Grid Tied and Generators
Philip C
Solar Expert Posts: 45 ✭
I have a small problem, I need to wire in a 10kW PV system into a building with an existing 22kW generator, usually not a big issue, just tie in on the line side. Well here is the problem; the generator ties in at the transformer/meter about 300ft away from the building.
How can I backfeed the panel without concerns of backfeeding the generator? Can one adjust the frequency tolerance on the inverter to be more sensitive to swings?
Thanks,
How can I backfeed the panel without concerns of backfeeding the generator? Can one adjust the frequency tolerance on the inverter to be more sensitive to swings?
Thanks,
Comments
-
Re: Grid Tied and Generators
You should be able to find a connection upstream, between the generator transfer switch, and the grid feed. Larger generators tend to have pretty good fq regulation, so I don't think you can rely on that to drop the PV inverter.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Grid Tied and GeneratorsYou should be able to find a connection upstream, between the generator transfer switch, and the grid feed. Larger generators tend to have pretty good fq regulation, so I don't think you can rely on that to drop the PV inverter.
-
Re: Grid Tied and Generators
I don't recomend anyone try to use their PV to asssist a generator, unless it's through a hybrid GT/battery inverter. Without battery to take any overload, it's just a matter of time, till the loads become less than the PV is generating, When that happens, the system voltage will suddenly climb, and you have a race to see what happens first:
Generator fries from overvoltage
inverter senses overvoltage and shuts off.
Using only PV inverters and gensets, you have no room for error, or edge of cloud surge.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Grid Tied and Generators
Mike,
To tie in upstream of the gen set would require trenching through a parking lot. So in this case even the Hybrid XP/Sunny Island would not work as you still have to tie upstream (Well at least to sell extra power back to grid)
I was thinking by tighting up the tolarance of the freguency settings, when the PV starts to produce to much power, the frequency will speed up causing the inverter to shut down. But one could never guarantee. -
Re: Grid Tied and Generators
Is there any ac wiring at all (even a single circuit that comes from the utility power?
Run that back to the gt inverter to inhibit the inverter or turn off a solid state relay..
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 425 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed