Charge controller power loss
beth
Solar Expert Posts: 32 ✭
If an outback fm 80 is being used with an array that puts out 40 amps at 60v.
and you are charging a 24v battery, then if the panels were putting out this max, that would be 100 amps at 24v comming out of the controller correct?
so since the max out put of this controller is 80 amps, are you losing the 20 amps in this example
Thanks all
and you are charging a 24v battery, then if the panels were putting out this max, that would be 100 amps at 24v comming out of the controller correct?
so since the max out put of this controller is 80 amps, are you losing the 20 amps in this example
Thanks all
Comments
-
Re: Charge controller power loss
Controller will limit output to 80A max regardless of what your panels are capable of. You will not capture all available power for PV array in that situation. You need to get another controller and offload excess panels to it, or split array in two. Is 60V 40A measured values or what's on the sticker? Because panels rarely perform at STC rating. -
Re: Charge controller power loss
Yes that is whats on the sticker, the controller says its good up to 2500w for a 24 v system. and my total array is 2350w. -
Re: Charge controller power loss
From a real-world perspective (instead of theoretical):
60 Volts @ 40 Amps = 2400 Watts. Your array is 2350 Watts, so that's pretty close.
Now the thing is the array probably won't put out that much except on rare occasions. More likely it will average 80% (or less) than that: 1880 Watts. Divide that by the charging Voltage of a 24 Volt system: 28.2 Volts. Net result: 66 Amps.
So whereas the controller will "choke off" the output @ 80 Amps (80 Amps * 28.4 Volts = 2272 Watts, btw - they allow for 30 Volts equalization) most of the time you're not going to see that much current available anyway. But you are about at the "saturation point".
The old MX60's preferred to run at 75% capacity. I'm not sure if the FM's have this same "feature". :roll: -
Re: Charge controller power lossYes that is whats on the sticker, the controller says its good up to 2500w for a 24 v system. and my total array is 2350w.
2500 Watts / 80 amps = 31.25 Volts
Maybe they mean 2500 Watts when equalizing ??
Where does the 2500 Watt figure appear ??
On the unit itself ? If so, that may be it.
boB -
Re: Charge controller power lossYes that is whats on the sticker, the controller says its good up to 2500w for a 24 v system. and my total array is 2350w.
Technically FM80 can do 2500W with 24V system. No lie here. But only during battery equalization mode. During normal charging, your battery will be around 25 - 26V and so would be FM80 output. 25V * 80A = 2000W maximum output power from FM-80 at that battery voltage. Input > Output efficiency will be 95%, so maximum usable PV input power = 2000W/.95 = 2105W. You say you have 2350W PV array. Is it factory rating written on the back of solar panel? If so, then in real world your array will output between 1998 - 2233 Watts due to ambient temperature caused efficiency loss of solar cells and less than perfect solar angle and air clarity. Add wiring loss to that, and PV output will be even less. So you have your FM80 maxed out, and on very cold and clear days you may run into FM80 hard limit. This will cause your system to harvest slightly less solar energy than available. A well designed system will not max out charge controller like that. -
Re: Charge controller power lossTechnically FM80 can do 2500W with 24V system. No lie here. But only during battery equalization mode. During normal charging, your battery will be around 25 - 26V and so would be FM80 output. 25V * 80A = 2000W maximum output power from FM-80 at that battery voltage. Input > Output efficiency will be 95%, so maximum usable PV input power = 2000W/.95 = 2105W. You say you have 2350W PV array. Is it factory rating written on the back of solar panel? If so, then in real world your array will output between 1998 - 2233 Watts due to ambient temperature caused efficiency loss of solar cells and less than perfect solar angle and air clarity. Add wiring loss to that, and PV output will be even less. So you have your FM80 maxed out, and on very cold and clear days you may run into FM80 hard limit. This will cause your system to harvest slightly less solar energy than available. A well designed system will not max out charge controller like that.
Well designed for what Antron? Most all design is balancing parrameters to the customers need. Most panels never put out their nameplate power levels after 6 months for significant hours. The FM -80 will current limit either way. I doubt Beth needs to be concerned here.
Other than code, a good case could be made for her having more solar for the summer if this parrameter was important to her."we go where power lines don't" Sierra Nevada mountain area
htps://offgridsolar1.com/
E-mail offgridsolar@sti.net -
Re: Charge controller power loss
Well designed for ability to handle all power that panels can generate. -
Re: Charge controller power lossWell designed for ability to handle all power that panels can generate.
I seriously doubt it is worth spending the extra money for a second charge controller to handle those rare occasions when the panels actually peak production and the batteries need all that current.
It is the batteries which determine how much panel and what controller is needed, and you base that on an averaged expected panel output; not the rare peak production. This isn't grid-tie where you grab every Watt you possibly can because the utility can take it. -
Re: Charge controller power lossController will limit output to 80A max regardless of what your panels are capable of. You will not capture all available power for PV array in that situation. ......
If my fixed array has been charging my batteries all morning, and the charge rate starts to taper off, come solar noon, I won't be able to force all those amps into the batteries unless I start an EQ cycle at 11:30 am daily. and that's not good !
It's always a trade off, I think at max power I can just saturate my controller, but generally, it's only running 30-40A , not it's 60A sticker. Should I have gotten the 45A controller ?
come on, we're never going to capture "all available power" - i'll settle for most.Powerfab top of pole PV mount | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister , -
Re: Charge controller power loss
OK, she does not "need" another controller. One will work just fine. I did not word my first post clearly enough. BUT in certain conditions the system may run into controller's current limit. How often? I don't know, since I do not know enough data about the system, like: geographical location, panel mounting orientation, battery bank type and capacity, wire size from PV to CC, solar panel type. -
Re: Charge controller power loss
Thanks for the replies, I did want to max out the controller, I am adding an array to my 24V system and wanted to make it as big as one controller can handle. We do have a lot of partly cloudy days so I want to catch as much sun in those conditions.
Categories
- All Categories
- 222 Forum & Website
- 130 Solar Forum News and Announcements
- 1.3K Solar News, Reviews, & Product Announcements
- 191 Solar Information links & sources, event announcements
- 886 Solar Product Reviews & Opinions
- 254 Solar Skeptics, Hype, & Scams Corner
- 22.3K Solar Electric Power, Wind Power & Balance of System
- 3.5K General Solar Power Topics
- 6.7K Solar Beginners Corner
- 1K PV Installers Forum - NEC, Wiring, Installation
- 2K Advanced Solar Electric Technical Forum
- 5.5K Off Grid Solar & Battery Systems
- 424 Caravan, Recreational Vehicle, and Marine Power Systems
- 1.1K Grid Tie and Grid Interactive Systems
- 651 Solar Water Pumping
- 815 Wind Power Generation
- 621 Energy Use & Conservation
- 608 Discussion Forums/Café
- 302 In the Weeds--Member's Choice
- 74 Construction
- 124 New Battery Technologies
- 108 Old Battery Tech Discussions
- 3.8K Solar News - Automatic Feed
- 3.8K Solar Energy News RSS Feed