
    Voc cold ____
    Voc hot ____
  • solarquestion2011
    solarquestion2011 Registered Users Posts: 9
    Voc: 36.8V @ STC , 110.95V String
    Voc: 40.66 @ -15C , 121V String
    First Time it Blew Voc of each string was about 108VDC
    This Time the tech checked and the string was 98VDC.
    150V max is the input voltage for the fm60 i think.
    If all else is equal and only the one controller in the same location is dying I would suspect a wiring fault to that location. Likely as not it is an intermittent problem - the hardest to find. Since the input and output should both have circuit protection, it might be something is shorting on the "wrong side" of that; hot touching ground on the output would be favourite.
    Difficult to diagnose by remote. Not so easy in person either, eh?
  • solarquestion2011
    Its possible that this could be the cause as there is over-current protection at the combiner on the strings and the gfdi with breakers between the battery and the charge controllers. If this was the case wouldn't the gfdi open if the short was in the enclosure. The first time it blew I was looking at it. I did not see any arcing at the charge controller just the sound of popping inside. There was arching in the gfdi breakers also. It was strange, I had cycled the system several times then one time it just blew.
    For Note: The GFDI is the Outback Unit with the twin 80A Breakers ganged with a .5A gfdi breaker.
    I originally feared that the GFDI was not clearing properly and replaced the unit after the first failure along with the charge controller.
    I have to confess to not being a fan of DC GFCI. What I'd do is probably illegal; remove the GFCI stuff.
    But it still isn't likely to be the problem as all the systems are the same and only one FM is frying.
    I can't imagine a situation that would cause that one controller to somehow become connected to both arrays in series (negative from one array being interrupted and at the same time shorting to positive of the other; controllers have shared negatives) but that would fry it too.
  • waynefromnscanada
    Arcing in the gfdi breakers? Now that's scary!
  • solarquestion2011
    It was strange. The gfdi breaker appeared to try to trip, but got stuck half way. I manually opened the breaker as it was arcing and popping. Strange thing was that the CC continued to blow even after opening the gfdi and the ganged breakers between the battery and the CC. At first I thought maybe the gfdi breaker was not able to break under load. I checked with Outback and Tech Support said that I was rated for load break operation. I didn't see if the arcing in the breaker was in the gfdi or the CC breakers attached (I was quickly walking down the step ladder. ha)
    The whole episode began after I cycled the breakers a couple of times.
    - PV circuit was closed to the CC
    - Inverter was on but not pulling a load.
    - Breaker was cycled several times with no problems.
    Should I bother to mention they're not supposed to do that?
    They are supposed to trip if something goes wrong - load or no.
  • solarquestion2011
    I do know that.
    That's why I replaced all the breakers after the first incident along with the CC.
    I assumed that the breakers weren't clearing properly.
    I personally do not like DC GFI setups...
    However, one way to debug the GFI is to use a filament light bulb.
    Pick a 40 watt or so 120 VAC appliance light and place it across your 48 volt battery bus--it should light... If not, you may have to take 4x 12 volt car bulbs (brake lights or similar) in series... Anyway, something that lights on 48 volts.
    Place the filament light bulb across Battery Return and Trailer Frame/Earth Ground...
    Start moving wire and equipment and see if you can trip the GFI breaker and/or get the test lamp to light. The lamp will show + to earth ground short circuits---but limit the current to something less spectacular (just enough to light the lamp).
    You could also hard bond your battery bank return to trailer frame (bypass the GFI breaker)--You might find the short that way too (trip a branch circuit breaker)... But it may be bit more eventful.
    i don't think i'm quite following this as you keep saying the fm60 is blown. define blown. i can't figure how any short or any other condition with your said equipment in the system would blow an fm60 unless somehow ac power got caught up in the mix. is the inverter output somehow feeding into that controller? this is crazy. there obviously is a difference between the trailers or one wouldn't be failing. do try bb's light bulb idea and keep looking as it has to be there even though it isn't obvious to you.
  • solarquestion2011
    by blown I mean the CC is dead. The CC smells of burned electrical equipment and the room had a little smoke in it. The CC that i had previously replaced in the system in the same location sounded like popcorn popping when it blew. There appears to be a nothing between the pv input terminals and the CC output terminals. The PV input terminals are now reading the 48V battery voltage not the pv array voltage normally measured.
    To make it stranger the other CC is still running and the inverters are fine like nothing happened.
    if i read that rightly you are not seeing the pv volts at the input to the cc. if so disconnect the pvs from the cc and see if proper pv voltages are still there. there isn't that much to this so please recheck everything step by step. is the anyway you can verify proper operation on the inverter in the trailer in question in addition to polarities being properly observed?
  • solarquestion2011
    When pulled from the CC the pv voltages were correct and polarities checked (~100V).
    Checked the voltages and polarities at blown CC
    At PV input 48V
    At CC output 48V
    Checked the voltages and polarities at the other CC to compare
    At PV input 100V
    At CC output 48V
    Afterwards the PV for that CC was disconnected at the combiner, b/c i was afraid of the batteries backfeeding the array at night.
    The Inverter and other CC are running normally.
    this is a baffler and if you find the cause, do let us know please.