Selecting the correct backup generator
Anyway, I'll probable end up sellling both and getting the correct model and required bits, but need to know what that is. I want to hook it up to an Outback VFX3524 inverter/charger. At most I'm thinking the max output does not need to go over 3kw (since the inverter won't, and the highest draw I would have would only be about a 1.5kw draw (2.5 kw surge) for the AC unit).
So, what might will I need? I see the Honda 3000i series get good marks and is very quiet .. What about the parts to hook into the inverter (AGS switch, relays, ect).
Thanks for you help!
Roy
Comments
-
Re: Selecting the correct backup generator
The problem I have seen is there are few (if any) small (<3-5 kW) gensets that are setup for automatic start. The Honda's all need to use the choke to start when cold (as I understand)...
I think a eu2000i with auto-start capabilities would be a really nice unit. 1,600 watts is a nice size for a cabin or small off grid home (or even emergency power).
How about anybody here that has done a propane conversion on the Honda eu3000i? Do they start in cold weather without a choke?
Otherwise, what about electric start Onan gensets for RV's... Do they have/need automatic chokes? Can they be setup for auto-start?
Sorry, more questions than answers here.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Selecting the correct backup generator
I have an Onan 5.0 CCK that starts remotely. On gasoline it had an automatic thermo choke, but I removed the choke and the carb butterfly when I converted it to propane as you cannot use a choke on propane - at least with this unit. -
Re: Selecting the correct backup generator
I think I found a possible solution on the Ridgid Generator forum:
http://www.ridgidforum.com/forum/showpost.php?p=314307&postcount=7
Going to see if he still has the plans or is selling the modification. If so, then my current generator should work if I can get a 2/3 wire relay hooked up to it and the AGS on the Outback.
Its a bit of a gas hog, but its better than nothing for an emergency charge when not around.
Roy -
Re: Selecting the correct backup generator
If you want a quiet generator that isnt a gas hog find a diesel generator with a 4 pole alternator.
They are quiet and fuel efficient because they only run at 1800rpms.
I don't care what any one says, there is no such thing as a quiet 3600rpm gas generator.
On of the smallest generators I work on is a little liquid cooled 5kw diesel kubota with a kohler generator. When running at a 2kw load they can go 3 nights dusk till dawn on 14-15 gallons of diesel.Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
-
Re: Selecting the correct backup generator
~36 hours of 2kw load on 15-16 gallons of fuel seems like no bargain!
A honda Eu 2000 will use ~ 1/2 gallon every 6 hours if memory serves. I don't know what a Eu 3000 will burn at 2 kw load.
My ancient Lister 5 kw SL 2 will pump out 5 kw forever on ~ 1/4 gallon of fuel per hour.
Tony -
Re: Selecting the correct backup generator
Only problem with diesel gensets is they need to be constantly loaded to a minimum % to prevent "wet stacking" (lots of info via Google). Suddenly the genset is dead from deposits.
That is usually not a problem in a commercial setting where loads are fairly constant day-to-day... the usual lights, computers, HVAC and industrial equipment. A typical home might need 500 watts 24/7 if they aren't too energy efficient; of course an energy efficient home will need far less. Then an A/C compressor will kick on and the home will need an additional 4000 watts for 20 minutes (even more to get through the startup surge). If you size a genset to handle the peak loads it will run most of the time at >10% of its capacity most of the time. Not an issue for a gas, NG, or LPG genset, but a big issue for diesel.4.5 kw APC UPS powered by a Prius, 12 kw Generac, Honda EU3000is -
Re: Selecting the correct backup generator
The diesel generators seem to run fine for many thousands of hours running at less than a half load.
Diesel generators that wet stack do so from being run at light load or almost no load, throw in worn piston rings and bad valve guide seals and that makes it worse.
If you were real creative you could always run propane or natural gas fumigation.Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
-
Re: Selecting the correct backup generatorIf you were real creative you could always run propane or natural gas fumigation.
What in the world is that? -
Re: Selecting the correct backup generatorThe diesel generators seem to run fine for many thousands of hours running at less than a half load.
Many of them can go down to 40% load without wet stacking, I didn't say you had to stay above 50%, only that there was a minimum %. Even at 40% they usually aren't a good idea for a backup generator because a home's loads are well below that minimum % most of the time.
Far different situation if you are living off grid and you need to bulk charge your batteries in the morning after several cloudy days, or need it to run a heavy load every day like a water pump. Then your load is a known steady load and you can size a diesel genset accordingly.4.5 kw APC UPS powered by a Prius, 12 kw Generac, Honda EU3000is -
Re: Selecting the correct backup generatorWhat in the world is that?
+1, I'd love to know too.4.5 kw APC UPS powered by a Prius, 12 kw Generac, Honda EU3000is -
Re: Selecting the correct backup generator
Fumigatin' diesels! The process of feeding them some natural gas or propane to increase combustion temperatures and reduce deposit build-up. They make kits for diesel trucks for this (Bullydog) because it also boost HP & torque. It also shortens engine life, especially if you get it wrong. On the tractor pulling circuit they feed them ether. Very impressive power output; very shortened lifespan. (It is standard practice to use a shot of ether to start some diesel engines.)
In any case, matching the gen size to the application is key. There's no sense running a 20kW unit where only a 2kW is needed, no matter what the fuel. -
Re: Selecting the correct backup generatorIf you were real creative you could always run propane or natural gas fumigation.What in the world is that?
Where vapor fuel is added to the intake air, and can replace up to 80% of the diesel. Some diesel fuel needed to provide the ignition. Supposed to help clean out carbon deposits from the engine too.
