I'm ask this question
henry1
Solar Expert Posts: 51 ✭✭✭✭
If 13 watts equal 1-amp hour out of the battery unit so how many watts per hour is my draw out of my system x-10 battery string system .-x-255 amp hours per battier-x-10 battery string for total -x-2550 amps total for the string of 10 batties ..
So how many watts total for the whole single bank
So how many watts total for the whole single bank
Comments
-
Re: I'm ask this question
If the batteries are connected in parallel, then the amp hours add.
In
Note, for longer battery life, try to not discharge more than 50% of capacity.
Also, having a lot of batteries in parallel makes it difficult to balance current equally through all batteries equally.
Charging watts: 2,550 ah x 14.5 volts = 36,975. WattHours in
Discharging watts: 2,550 ah x 12.0 volts = 30,600. WattHours out
The above numbers are approximate.
There are lots of issues with lots of batteries in parallel. Is there some reason you need this setup?
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: I'm ask this question
welcome henry,
1st of all 13w will not be 1a for a battery. the nominal voltage for a battery is 12v and watts/volts=current. 13w/12v=1.0833a.
also with concerns for why this large of a 12v battery bank aside, the wh is as bb states 12v x 2550ah = 30,600wh (30.6kwh) of which up to 15,300wh can be considered usable. -
Re: I'm ask this questionIf 13 watts equal 1-amp hour out of the battery unit so how many watts per hour is my draw out of my system x-10 battery string system .-x-255 amp hours per battier-x-10 battery string for total -x-2550 amps total for the string of 10 batties ..
So how many watts total for the whole single bank
What kind of batteries? 225 ah sounds like you're talking about 6V golf cart batteries.
If that's the case a single 225 ah golf cart battery is good for about 675 watt hours assuming you only drain it about 50% (deeper discharges will quickly wear out the battery)
So 10 batteries are good for about 6,750 wh.
If you are talking about huge 12V 225ah batteries (weighs about 150 lbs each?) then double than number: 13,500 whs
P.s. please don't put '-x-' in you posts, it makes it hard to read -
Re: I'm ask this questionWhat kind of batteries? 225 ah sounds like you're talking about 6V golf cart batteries.
If that's the case a single 225 ah golf cart battery is good for about 675 watt hours assuming you only drain it about 50% (deeper discharges will quickly wear out the battery)
So 10 batteries are good for about 6,750 wh.
If you are talking about huge 12V 225ah batteries (weighs about 150 lbs each?) then double than number: 13,500 whs
P.s. please don't put '-x-' in you posts, it makes it hard to read
First off Sorry about that ..I was trying to times the batties by the number of ten to make a total single string of ten batterys in the string and yes that one the huge 12V 225ah batties that way 150.pds each .
I would like 10 each of those batties in each of the battie strings for use on the cabin design .. -
Re: I'm ask this question
Hi Henry,
to be clear : Are your 10 - 12 v batteries in series or parallel?
If the batteries are in series you have a 120volts and 225 amps
If the batteries are in parallel you have 12 volts and 2250 amps.
This is a very important issue. Which do you have?
KID #51B 4s 140W to 24V 900Ah C&D AGM
CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM
Cotek ST1500W 24V Inverter,OmniCharge 3024,
2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
West Chilcotin, BC, Canada -
Re: I'm ask this questionwestbranch wrote: »Hi Henry,
to be clear : Are your 10 - 12 v batteries in series or parallel
If the batteries are in series you have a 120volts and 225 amps
If the batteries are in parallel you have 12 volts and 2250 amps. -
Re: I'm ask this question
Going with the 10% rule, you will need at least a 225a charger to keep that kind of battery bank happy. -
Re: I'm ask this question
It's very difficult to get 10 batteries to charge well in parallel, without 1 hogging all the workPowerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: I'm ask this question
Mike's got it.
Trying to build a 27 kW hour battery bank (2250 Amp hours * 12 Volts) on a 12 Volt system is nearly impossible.
On a 48 Volt system you would have only need 3 parallel banks to get 32.4 kW hours. Far fewer problems with current sharing, high Amperage, et cetera. If you need this kind of power you really should up the system Voltage. -
Re: I'm ask this question
Here is a quick explanation of how to connect multiple parallel batteries properly:
SmartGauge Electronics - Interconnecting multiple batteries
Note, you should have fuses with each battery (prevent a short circuit melting you wiring).
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: I'm ask this question
thank you for the info about the battery set up -
Re: I'm ask this questionFirst off Sorry about that ..I was trying to times the batties by the number of ten to make a total single string of ten batterys in the string and yes that one the huge 12V 225ah batties that way 150.pds each .
I would like 10 each of those batties in each of the battie strings for use on the cabin design ..
10 batteries in each string? How many strings are you going to use?
Why so many batteries for a cabin?
Probably a lot cheaper to reduce your power consumption and then use a smaller solar setup. -
Re: I'm ask this question
The basic idea was to make the bank last a week before switching over to a new bank with new bank was recharge dureing the week with solar and wind or gen set if need .. -
Re: I'm ask this question
The problem is that Lead Acid batteries do not like to sit for days/weeks below 75% state of charge.
If you discharge a bank to 50% and recharge back to 100% the next week--I would fear that your batteries are going to die a few years early from sulphation (the soft lead sulfate that participates in the recharge/discharge cycle begins to crystallize and no longer is in the charge/discharge chemistry--slowly reducing the battery capacity.
Lead Acid it probably the wrong chemistry to use in this type of setup...
There are other chemistry's that do work (NiCad, Lithium Iron Phosphate Batteries; LFP; LiFePO4) (and others?) that would work--but they are probably 2x more expensive and, in the case of NiCad can be expensive to properly recycle/dispose of...
My guess is that a small genset (fuel efficient) is going to be a better/more cost effective solution unless you are ready to go "out there" with other battery chemistry.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: I'm ask this questionThe basic idea was to make the bank last a week before switching over to a new bank with new bank was recharge dureing the week with solar and wind or gen set if need ..
No, no, no, no, NO!
That is NOT the way to set up your batteries.
To get the best life out of Lead-Acid batteries, drain them as little as possible and recharge them as soon as possible.
You don't use one battery bank while charging a different one. You use ONE bank and charge it every day. You can charge the bank while using power.
What you need to do is figure out how much energy (kwh) you need on an average day. Then you find out what the worst case charging will be, for example if 4 day storms are common there, then you'll need to run about 4 days without being able to charge or not much charging) so you size your pack to provide 4 days of power while only using 80% of capacity.
Using only 20% of your batteries capacity on an average day will ensure maximum life from your batteries. -
Re: I'm ask this question
I'm going to turn down the job and focus more on the small system of the place in Northern Az area up on the Four Corners Area to make it my retirement place
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed