Need input for Glass mat Batt
System
Posts: 2,511 admin
I have 2 glass mat batteries that are used only 2 times a years to start generators...
Will a float voltage of 12.98 volts maintain these batteries at the proper charge? They are sunextenders 12 volt
Charlie
Will a float voltage of 12.98 volts maintain these batteries at the proper charge? They are sunextenders 12 volt
Charlie
Comments
-
Re: Need input for Glass mat Batt
AGM's have a very low self-discharge rate. Maintaining them with a constant float charge isn't necessary. If they start the generators a couple of times a year they're probably okay. It might be advisable to check the resting Voltage once a month and recharge if necessary. -
Re: Need input for Glass mat Batt
From their website:Initial charge or recharge: 2.37 to 2.40 volts per cell at 25 C (77 F). Float charge: 2.20 to 2.22 volts per cell at 25 C (77 F). Equalize charge: 2.40 volts per cell at 25 C (77 F). Temperature compensation = ±3.75 mV. per cell per degree C [Reference to 25 C (77 F)]. This is for battery temperature (not ambient temperature) and is useful for battery temperatures from 0 C (32 F) to 40 C (104 F). Contact Concorde Battery Corporation for temperatures that exceed this range.
For a 12 volt battery, that would be 13.20 to 13.32 volts float voltage. Also, remember that this is at ~77F... If your batteries are stored in a cold area (batteries last longer if kept cool)--say 77F-18F=59F, then:- 6 cells * -10C * -0.00375 volts + ~13.25 volts float = ~13.475 volts
I have done with with a few different cars and it works out well. Before, the "float" chargers plugged in 24x7 to a "maintenance free battery" would require fulling every month or three.
Or, monitor the resting voltage of the batteries... As long as they are over 75% state of charge, they are "OK".
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Need input for Glass mat Batt
an unregulated charge source could continue to raise the voltage on the batteries so some sort of regulation should be used as agm batteries are sensitive to overcharging. you cannot put a unregulated 1 or 2 amp charge source on say a 100ah agm long term.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed