12 volt Battery/Solar System Recharging Problem

Marco57
Marco57 Registered Users Posts: 7
New Member,

5 years ago i purchased a complete solar system for my small cottage in the woods since there is no hydro service available in the area.

The system includes 5 solar panels (100W/each), a 2500 Watt Inverter/Charger (Trace SW), and 8 – L16 (6 volt) batteries wired for 12 Volt.

The system was designed for 3 day usage and 4 day charge. My cottage is only used on weekends. I use aprox. 100 amps daily (between 200 and 250 amps a weekend) I don't believe that I ever used the batteries more than 30-40% of their power.

In spring 2009, i had to return all 8 batteries to their manufacturer to be recharged, because the batteries were high in voltage but very weak in amperage (strength). All normal battery chargers were not able to bring them up in amperage.

This fall i have the same problem. (Yes, it hasn’t been very sunny in my part of the country this fall, but I’ve been using my generator to compensate) I get to the cottage and the batteries are fully charged, but as soon as i start using a few lights, they drop down below 12 Volts. I've been so careful with my usage in the past year, and yet, i still have the same problem. I've been equalizing the system monthly as recommended by the manufacturer.

I never used to equalize monthly, till i sent the batteries back to the manufacturer. My solar system provider, along with engineers from Trace Engineering, and the battery manufacturer informed me to start equalizing monthly. It's apparently the newest recommendation for solar systems with batteries.

My main consumption comes from a 3/4HP-220Volt water centrifuge well pump. It's peak is 3000 watts for a few seconds and then stabilizes at 1200 ... to fill up my tank, it takes aprox. 30 seconds and consumes aprox. 3 amps.

I've checked the system with a hydrometer, it's been stuck in the middle of white area for two months now. (All cells have identical readings) … also, the batteries were rotated in spring 2009.

The system is fully maintained when I’m gone.

The water level in the batteries has never been below the plates.

I've always left the batteries in a warm place between 41 F in winter, and a maximum of 68 F in summer.

My supplier always has a different excuse. I use the system too little, or too many batteries, should go down to 4 instead of 8 etc...

It's been a 5 year trial and error situation. I'm tired of dealing with it.

Do any of you have any idea on why the batteries always get so weak?

Thanking everyone in advance for your answers!
Mark

Comments

  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Re: 12 volt Battery/Solar System Recharging Problem

    Hello and welcome!

    Your problem is a very common one: not enough panel for the batteries.

    You have four parallel banks of L16's, right? At 320 Amp hours each that's 1280 Amp hours. There is absolutely no way that 500 Watts of panel will properly recharge this. Your batteries are getting sulphated - the plates coated with sulphor from the electrolyte solution, thus reducing the Amp hour capacity (even though the Voltage appears normal). It's classic.

    To elaborate: 500 Watts of panel would probably at best charge 14.2 Volts (for a 12 Volt system) at 28 Amps. That's enough current for 280 Amp hours of battery. It won't even keep one of those L16 banks in a proper state. You'd need over 2000 Watts of panels and two charge controllers to keep that much battery "happy".

    Time was when the thinking went like this: you can charge any size bank if you've got enough charge time. Turns out that was a fast way to shorten the life of the batteries. Now we know you need to get them recharged as quickly as possible, preferably daily. You need a current rate of 5-13% of the bank's Amp hour capacity. And the L16's in particular need higher current to avoid the stratification they are prone to. Here's a link to the battery FAQ's, a good place to start:
    http://www.windsun.com/Batteries/Battery_FAQ.htm#Battery%20Charging

    I suggest you re-evaluate the whole system, starting with your load requirements. It may be possible to drop some battery capacity and/or add a bit more panel rather than go whole-hog. If you really need that much capacity you should be looking at a higher Voltage system.

    We'll all be happy to help you get this straightened out. :D
  • Windsun
    Windsun Solar Expert Posts: 1,164 ✭✭
    Re: 12 volt Battery/Solar System Recharging Problem

    What you have is a classic case of sulfation, mainly from having far too much battery capacity for the size of the solar panels. A single pair of L16's would have been far better - and a lot cheaper.

    Here is a fairly good writeup on sulfation http://www.boatelectric.com/sulfation.htm

    You can try using one of the battery desulfators - they work.. sometimes. We have seen them bring back batteries from 5% to 70% capacity in some cases, in other cases there was only a marginal increase. A lot depends on factors you cannot see without actually tearing the battery apart, which kind of renders the battery unusable. In your case it might be worth trying on half the bank, but no guarantess it will bring them back. Given the age of the batteries, you might be better off just buying a new pair. You can probably get around $10 each for the old ones as recycle.
  • BB.
    BB. Super Moderators, Administrators Posts: 33,613 admin
    Re: 12 volt Battery/Solar System Recharging Problem

    Good Morning Mark,

    I have deleted the second thread--It will just cause confusion as people may split their posts across the two threads.
    Marco57 wrote: »
    The system includes 5 solar panels (100W/each), a 2500 Watt Inverter/Charger (Trace SW), and 8 – L16 (6 volt) batteries wired for 12 Volt.
    Lets look at what you have right now... 500 watts of solar panels and lets assume this L16's:
    • Trojan L16RE-A 6 volt @ 325 Amp*Hours (20 hour rate)
    Lets assume this is a 24 volt battery bank--But it does not matter that much--the numbers will be the same if it is 4x325AH@12volts or 2 strings x 325AH@24volts.

    Your rate of charge with the solar panels and the L16's is (24 volt calc):
    • 500 watts * 0.77 derating / (2x325AH * 24 volts) = 0.025 = 2.5% rate of charge
    The first issue is, when charging purely with solar panels, you really do not have enough solar panels to fully recharge the battery bank in normal use.

    We use several rules of thumb here... One is a 5-13% charge current/bank capacity... Below 5% you have problems mixing the electrolyte and it takes too long to recharge the battery bank (run risk of sulfate hardening).

    Another is 10% minimum rate of charge for "tall batteries" like the L-16 to properly mix the electrolyte...

    Over 13% rate of charge can overheat the battery bank--But for the most part, a good charge controller (with remote battery temperature sensor) will limit that problem. Leaving that 13%+ rate of charge just being expensive for power/panels/capacity you will hardly ever use.

    So, for 8x L16's and 10% rate of charge (with 0.77 solar panel+charge controller derating), you would be looking at needing:
    • 2x325AH * 24 volts * 0.10 rate of charge * 1/0.77 = 2,026 Watts of solar panels recommended
    If you once a week recharged the bank at 10% rate of charge (~65 amps) from an AC genset:
    • 2x325AH * 29 volts charging * 0.10 rate of charge * 1/0.80 charger eff * 1/0.50 generator loading = 4,700 watt genset (approx)
    A 3-5kW genset running > 50% capacity will be fairly fuel efficient.

    You could also add the "Mix charging/Equalization" by running a smaller genset during the middle of the day when the solar panels are charging too (if needed).
    The system was designed for 3 day usage and 4 day charge. My cottage is only used on weekends. I use aprox. 100 amps daily (between 200 and 250 amps a weekend) I don't believe that I ever used the batteries more than 30-40% of their power.
    The problem with small charging systems and large battery banks is the longer the batteries sit below approximately 75% state of charge, the more they will sulfate (lead sulfate crystallizes and permanently reduces battery capacity).

    A day below ~75% is not going to kill your battery, but cumulative time of weeks and months below 75% will.

    So, you have one of the common mistakes of having too much battery bank capacity for your charging capacity.

    If you do not want to add solar panels at this time, at least running a genset to get the batteries > 80-90% state of charge when you leave would be a good idea (assuming no power usage while you are away--the current solar panels are, more or less, just trickle charging your battery bank).
    In spring 2009, i had to return all 8 batteries to their manufacturer to be recharged, because the batteries were high in voltage but very weak in amperage (strength). All normal battery chargers were not able to bring them up in amperage.
    Sounds like it can be sulphation--Does not sound like a battery manufacturing problem.
    This fall i have the same problem. (Yes, it hasn’t been very sunny in my part of the country this fall, but I’ve been using my generator to compensate) I get to the cottage and the batteries are fully charged, but as soon as i start using a few lights, they drop down below 12 Volts. I've been so careful with my usage in the past year, and yet, i still have the same problem. I've been equalizing the system monthly as recommended by the manufacturer.
    Now sounds like a good time to analyze your loads (watts peaks, and Watts*Hours use per day). Redesign the battery bank/solar array/generator to meet your needs, with a cost effective solution.
    I never used to equalize monthly, till i sent the batteries back to the manufacturer. My solar system provider, along with engineers from Trace Engineering, and the battery manufacturer informed me to start equalizing monthly. It's apparently the newest recommendation for solar systems with batteries.
    Equalization has been a common recommendation (forever?)... There are several issues with equalization.

    One is that end-users assume that equalization "fixes" battery problems and tend to equalize way more often and way longer (hours+) than needed. This can actually cause the batteries to fail much sooner (plate erosion, positive grid corrosion, etc.).

    And, in your case, you may not have enough charging current (size of AC generator and battery charger, definitely not enough solar panels) to properly mix the electrolyte (stratification) in your tall battery cases. You can get a mix of problems--Dense electrolyte at the bottom cell (over-charged) and mostly water at the top of the cell (undercharged and sulphation).
    My main consumption comes from a 3/4HP-220Volt water centrifuge well pump. It's peak is 3000 watts for a few seconds and then stabilizes at 1200 ... to fill up my tank, it takes aprox. 30 seconds and consumes aprox. 3 amps.
    A large battery bank will certainly help when running large AC (and DC) and their starting surges.

    A longer term solution may be to look at running a smaller DC (or AC) pump to reduce surges and keep other system components smaller.

    Another solution may be to use a large cistern with the AC pump and genset (run once every few days). And use a small DC pump for pressurization in the cabin.
    I've checked the system with a hydrometer, it's been stuck in the middle of white area for two months now. (All cells have identical readings) … also, the batteries were rotated in spring 2009.
    Sounds like the battery wiring is OK (balanced):

    Smart Gauge Battery Bank Wiring Guide

    The system is fully maintained when I’m gone.

    The water level in the batteries has never been below the plates.

    I've always left the batteries in a warm place between 41 F in winter, and a maximum of 68 F in summer.
    Sounds OK.
    My supplier always has a different excuse. I use the system too little, or too many batteries, should go down to 4 instead of 8 etc...
    I would guess 1/2 or 1/4 the battery bank with your existing solar panels

    But, we also need to discuss your power needs by season... If you are in the Montreal Canada (or further north) area and use the system a lot in the winter--You will probably have to use the genset more than you are today.
    It's been a 5 year trial and error situation. I'm tired of dealing with it.
    It is frustrating... Lets start with how much power you use, by season, and where is the cabin located (You can look at the PV Watts website and pick a site in US/Canada that is close to your place).

    Some random suggestions (read first--don't buy anything yet):

    Deep Cycle Battery FAQ
    www.batteryfaq.org
    Battery Monitors (and Victron Battery Monitors)
    Kill-a-Watt Meter (for measuring 120 VAC appliance power usage)
    All About Charge Controllers
    Read this page about power tracking controllers

    I really like Battery Monitors--They let people look at one meter and figure out the state of charge of their battery bank. Great for family members/guests that you don't want going out and using a hydrometer to measure the bank's charge.

    Another thing to do is look at your loads... We tend to stress conservation as being a better "investment" vs throwing more solar panels / batteries / generators at the problem.

    Don't let coffee makers, hair driers, microwave ovens become a major set of loads unless you are willing to pay for their use (more panels, more batteries, larger inverters, etc.). On occasion, the spouse will give you a minimum set of requirements for their (and yours) happiness. ;)

    Also look at the genset / charger / battery sizing... Many times a large generator has a nice price for a large / reliable unit. However, for cabin use, a 8-15kW genset is way too large to efficiently power the day to day loads/battery bank charging needs.

    Sometimes, a better solution is to get a second, smaller genset, (like the Honda eu1000i/eu2000i/eu3000i) for day to day use. Pick your genset to run > 50% rated load most of the time... Other than the Honda (and a few others) that idle down with light loads, most gensets use ~50% fuel flow for 0-50% electrical use. And diesel gensets should be operate at least 50-65+% rated load for long life.

    I will stop typing here... I have made some pretty broad statements. They are intended to be starting points in our discussions--not the only possible end results.

    Your thoughts?

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Marco57
    Marco57 Registered Users Posts: 7
    Re: 12 volt Battery/Solar System Recharging Problem

    Thanks Bill for all your insight. Also, i apologize for adding my question to another forum, i thought i had posted the original one on the wrong forum.

    My thoughts you ask?

    I just found out from my so called "specialist" that my panels are not 100Watts each, but 85Watts each. Maybe that's why he told me just last week that i could probably get rid of the 8 batteries and replace them with 4 new L16's and that with my weekly power consumption (+/- 300Amps), the system would work just fine.

    Should i remove 2 of the eight batteries from the system and see what happens?

    I purchased the solar system because i was tired of having to start the generator (5500 Watt) everytime that i ran out of water. My fridge, stove, & hot water tank work on propane. I don't use any coffee makers, microwaves, blow dryers, etc... I use the system for the centrifugal water pump (well is 153 feet deep), lighting and some TV viewing.

    I cannot use a 1000W-3000W genset. The Trace Engineering inverter/charger doesn't recognize it's power and automatically transfers to "bulk" mode, and it chokes the smaller generators.

    I'm wondering now if i use only 300A weekly, maybe 4 L16's will do the trick without having to add panels.

    What do you think?
  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Re: 12 volt Battery/Solar System Recharging Problem

    I think it's even worse than we first thought. :p

    Five 85 Watt panels is only 425 Watts, which will actually perform like 340 Watts at best.
    That's 340 / 14.2 Volts (yes, Bill; it's a 12 Volt system :D ) = 23.9 Amps. That's pretty meager for even one set of L16's.

    Any chance you could switch to a pair of T105's? At 225 Amp hours they'd be more suited to your panels. That would give you a maximum of about 100 Amp hours to work with: roughly 1.2 kW hours per day. That's more in line with what the panels are likely to "harvest".

    I'd suggest you get a hydrometer, charge each L16 fully, let it rest over night, then check the Specific Gravity readings on each cell. Just to see if there's any salvageable batteries there. You might get away with one set and generator charging + solar, but you have a problem with the gen set on the Trace? I can't remember the SW specifically, but it should be programmable to lower its charge rate so it doesn't overwhelm a small gen set.

    As for running a well pump 153 feet deep ... has that ever worked? Frankly it's not a good set up. That's likely a 1 HP pump down there, which has a fairly substantial start-up current. It would be easily capable of overwhelming a 12 Volt inverter, no matter what Wattage.

    Just a semantics note: "300A weekly" isn't quite the right way to express it. You would use 300 Amp hours weekly, perhaps, and that's not very much.

    Any possibility of an above-ground reservoir you could pump to via generator power say once a week and then draw off as needed? Or really big pressure tank to at least reduce the pump cycling needs?
  • Marco57
    Marco57 Registered Users Posts: 7
    Re: 12 volt Battery/Solar System Recharging Problem

    Actually the 3/4HP water pump does and has always worked well with this inverter:

    Trace Engineering SW series owner's manuel:

    http://www.kyocerasolar.com/pdf/specsheets/sw2_user.pdf

    Thanks 'Coot for helping me with my terminology!

    Therefore, if 300 Amp hours weekly, aren't much, are 4-L16 type batteries sufficient for my usage?
  • BB.
    BB. Super Moderators, Administrators Posts: 33,613 admin
    Re: 12 volt Battery/Solar System Recharging Problem

    Sorry--I missed the Title with 12 volt system... Anyway, the wattage numbers still add up. ;)

    And I will forgive the double posts (including one in the wrong forum) this one time--that is normally sufficient cause for instant banning. :p;)

    Regarding using a smaller genset--The inverter/charger has both a maximum charge charging current and a maximum AC-2 (Generator Max Current) setting.

    You could program both to better match a smaller genset...

    However, you are still in need of a lot of current and a 1,600 watt genset may be pushing it:
    • 4x325AH * 0.10 rate of charge= 130 amps
    • 1,600 watt genset * 0.80 charger eff * 0.6 power factor * 1/14.5 volts = 53 amps max for 12 volt bank
    • 52 amps / 130 amps = 0.32 = 3.2%
    So, a Honda eu2000i (1,600 watt) would still be way on the small side of charging for your full bank.

    One reason for a large battery bank is to support the surge current for starting your AC well pump... If we assume that the inverter is outputting 1,000 watts while running and ~2,500 watts into the motor while starting:
    • 1,000 watts (run load) * 1/10.5 volts cutoff battery voltage * 1/0.85 inverter eff = 112 amps @ 12 volt bank
    • 2,500 watts * 1/10.5 volts cutoff battery voltage * 1/0.85 inverter eff = 272 amps @ 12 volt bank
    The maximum sustained load and surge currents should be around C/8 and C/2.5...
    • 112 amps run * 8 hour rate = 896 AH @ 12 volts for run
    • 272 amps start * 2.5 hour rate = 680 AH @ 12 volts for surge
    • 4x325AH = 1,450 AH @ 12 volts your battery bank
    So--Your bank is sized pretty nicely to support the well pump requirements...

    And that is where we get into problems with "unbalanced" systems... Heavy surge currents are a real killer for Off-Grid systems. You have to size the hardware to support the very short and heavy current spikes. Then you have support the charging systems to recharge the extra large battery banks.

    There are different ways around the issues... There are some soft start solutions for well pumps. But they are not cheap and you may need to change the AC pump out to a 3 wire or 3 phase motor.

    Or, you go with a DC / Off Grid pumping setup (several potential solutions). But that is not cheap or easy either.

    Then back to your 300 Amp*Hours per every two days? Or 150 AH per day?

    That is not very much power. For a system around Montreal (PVWATTS), 0.52 system efficiency, fixed array and 1 kW of panels (minimum size for program):
    "Station Identification"
    "City:","Montreal"
    "State:","QU"
    "Lat (deg N):", 45.47
    "Long (deg W):", 73.75
    "Elev (m): ", 31
    "Weather Data:","CWEC"

    "PV System Specifications"
    "DC Rating:"," 1.0 kW"
    "DC to AC Derate Factor:"," 0.520"
    "AC Rating:"," 0.5 kW"
    "Array Type: Fixed Tilt"
    "Array Tilt:"," 45.5"
    "Array Azimuth:","180.0"

    "Energy Specifications"
    "Cost of Electricity:"," 0.1 Can$/kWh"

    "Results"
    "Month", "Solar Radiation (kWh/m^2/day)", "AC Energy (kWh)", "Energy Value (Can$)"
    1, 3.24, 55, 0.05
    2, 4.02, 62, 0.05
    3, 4.40, 72, 0.06
    4, 4.61, 67, 0.06
    5, 4.77, 69, 0.06
    6, 5.12, 70, 0.06
    7, 5.62, 78, 0.07
    8, 4.76, 66, 0.06
    9, 4.92, 69, 0.06
    10, 3.66, 55, 0.05
    11, 2.01, 29, 0.02
    12, 2.10, 34, 0.03
    "Year", 4.10, 726, 0.63
    Ok, lets assume deep winter is going to require generator backup. And pick the 4th month (October) to design the "nominal" system around--29 kWH per month (long term average).

    And you are using 150 Amp*Hours * 12 volts per day:
    • 150 Amp*Hours per day * 12 volts = 1,800 Watt*Hours per day
    And the average collection from 1,000 watts of solar panels in October:
    • 29 kWH per month / 30 days per month = 0.97 kWH per day = 970 Watt*Hours per day per 1,000 watts of solar panels
    And to supply your daily load would require:
    • 1,800 Watt*Hours per day load / 970 WH per day per 1,000 watts of panels = 1,856 Watts of panels
    To size the battery bank based on average loads--We use 1 to 3 days of no-sun and 50% maximum discharge (this is based on a 12 volt battery bank):
    • 1,800 WH per day load * 1/12 volt bank * 1/0.85 inverter losses * 1 day no sun * 1/0.50 max discharge = 353 AH battery minimum
    • 1,800 WH per day load * 1/12 volt bank * 1/0.85 inverter losses * 3 day no sun * 1/0.50 max discharge = 1,059 AH battery maximum
    Now--that does not account for the run/surge current from a 3/4 HP well pump which would push you over the 700 to 900+ Amp*Hour (20 Hour battery rating capacity) anyway.

    So--based on various issues--It looks like a 700 AH battery bank @ 12 volts would be the minimum bank size for your existing loads (with the well pump probably being problematic at this level).

    If / when you decide to replace your inverter--You should be looking at a 24 or 48 volt system. That will at least reduce the surge currents by 1/2 or to 1/4 the 12 volt battery bank value. Smaller wire gauges would make the next install better and reduce any DC wiring voltage drop issues.

    Note--a 12 vs 48 volt battery system is no difference in costs... If you have, 8x 6 volt batteries in parallel (12 volt bank) vs 8x 6 batteries in series (48 volt bank)--You sill have the same amount of stored "energy". Just delivered at a higher voltage / lower current (power=volts*current).

    Also, solar charge controllers are rated based on their DC output current, so on a 48 volt battery bank, a 60 amp solar charge controller can handle more solar panels (fewer charge controllers to purchase):
    • 60 amps * 14.5 volts * 1/0.77 derating = 1,130 watts of solar panels @ 12 volts
    • 60 amps * 29 volts * 1/0.77 derating = 2,260 watts of solar panels @ 24 volts
    • 60 amps * 58 volts * 1/0.77 derating = 4,520 watts of solar panels @ 48 volt
    If you could figure out the way to limit the power from the water pumping system--that would allow you to use a smaller battery bank.

    However, you are still left with needing a large array for your daily loads. If you assumed that you only stayed there 2 days at a time and wanted to cut back to 1/2 the amount of solar panel... But you still need to make sure the battery bank does not spend much time below ~75% state of charge to reduce sulphation (if bad weather if forecasted after you leave--then running the genset before you take off to get the batteries over 80% State of Charge will help).

    And, if you still need the high surge current... Using a smaller bank of AGM's may be a possible solution. AGM's can support much higher surge currents than flooded cell storage batteries (higher than C/2.5 rate I used in the above surge calculations).

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Windsun
    Windsun Solar Expert Posts: 1,164 ✭✭
    Re: 12 volt Battery/Solar System Recharging Problem

    You should be able to set the max charge rate on that inverter down so that it does not drag the generator down.
  • Marco57
    Marco57 Registered Users Posts: 7
    Re: 12 volt Battery/Solar System Recharging Problem

    Thanks Guys for all your help so far!

    The reason that my pump is a 3/4HP - 220V unit, is because when i bought my lakefront lot 7 years ago, hydro had told me that within two years, our area would have hydro service. So i wired the house 120V-220V with my electrician. Now their policy changed and they will not feed our lake with hydro unless we pay, in advance, the whole bill of over $350,000.

    Bill, i'm no expert, but all your calculations seem to make sense. I do know that my pump will still work with only 6 - L16's. That was the original set-up. My "guy" added the other two L16's to my bank 5 weeks later, because i was interested in purchasing one of his 12V refrigerators. He told me that i needed 2 L16's for that type of fridge.

    Now, if i understand correctly, my batteries are almost no longer good anymore, and i'm going to have to add on more panels to make sure this doesn't happen again to the new batteries. Unfortunately, with my limited budget, i cannot change the inverter also and rewire for 24V or 48V. That Trace inverter cost me a fortune.

    Here's what i think i should do:

    1. Not worry about the batteries this winter, and use them till they're dead. (Should i remove a pair from the bank?)
    2. In spring, add a minimum of 3 solar panels.
    3. Replace all 8 L16's with either 6 new L16's or 8 new T105's (which one's are better for 12 Volt applications?)
    4. And if i have any money left over, maybe replace the 220 Volt well pump with an equivalent 12V pump.

    What do you guys think?
  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Re: 12 volt Battery/Solar System Recharging Problem

    Like I said, check all the batteries with a hydrometer. Pick the two best and put them in place. One set of these is 320 Amp hours; you could use up to 150 per day if necessary.

    If you can, get a battery meter to keep an eye on the in/out current: http://www.solar-electric.com/tm2020.html

    Keep the other batteries charged via the generator and a good battery charger so they're available if needed. Once a month should suffice if they're not too far gone. 3-stage battery charger: http://www.solar-electric.com/bach1.html

    Definitely add 2-3 more panels if you can. Another 200+ Watts worth would be good. Like a couple of Kyocera 135's: http://www.solar-electric.com/kyso130wa12v.html Note you may need an additional charge controller for this, depending on your existing controller's capacity and the compatibility of the new panels with the old (Vmp needs to be close for parallel connecting, Imp for series).

    Get a big pressure tank to reduce the pump cycling. Start-up surge on these motors is murder!

    My system runs everything with just 320 Amp hours but at 24 V - that's like two L16 12V strings. It's a bit dicey, and the loads need to be managed carefully but it can be done. My water pump is smaller, but there's an electric refrigerator that uses most of the power and a satellite/computer/phone set-up that chews through a lot as well.

    Just my two cents (Canadian - nearly at par!) :p
  • BB.
    BB. Super Moderators, Administrators Posts: 33,613 admin
    Re: 12 volt Battery/Solar System Recharging Problem

    The inverter may last you 10-15 years total--and at that point, it is usually better to replace the inverter/charger with something new (10+ year old electronics are nearly impossible to find parts and repair shops for).

    So, you will have your long term plan.

    Short term, if this cabin is only used 2 days a week, see if you can find a used Propane Refrigerator (perhaps from a wrecked RV). That will reduce much of your daily power usage and reduce your needs for more solar panels/generator run-time.

    It is a close call, but solar PV off-grid power usually makes good economic sense for a cabin/home lived in 9+ months of the year. If your place is not occupied as much--or much of your time in place is during the winter (less sun, freezing weather anyway)--A propane powered fridge may be less expensive to run.

    Your next battery bank may be better to use batteries that are not as tall at the L-16s until you can size the array to at least ~10% rate of charge.

    AGM's would be a very nice alternative--But they tend to be much more expensive (and may not last quite as long as a very good set of flooded cell batteries). The economics on AGM may be a bit murky for your setup.

    As Marc says, using a Battery Monitor to check out your exact loads and charging profile--and use the Genset in the early morning (let the solar finish off the charging the rest of the day) to keep the batteries "happier". Don't feel you have to recharge the battery bank to nearly 100% full using the genset every day. That will be very expensive fuel wise and not very efficient (as the charging current tappers down as the batteries are >~80-90% state of charge).

    I am not sure you need a really nice 3 stage charge controller (with float) unless you use it at home with utility power. You will never use float voltage when running with a genset (total waste of fuel).

    You can also use small Battery Tenders or equivalent float chargers at home after you get the batteries fully charged too (just monitor water usage once per month--Even float chargers will still use water).

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Marco57
    Marco57 Registered Users Posts: 7
    Re: 12 volt Battery/Solar System Recharging Problem

    Bill, i mentioned earllier that only use the inverter for 3 things, 1 my well pump, 2, my lighting, and 3, my TV on occasion. I already have a propane fridge, stove and hot-water tank ... i never purchased the 12V fridge .... the system wasn't working well enough for me to invest another $2000 to replace my propane fridge.

    Marc, The problem is that i'm only there on weekends ... my cottage is 2 hours away from my home in Montreal, Canada. I can only charge the batteries with my generator when i'm there, and i cannot bring them home, i live in a small condo.

    I already have a battery monitor, that's how i know that i consume aprox. 120-150amp hours daily. The monitor does not show amperage though, only voltage. It believes the batteries are full and in good condition.
  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Re: 12 volt Battery/Solar System Recharging Problem
    Marco57 wrote: »
    Bill, i mentioned earllier that only use the inverter for 3 things, 1 my well pump, 2, my lighting, and 3, my TV on occasion. I already have a propane fridge, stove and hot-water tank ... i never purchased the 12V fridge .... the system wasn't working well enough for me to invest another $2000 to replace my propane fridge.

    Marc, The problem is that i'm only there on weekends ... my cottage is 2 hours away from my home in Montreal, Canada. I can only charge the batteries with my generator when i'm there, and i cannot bring them home, i live in a small condo.

    I already have a battery monitor, that's how i know that i consume aprox. 120-150amp hours daily. The monitor does not show amperage though, only voltage. It believes the batteries are full and in good condition.

    :confused: If the monitor only shows Voltage, how do you get the 120-150 Amp hours daily figure?

    Still the best place to start is with a hydrometer to check the Specific Gravity. Voltage is not a reliable indicator of State Of Charge nor battery condition; sulphated batteries can read "proper" Voltage and still have lost significant capacity. It's like going from a 'D' cell to a 'AAA'; both are 1.5 Volts, but there's a big difference in how long they'll supply that Voltage for any given load. A sulphated battery "looks" like a 'D' cell, but performs like a 'AAA' (so to speak).

    Hey; our cabin used to be 6 hours from home. Since the move it's down to 1, but it's still and arduous trek! I know just what you mean! :cry:
  • BB.
    BB. Super Moderators, Administrators Posts: 33,613 admin
    Re: 12 volt Battery/Solar System Recharging Problem

    There are different types of battery monitors. The simple ones just measure voltage. The more complex ones have a large current shut placed in the main battery wiring and measure current flow, in and out, over time.

    If you leave with the batteries mostly charged, then the existing solar will keep the battery bank safely charged.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • westbranch
    westbranch Solar Expert Posts: 5,183 ✭✭✭✭
    Re: 12 volt Battery/Solar System Recharging Problem

    Hey guys, pardon my ignorance on FLA's ...

    but is there not a table provided by the manufacturer showing the time a specified load ( XXX amps) can be applied to achieve an 'end voltage'.

    I know these are available for most AGM batteries.

    If such a table is available it will tell Marco57 how good or bad his batteries are.
    the shorter the time to reach the 'end voltage', the worse the batteries are. Though this does not tell anything about potential recovery.

    NOTE
    These tables are specified to voltages we consider damaging to any battery eg 9.6V and above.

    cheers
    Eric
     
    KID #51B  4s 140W to 24V 900Ah C&D AGM
    CL#29032 FW 2126/ 2073/ 2133 175A E-Panel WBjr, 3 x 4s 140W to 24V 900Ah C&D AGM 
    Cotek ST1500W 24V Inverter,OmniCharge 3024,
    2 x Cisco WRT54GL i/c DD-WRT Rtr & Bridge,
    Eu3/2/1000i Gens, 1680W & E-Panel/WBjr to come, CL #647 asleep
    West Chilcotin, BC, Canada
  • Marco57
    Marco57 Registered Users Posts: 7
    Re: 12 volt Battery/Solar System Recharging Problem

    I went to the cottage for a few hours this weekend, just to check & see if all was well, then returned home.

    I checked all 8 batteries with my hydrometer, and they're all stuck at 1.200 (white area close to the red). I also checked to see if the water had any sulfation happening at the surface (film) ... no, the water was clear.

    My voltage meter says that the batteries are "FULL", and i consumed 15 amp hours while i wasn't there in 8 days. (I have a burglar alarm system hooked-up to the batteries which uses about 8 Ah, and 7 Ah for the inverter itself) Yes, the inverter charger uses 7Ah weekly at the "OFF/CHG" position.

    Since it was another cloudy day in the Laurentians, i started the generator thinking i was going to charge the batteries for a couple hours while i was there. The inverter changed from bulk charge to float in about 20 minutes. The inverter thinks the batteries are full, but the hydrometer says different.

    One thing crossed my mind while i was there. Even if i add panels, and change batteries, etc..., if the weather doesn't cooperate, i'm still in the same boat. I'm thinking now of investing instead in a automatic propane generator, between 6KW-8KW. It would automatically start when the batteries are low, even when i'm not around. Same cost, but a better backup, don't you think???
  • Cariboocoot
    Cariboocoot Banned Posts: 17,615 ✭✭✭
    Re: 12 volt Battery/Solar System Recharging Problem

    Consistent SG is good. Low SG is bad. This is what sulphation looks like. It doesn't show up in the electrolyte; it coats the plates. The Voltage will be "normal". Unfortunately charge controllers can't read SG, they read Voltage.

    I've gone back over this thread and don't see any specs on what you've got for a charge controller. Some of them are programmable. It could help to alter the Absorb time, if possible. Sounds like the system is coming up to 'X' Volts for Absorb and then dropping back to a lower Float Voltage.

    But there's still more battery than the panels can manage.

    Personally I'm not keen on unattended auto-start generators. If it doesn't start, nothing happens. And that's not the worst-case scenario (says the man who has to replace a gas line on a gen that started leaking while it was running).
  • icarus
    icarus Solar Expert Posts: 5,436 ✭✭✭✭
    Re: 12 volt Battery/Solar System Recharging Problem
    i mentioned earllier that only use the inverter for 3 things, 1 my well pump, 2, my lighting, and 3, my TV on occasion. I already have a propane fridge, stove and hot-water tank ... i never purchased the 12V fridge .... the system wasn't working well enough for me to invest another $2000 to replace my propane fridge.

    In addition to the now obvious "too much battery/too little pv issue, consider using different inverters for different tasks. For example, the suresine 300 is a great, very efficient inverter for general lighting and TV, and it's stand by draw is very small. Using a large inverter to consistently power small loads is very inefficient .

    I would personally shy away from a 12 vdc fridge, or even a high efficiency compressor fridge for a part time cabin. As I have said before, the more the fridge is used annually the smarter it is to move away from propane, but for weekends, and occasional holidays a propane wins. (Not to mention that you already have it.

    I confess I haven't read the entire thread in detail, but from the sound of it, it sounds like the biggest issue (aside from too much battery/to little panel) is the pump. I might suggest getting a much bigger storage tank, run the genny once a day, once a weekend, fill the tank, and do some battery charging at the same time, and forget about pumping water with the solar.

    A pair, or 2 pairs of l-16s make a great part time battery bank, and coupled with 3-600 watts of Pv works pretty well.

    Just fyi, we live off grid, with 400 watts of PV, we consistently draw ~6-800 wh of power/day, and generate just about the same. On a great solar day, we can generate 1-1.5kwh/day. So my rule of name plate/2*4 seems to work quite well.

    Good luck and keep in touch,

    Tony
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Re: 12 volt Battery/Solar System Recharging Problem

    What are your pump requirements ? Depth in well ? Pumping to a pressure tank, or to a cistern ? Many starts daily, or just 1x a week ?

    Perhaps going to a smaller AC 240V 1/2 hp or 1/3 hp pump, with longer runtime will be an easier starting surge for the batteries/inverter. But even switching out a working pump is a $500 expense.

    Mike
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • Marco57
    Marco57 Registered Users Posts: 7
    Re: 12 volt Battery/Solar System Recharging Problem

    Well depth is 153 feet, therefore the need of a 3/4HP motor ... consuption is aprox. 3 minutes in length, 7 times daily, for 2 days (weekends) weekly, into a pressurized tank.
  • mike95490
    mike95490 Solar Expert Posts: 9,583 ✭✭✭✭✭
    Re: 12 volt Battery/Solar System Recharging Problem
    Marco57 wrote: »
    Well depth is 153 feet, therefore the need of a 3/4HP motor ... consuption is aprox. 3 minutes in length, 7 times daily, for 2 days (weekends) weekly, into a pressurized tank.

    165' into cistern gives me 9gpm, if you can live with lower flow of about 6-7gpm, you could go with 1/2 hp. just have to give up the long hot showers.

    What is size of your pressure tank ? 40 gal gives about 20 gal of storage. Adding another tank will increase Run time, but decrease the number of Starts.

    it's all options and trades.
    Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister ,

  • icarus
    icarus Solar Expert Posts: 5,436 ✭✭✭✭
    Re: 12 volt Battery/Solar System Recharging Problem

    Larger storage tank=longer run times, fewer starts and vise-versa.

    Consider using a genny for a while each day (or week) for bulk pumping instead of sizing a PV system?

    Tony