The poor mans way is to use a unlit propane torch spraying fuel into the intake. When it explodes, you are poor.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Selecting the correct backup generator
I have experemented with propane fumigation.
It works really well as long as you dont over do it.
Diesel truck/tractor sled pulling would be a good example of over doing it.
Or you could get 2 smaller generators, fire them both up as needed and phase sync them so they can work together on one load.Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
-
Re: Selecting the correct backup generatorCariboocoot wrote: »Fumigatin' diesels! The process of feeding them some natural gas or propane to increase combustion temperatures and reduce deposit build-up. They make kits for diesel trucks for this (Bullydog) because it also boost HP & torque.
Ah, thanks. I had heard of using LPG for power boost, just hadn't heard that term and didn't know it also helped with deposits.4.5 kw APC UPS powered by a Prius, 12 kw Generac, Honda EU3000is -
Re: Selecting the correct backup generator
I was wrong about that 5kw 4-pole kubota I work on. Friday I filled one up and it holds just over 11gal, not 14 or 15. I was thinking of another type of unit.
I don't work on the tiny ones as much these days.
So 3 nights around 36hr for less than 12 gallons of diesel.
I have had these engines completely apart before and they dont wet stack or soot up or any thing running a 40% load for thousands of hours.
The only generators I have that wet stack are the big ones that normally get run at like 2% or 3% load continiously.
The way you un-wet stack them is run them at as much load they hold for a few minutes to 20min until the smoke lets up.
What I did for years until I got a generator was I bought a stand alone inverter and hooked it up to a vehicle battery to run the small loads when the power went out. You can use your vehicle as a little generator for short peroids.
Propane and natural gas fumigation when done right can help the engine last longer, the engines run cleaner, less soot gets in the oil, the oil stays cleaner longer, the flameable gas aids the diesel in completely buring up.
Any flameable gas or easy to vaporize liquid can be used. Something having a high "octane" rating helps avoid pre-ignition. Methanol, ethanol, propane and methane all have "octane" ratings near or well above 110.
Fumigation with Ethanol or methanol is called a "hot shot".
Water Methanol mixes are used to cool EGT's and boost fuel mpg.
When I ran propane funimation I had an EGT gauge and the temp read no different unless I had it floored.Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
-
Re: Selecting the correct backup generator
It would be neat to see auto start 2kW diesel or propane gensets... Guess that market is just too small now.
I would suggest to people that they put some sort of Watt*Hour meter on their genset and do a kWH per Gallon (lb, liter, etc.) measurement and see what their "mileage" really is.
I have seen people's whose numbers for diesel work out to 7kWH per gallon (or even more).
A typical "noisy" 3.5-5kW genset probably gets around 6kWH per gallon at full power. If we assume that these gensets run about 1/2 fuel flow on 0-50% output loading, running 400 watts on a 5kW genset would be (these are just rough guesses and assuming a fridge, few lights, radio will average 400 watt draw):- 0.5 * 5 kWH / 6kWH per Gallon = 0.42 gallons per hour
- 0.4 kWatts * 1 Hour / 0.42 gallons per hour = 0.95 kWH / gallon
- 1.6kW * 4 hours / 1.1 gallons = 5.8 kWH per gallon
- 0.4kW * 9.6 hours / 1.1 gallons = 3.5 kWH per gallon
- 5kW * 36 hours * 0.40 / 11 gallons of diesel = 6.5 kWH per gallon
If you needed ~2kW or more of electric power during an outage, that 5kW diesel would be the way to go... If you needed ~400 watts or so to run "your home" during an outage, then I would humbly suggest a smaller genset as it would only use:- 36 hours / 9.6 hours per gallon = 3.75 gallons of fuel
A standard 5kW "noise maker" genset powering a 400 watt load would run about 0.42 gallons per hour or:- 0.42 gallons * 36 hours = 15.1 gallons of gasoline
Again, power usage/needs are a very personal choice... Just suggesting ways to help you make your own decisions about what will work well for your setup.
Please note, the numbers above for the diesel genset are just guess work on my part--Oil Pan 4 may be able to tell us what his loads actually where and we can work out the real fuel flow equations.
-BillNear San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset -
Re: Selecting the correct backup generator
These generators run two 1000w halide lamps.
I would say fuel consumption isn't bad, right around 2lb/hr for a 2kw load.
If this were my personal generator I know I could get better fuel economy, I would mod it by tossing the belt driven battery charge alternator and running a charger off 115VAC power. Install a larger radiator so the fan wouldn't be needed that often and ditch the belt driven fan for an temp switch controled electric one, powered by AC. Lastly make the generator speed switchable between 50 and 60Hz, That way I can run low power loads (if I have to) on 50Hz and save some fuel. It would be 300 less RPMs.
I have a lot of crap to run and I would want to be able to make my equipment mobile.
As of 2010 the density of petroleum diesel is about 0.832 kg/l (6.943 lb/US gal), about 12% more than ethanol free petrol (gasoline), which has a density of about 0.745 kg/l (6.217 lb/US gal).
E10 gas weighs in at about 6.12 lb/gal.Solar hybrid gasoline generator, 7kw gas, 180 watts of solar, Morningstar 15 amp MPPT, group 31 AGM, 900 watt kisae inverter.
Solar roof top GMC suburban, a normal 3/4 ton suburban with 180 watts of panels on the roof and 10 amp genasun MPPT, 2000w samlex pure sine wave inverter, 12v gast and ARB air compressors.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 192 Solar Information links & sources, event announcements
- 888 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.4K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 426 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 624 Energy Use & Conservation
- 611 Discussion Forums/Café
- 304 In the Weeds--Member's Choice
- 75 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed