TriMetric confusion

Solar Expert Posts: 39
Howdy. I just installed the TriMetric and am trying to enter the setpoints. The manual says to use 28.6 for the charged setpoint voltage. I have 12 Trojans L16RE-2V in a 24 volt system. The battery is rated at 1235 AH @100hr and 1110 AH @20 hr. I don't understand their instructions for calculating the battery system capacity. My batteries are connected in series. Please help me with the math. Thanks a lot!

Welcome!

It looks like you're new here. Sign in or register to get started.

Comments

  • Super Moderators, Administrators Posts: 33,671 admin
    Re: TriMetric confusion

    Correction: The below I made a mistake and thought the OP had 24x2 volt batteries... Not 12x--The stuff following is correct in principle--but for the original question, the OP should enter in 1,110 AH (20 Hour rate) because there is just one string of 12 batteries. -Bill B.

    L16re-2v 1110 @ 20 Hour Rate.
    • 12 batteries * 2 volts = 24 volts @ 1,110 AH per string
    • 2 strings at 24 volts * 1,110 AH = 24 volts @ 2,220 AH
    Adding batteries in series increases the voltage.

    Adding batteries in parallel adds the AH capacity.

    There is no loss if power/energy if you have a 12 volt bank at 4,440 Amp*Hours or a 24 volt at 2,220 AH.
    • Power = Volts * Current
    • Power = 2*volts * current = volts * 2*Current
    Is that the question?

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Solar Expert Posts: 1,485 ✭✭✭✭
    Re: TriMetric confusion

    The 28.6v setting is just the voltage trigger that the Trimetrics resets the battery to 100% full. That is a good number as your absorb charge setting should be at least 28.6 vdc.

    The AH setting is just the reference for the AH count up/down. You can play whatever psychological games you want on this setting by setting the reference number to 50% to 80% of you batteries AH rating.

    I have mine set to 50% of 20 hr. AH rating to encourage me not to discharge batteries below 50% SOC.
  • Solar Expert Posts: 386 ✭✭✭
    Re: TriMetric confusion
    he battery is rated at 1235 AH @100hr and 1110 AH @20 hr
    Use the 20 hour rate: 1110 AH @20 hr on the Trimetric. Set the charged set-point current around 20 amps and the charged set-point voltage around 29 volts. This is used by the Trimetric to determine when the battery is fully charged.
  • Super Moderators, Administrators Posts: 33,671 admin
    Re: TriMetric confusion

    MikeO,

    You are suggesting 1,110 AH setting to show 0-100% capacity based on 50% maximum discharge for long battery life?--Or did I mess up reading the original question?

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Solar Expert Posts: 39
    Re: TriMetric confusion

    I'm sorry, this is a struggle for me. So, is the number I program for the battery system capacity gonna be simply the AH number, which is 1235?
  • Solar Expert Posts: 386 ✭✭✭
    Re: TriMetric confusion
    which is 1235?
    No use the 20 hour rate for you battery capacity which is 1110 amp hours. Bill I am suggesting just putting in the new battery capacity rating so when the Trimetric reads 50% full on battery capacity, you know its time to get it charged up again. The Trimetric also has an amp-hours from full reading which would correctly read -555 amp-hours at 50% DOD.
  • Super Moderators, Administrators Posts: 33,671 admin
    Re: TriMetric confusion

    Opps--I did miss-read the post... It is 12 batteries--Not the 24 I thought I saw.

    Fixed original link.


    Thank you Mike.

    -Bill
    Near San Francisco California: 3.5kWatt Grid Tied Solar power system+small backup genset
  • Solar Expert Posts: 39
    Re: TriMetric confusion

    Okay, thanks for the help folks. My P1 is 28.6, P2 is 22.2, P3 is 1.11(decimal is flashing which means 1,110). Do I have it right?
  • Solar Expert Posts: 39
    Re: TriMetric confusion

    I can't get P2 to be 22.2. It won't do the .2. All it will do is 22. Is that okay?