XW auto gen start and other XW questions
lotek
Solar Expert Posts: 65 ✭✭✭✭
concerning the XW remote generator start, I have written Xantrex about this but so far no responce.
Does anyone happen to know what type (1 through 13)connection diagram would work for the Briggs 40248 generator. type as listed in owners manual pg 2-9 through 2-21
http://www.wholesalesolar.com/pdf.folder/inverter%20pdf%20folder/XantrexXWAutomaticGeneratorStartManual.pdf
the 40248 is a propane powered generator, so no preheat
The switch toggles from middle, both left and right. Hold down the left side untill it starts, the switch returns to the center . hold down right side until it stops, switch returns to center. Im fairly sure by the way the off side works , its just grounding out the plug. if you let up on the off side before the motor is completely stopped, it starts running again.
Does anyone happen to know what type (1 through 13)connection diagram would work for the Briggs 40248 generator. type as listed in owners manual pg 2-9 through 2-21
http://www.wholesalesolar.com/pdf.folder/inverter%20pdf%20folder/XantrexXWAutomaticGeneratorStartManual.pdf
the 40248 is a propane powered generator, so no preheat
The switch toggles from middle, both left and right. Hold down the left side untill it starts, the switch returns to the center . hold down right side until it stops, switch returns to center. Im fairly sure by the way the off side works , its just grounding out the plug. if you let up on the off side before the motor is completely stopped, it starts running again.
Comments
-
Re: XW auto gen start and other XW questions
My diesel uses the stop signal to energise a solenoid that shuts off the fuel. So similar to yours, if I press the stop button and then disconnect the electrical system before the engine has stopped, it'll start up again. So the stop signal doesn't ground, it energises.
I would _guess_ that type 10 or type 12 could be what you're looking for: no pre-heat. Energise relay 1 to stop, energise relay 2 to start. -
Re: XW auto gen start and other XW questionsconcerning the XW remote generator start, I have written Xantrex about this but so far no responce.
Does anyone happen to know what type (1 through 13)connection diagram would work for the Briggs 40248 generator. type as listed in owners manual pg 2-9 through 2-21
http://www.wholesalesolar.com/pdf.folder/inverter%20pdf%20folder/XantrexXWAutomaticGeneratorStartManual.pdf
the 40248 is a propane powered generator, so no preheat
The switch toggles from middle, both left and right. Hold down the left side untill it starts, the switch returns to the center . hold down right side until it stops, switch returns to center. Im fairly sure by the way the off side works , its just grounding out the plug. if you let up on the off side before the motor is completely stopped, it starts running again.
Telephone Xantrex."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Re: XW auto gen start and other XW questions
A couple of years ago I had to make an old Woodward control work with the XW GSP. In that case, I had to figure out what the start and stop logic was in the Woodward and match it to one of the drawings in the XW manual. There was a couple that were similar and I chose what I thought would work and it's still working. Xantrex may or may not have info. on your generator and you may have to do the same or see if you can get diagrams for your start/stop wiring on the generator.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed